Hello colleagues!
There is a packaging machine with an A1000 drive on a conveyor.
Five signals come from the controller.
1. Run forward
2. Jog
3. Reset alarm
4. Emergency stop
5. Transporter
Signals Jog, Emergency stop, Reset alarm work adequately (standard), ON is active.
The "Run forward" signal is always ON (unless there is an alarm). The signal "Transporter" in the stop is ON, it should start the conveyor by OFF.
How should the two inputs S1 and S5 be configured for the Run forward and "Transporter" signals.
[url] https://disk.yandex.ru/i/S_tzHZ79ZMa_rw[/url] |
|
| Back to top |
|
 |
matjajas Junior

Joined: 18 Jul 2022 Posts: 2
|
Posted: 16/08/2022 18:40 Post subject: |
|
|
check this procedure
https://mobile.yaskawa.com/delegate/getAttachment?documentId=TM.A1000.01&cmd=documents&documentName=TM.A1000.01.pdf
https://www.yaskawa.eu.com/Global%20Assets/Downloads/Technical_Documentation/Inverter_Drives/A1000/A1000_IP54_READY/A1000IP54READY_QSG_EN_TOEP_C710616_97A_1_1.pdf
or is this type?
https://assets.omron.eu/downloads/manual/en/v2/a1000_frequency_inverter_users_manual_en.pdf
Use the wire link between terminals SC and SP or SC and SN to select between Sink mode, Source mode or external
power supply for the digital inputs S1 to S8 as shown in Table 3.10 (Default: Sink mode, internal power supply).
See above manual
https://www.e-mechatronics.com/download/datas/catalog/kaepc71061622/kaepc71061622q_16_0.pdf
 |
|
| Back to top |
|
 |
niko7 Junior

Joined: 24 Sep 2012 Posts: 2
|
Posted: 16/08/2022 19:29 Post subject: |
|
|
Thanks for the answer.
The thing is that I can't affect the controller, and it gives out signals:
In the "STOP" mode (conveyor stopped), the PLC outputs signals:
1. Run forward ON
2. Transporter ON
In the "Run" mode (the conveyor is moving), the PLC outputs signals:
1. Run forward ON
2. Transporter OFF
In the "Alarm" mode, the PLC issues signals:
1. Run forward OFF
2. Transporter ON
This logic is not suitable for either 2-wire or 3-wire control mode A1000 |
|