PostPosted: 15/08/2022 19:09    Post subject: YASKAWA Configuration Reply with quote

Hello colleagues!
There is a packaging machine with an A1000 drive on a conveyor.
Five signals come from the controller.
1. Run forward
2. Jog
3. Reset alarm
4. Emergency stop
5. Transporter

Signals Jog, Emergency stop, Reset alarm work adequately (standard), ON is active.
The "Run forward" signal is always ON (unless there is an alarm). The signal "Transporter" in the stop is ON, it should start the conveyor by OFF.
How should the two inputs S1 and S5 be configured for the Run forward and "Transporter" signals.
[url] https://disk.yandex.ru/i/S_tzHZ79ZMa_rw[/url]
Back to top
View user's profile Send private message
matjajas
Junior
Junior


Joined: 18 Jul 2022
Posts: 2

PostPosted: 16/08/2022 18:40    Post subject: Reply with quote

check this procedure
https://mobile.yaskawa.com/delegate/getAttachment?documentId=TM.A1000.01&cmd=documents&documentName=TM.A1000.01.pdf

https://www.yaskawa.eu.com/Global%20Assets/Downloads/Technical_Documentation/Inverter_Drives/A1000/A1000_IP54_READY/A1000IP54READY_QSG_EN_TOEP_C710616_97A_1_1.pdf

YASKAWA Configuration YASKAWA Configuration

YASKAWA Configuration YASKAWA Configuration

or is this type?
https://assets.omron.eu/downloads/manual/en/v2/a1000_frequency_inverter_users_manual_en.pdf

Use the wire link between terminals SC and SP or SC and SN to select between Sink mode, Source mode or external
power supply for the digital inputs S1 to S8 as shown in Table 3.10 (Default: Sink mode, internal power supply).
See above manual

https://www.e-mechatronics.com/download/datas/catalog/kaepc71061622/kaepc71061622q_16_0.pdf
YASKAWA Configuration YASKAWA Configuration

YASKAWA Configuration YASKAWA Configuration
Back to top
View user's profile Send private message
niko7
Junior
Junior


Joined: 24 Sep 2012
Posts: 2

PostPosted: 16/08/2022 19:29    Post subject: Reply with quote

Thanks for the answer.
The thing is that I can't affect the controller, and it gives out signals:
In the "STOP" mode (conveyor stopped), the PLC outputs signals:
1. Run forward ON
2. Transporter ON
In the "Run" mode (the conveyor is moving), the PLC outputs signals:
1. Run forward ON
2. Transporter OFF
In the "Alarm" mode, the PLC issues signals:
1. Run forward OFF
2. Transporter ON
This logic is not suitable for either 2-wire or 3-wire control mode A1000
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> Drives & Inverters All times are GMT + 2 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group
Fa-ti si tu propriul forum GRATUIT, pe www.myforum.ro