drendgrave Junior

Joined: 03 Mar 2016 Posts: 11
|
Posted: 28/03/2016 22:40 Post subject: STARTUP Sinamic s120 |
|
|
Good afternoon! The problem arose from the ground up to configure the drive Sinamics s120. Installed Control Unit CU320-2DP + with the card (firmware 4.3.2) + Smart Line Module + Single Motor Module. Zakonnektili through Drive-Qlick. Filed postoyanku 24V loop 3 module. Force applied. Inserted BOP20 control panel.
Finally we got:
- The BOP20 control panel displays nothing - blank screen;
- On the Control Unit CU320-2DP block RDY COM blinking red light 0.5 Hz;
- On the other blocks are red RDY.
Lord, if any thoughts on the case? Thank you. |
|
| Back to top |
|
 |
vakon Member junior

Joined: 13 Feb 2016 Posts: 66
|
Posted: 29/03/2016 19:39 Post subject: Re: STARTUP Sinamic s120 |
|
|
| drendgrave wrote: | Good afternoon! The problem arose from the ground up to configure the drive Sinamics s120. Installed Control Unit CU320-2DP + with the card (firmware 4.3.2) + Smart Line Module + Single Motor Module. Zakonnektili through Drive-Qlick. Filed postoyanku 24V loop 3 module. Force applied. Inserted BOP20 control panel.
Finally we got:
- The BOP20 control panel displays nothing - blank screen;
- On the Control Unit CU320-2DP block RDY COM blinking red light 0.5 Hz;
- On the other blocks are red RDY.
Lord, if any thoughts on the case? Thank you. |
Do you have the project or try an initial commissioning with no project?
First of all.. can you boot correctly?
Try to boot:
while booting COM LED = OFF and RDY LED=ORANGE
After reboot if COM LED is flashing 0.5Hz then check MMC and FW version or if not corrupt.
Remedy: Change MMC with the proper firmware
Behavior of the LEDs in the operating state
If COM LED is flashing 0.5Hz you have problem with PROFIBUS ..cables, CU Address....
Remedy:Verify PROFIBUS Connection, address.....
CHECK PROFIBUS PINOUT
Check this manuals
Getting started
https://cache.industry.siemens.com/dl/files/202/99742202/att_872533/v1/GS1_042014_eng_en-US.pdf
Commissioning Manual
https://cache.industry.siemens.com/dl/files/069/26547069/att_91534/v1/IH1_112009_eng_en-US.pdf
https://cache.industry.siemens.com/dl/files/725/109478725/att_853873/v1/GH1_0415_eng_en-US.pdf
Off the record:
If BOP is dead check if your Sinamics is defective?????
But probably is better to explain step by step
What happens with LEDs exactly on booting?
Is boot process terminated correctly? |
|
| Back to top |
|
 |
vakon Member junior

Joined: 13 Feb 2016 Posts: 66
|
Posted: 29/03/2016 19:53 Post subject: |
|
|
By the way..when you are booting CU230-2DP try to disconnect PROFIBUS cable from PG.
The firmware must be v4.3 or higher.
If this step goes well then pass to the next step otherwise will not working anything. |
|
| Back to top |
|
 |
vakon Member junior

Joined: 13 Feb 2016 Posts: 66
|
Posted: 29/03/2016 20:24 Post subject: |
|
|
look
if you have not a ready project try to use only for check initial functioning
https://support.industry.siemens.com/cs/document/29056318/sinamics-s%3A-safety-control-of-a-s120-using-s7-300-400-%28step-7-v5%29-with-profibus-and-safety-integrated-%28via-profisafe%29
V2.0 (for SINAMICS V4.4) use starter project
https://support.industry.siemens.com/cs/attachments/29056318/29056318_MC_FE_I_006_V20_en.pdf
https://support.industry.siemens.com/cs/attachments/29056318/MC_FE_I_006_V20.zip |
|
| Back to top |
|
 |
drendgrave Junior

Joined: 03 Mar 2016 Posts: 11
|
Posted: 29/03/2016 22:47 Post subject: |
|
|
1 This initial commissioning still without project
2. Sorry! On the Control Unit CU320-2DP block RDY COM blinking red light 2 Hz - From the very first moment of switching on the drive. After the first inclusion have checked the card via the card reader. There was on the card only a text file with a litsenzioony key more than nothing..! The card is new.
3.Process of loading wasn't. All blocks new.BOP-20 perhaps has to be activated only after successful loading FIRMWARE from the CFC.
4.I tried to connect through LAN, PROFIBUS and RS232. No effect.
5.FW 4.3.2 i not finded. |
|
| Back to top |
|
 |
vakon Member junior

