How to enable a VPN connection on a SCALANCE M800 / S615 via TCP event?
https://support.industry.siemens.com/cs/document/109818271/
You can make sure that remote access to your plant or the individual plant components is not permanent by making the switching automatic. You can achieve this using a TCP event, for example. As output source for the TCP event you can use any device that is able to send a variable TCP packet to your security appliance, for example a PC, HMI or CPU.
Requirements

The firmware version of the security appliance must be V7.2 or higher
An established VPN connection
How to establish a VPN connection is described in
https://support.industry.siemens.com/cs/attachments/26662448/26662448_Remote_Networks_Overview_DOKU_V4_1_en.pdf
https://support.industry.siemens.com/cs/attachments/26662448/Archiv.zip
https://support.industry.siemens.com/cs/document/109476153/remote-access-to-simatic-hmi-operator-panels

Procedure
General Configuration
Enter the IP address of your device in the browser to open the configuration settings.
Enable the TCP event under the menu item "System > TCP Event".
Assign a user name and password.
Specify the port number. This is specified as the destination port when the TCP connection is established.
Select "VPN" as the event.
Confirm your configuration with "Set Values".
VPN connection on a SCALANCE M800 / S615 via TCP VPN connection on a SCALANCE M800 / S615 via TCP
Fig. 01

Configuration for SINEMA RC
Disable the option "Enable SINEMA RC".
Under the menu item "System > SINEMA RC" select the option "TCP Event" as "Type of connection".
Confirm your configuration with "Set Values".
Enable the option "Enable SINEMA RC".
VPN connection on a SCALANCE M800 / S615 via TCP VPN connection on a SCALANCE M800 / S615 via TCP
Fig. 02

Note
Nevertheless, the connection for the configuration change takes place immediately. Only the secured VPN connection is enabled and disabled via TCP event.

Configuration for IPSec
Navigate to the "Connections" tab under the menu item "Security > IPSec VPN".
For the "Operation" setting, select the "start on TCP" option.
Confirm your configuration with "Set Values".
VPN connection on a SCALANCE M800 / S615 via TCP VPN connection on a SCALANCE M800 / S615 via TCP
Fig. 03

Configuration for OpenVPN
Proceed in the same way as described for IPSec. The setting is available under "Security > OpenVPN".
VPN connection on a SCALANCE M800 / S615 via TCP VPN connection on a SCALANCE M800 / S615 via TCP
Fig. 04
Note
This option cannot yet be executed for OpenVPN with firmware V7.2, the function will be delivered with the new version.

Structure of the TCP packet
To use the TCP event, you must establish a TCP connection with the IP address of the device and the configured destination port.
The TCP packet is bound to a fixed syntax with the following structure:
“Username”#”Password”#”Command Code”#”VPN Type”;”Activate/Deactivate”; “Connection”

Parameter Value range
Username Pre-configured user name
Password Pre-configured password
Command Code Must be 108 for the VPN connection
VPN Type 1 (IPSec), 2 (OpenVPN), 3 (SINEMA RC)
Activate/Deactivate 1 (Activate), 2 (Deactivate)
Connection Connection Name, * (All Connections)

Example
Username: admin
Password: password
Command Code: 108
VPN Type: OpenVPN
Activate/Deactivate: Activate
Connection: All Connections
TCP Packet: admin#password#108#2;1;*
Note
There is no response from the device via the TCP connection.

Further Information
https://support.industry.siemens.com/cs/document/109815243/wlan-roaming-with-scalance-wum-via-tcp
https://support.industry.siemens.com/cs/attachments/109815243/109815243_WLAN_Roaming_V10_en.pdf
https://support.industry.siemens.com/cs/attachments/109815243/ScalanceW_TriggeredRoaming.zip
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> Simatic Automation Systems All times are GMT + 2 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group
Fa-ti si tu propriul forum GRATUIT, pe www.myforum.ro