Joined: 13 Feb 2016 Posts: 66
|
Posted: 30/03/2016 21:15 Post subject: |
|
|
| drendgrave wrote: | 1 This initial commissioning still without project
2. Sorry! On the Control Unit CU320-2DP block RDY COM blinking red light 2 Hz - From the very first ocazie of switching on the drive. After the first inclusion have checked the card via the card reader. There was on the card only a text file with a litsenzioony key more than nothing..! The card is new.
3.Process of loading wasn't. All blocks new.BOP-20 perhaps has to be activated only after successful loading FIRMWARE from the CFC.
4.I tried to connect through LAN, PROFIBUS and RS232. No effect.
5.FW 4.3.2 i not finded. |
Dear drendgrave,
look how you have to proceed:
Preconditions:
Any hardware release of the CU320-2DP with order number 6SL3040-1MA00-0AA0 can be upgraded to device version V4.6 /V4.7.
The CU320-2 PN with order number 6SL3040-1MA01-0AA0 is supported by firmware version V4.4 and higher.
Firmware versions of V4.3.x or higher can only be installed on 1GB or 2GB1 CompactFlash cards
If you do not have this then STOP but if yes proceed as follows:
-Reader for CompactFlash cards connected to a PC/PG
-PC/PG with STARTER Version >= 4.3.x incl. appropriate SSP for new firmware version
-Communication interface to the Control Unit (see manuals)
So
1. SWITCH OFF THE ELECTRONIC POWER SUPPLY
Disconnect the power supply from the Control Unit (including the 24 V DC supply)
2. Extract de CF CARD from CU230-DP and INSERT THE CF CARD IN THE READER FOR THE PC / PG
3. Back it up (copy) using the Windows Explorer on the PC/PG on a Folder.
Remember: This folder contains license keys for software options under license and do not delete by mistake.
4. Then ...Delete all files and folders from the CompactFlash card using Windows Explorer on the PC.
5. Extract the new firmware from the zip file using an unzip application, e.g. WINZIP, WINRAR (here you can uise V4.4 which can be downloaded from forum..to any temporary directory of your choice on the PC/PG.
6. COPY NEW FIRMWARE (ALL FOLDERS) TO THE CF CARD
Use Windows Explorer to move the contents of the temporary directory to the CompactFlash card
(The appropriate SSP for the firmware is stored in subdirectory ADDON\SINAMICS\ES_TOOL\SSP in the zip file containing the new firmware)
7. Use Windows Explorer to move the KEYS folder from the anterior folder where you saved the License from the PC/PG to the main directory on the CompactFlash card.
8.If you have aproject is now the time to copy to CF Card but if you have not go to the next step
9. Extras the CF Card from Laptop Eriter/Reader and insert the CompactFlash card into the CU320-2 Control Unit
10. Reconnect the power supply to the Control Unit (including the 24 V DC supply)
11. With firmware version V4.3.x and later, the firmware of the integrated components is updated automatically.
During this process, the RDY (READY) LED on the Control Unit flashes orange at a frequency of 0.5 Hz.
When the firmware update process is complete, the LED flashes faster at 2 Hz.
12. When the update process is complete, restart the Control Unit by switching the power supply off and then on again.
Then tell me what happened... |
|
| Back to top |
|
 |
vakon Member junior

Joined: 13 Feb 2016 Posts: 66
|
Posted: 30/03/2016 22:20 Post subject: |
|
|
download v4.4 from
http://plc.myforum.ro/sinamics-firmware-all-vt6998.html |
|
| Back to top |
|
 |
drendgrave Junior

Joined: 03 Mar 2016 Posts: 11
|
Posted: 30/03/2016 22:28 Post subject: STARTUP Sinamic s120 |
|
|
Thanks for the help! Only it's all been tried with different firmware (4.4 -4.7). LEDs as a blinking red light 2 Hz, and blink.
Communication between the PC and SU 320-2vz possible only after avtozagruzkiPO with cards, I think so. |
|
| Back to top |
|
 |
drendgrave Junior

Joined: 03 Mar 2016 Posts: 11
|
Posted: 30/03/2016 22:34 Post subject: STARTUP Sinamic s120 |
|
|
| Perhaps the license is tied to the number and firmware update firmware sous possible after flashing the old license. |
|
| Back to top |
|
 |
rott Senior

Joined: 23 Aug 2011 Posts: 2266
|
Posted: 31/03/2016 19:17 Post subject: Re: STARTUP Sinamic s120 |
|
|
| drendgrave wrote: | | Perhaps the license is tied to the number and firmware update firmware sous possible after flashing the old license. |
Download and install S7 technology.
Try to connect from Simatic Manager.
http://plc.myforum.ro/viewtopic.php?p=21232#21232
However for knowing exactly the compatibility please send the Siemens' codes for CF Card and CU230-2DP
Good luck. |
|
| Back to top |
|
 |
drendgrave Junior

Joined: 03 Mar 2016 Posts: 11
|
Posted: 31/03/2016 22:37 Post subject: |
|
|
| Quote: | | Download and install S7 technology. |
If SIMATIC S7? It is already established. Through him I tried on a Profibus. There is no effect. |
|
| Back to top |
|
 |
drendgrave Junior

Joined: 03 Mar 2016 Posts: 11
|
Posted: 31/03/2016 23:06 Post subject: STARTUP Sinamic s120 |
|
|
6SL3054-0TA01-1BA0 - kard
6SL3040-1MA00-0AA0 - Control unit |
|
| Back to top |
|
 |
rott Senior

Joined: 23 Aug 2011 Posts: 2266
|
Posted: 01/04/2016 16:33 Post subject: Re: STARTUP Sinamic s120 |
|
|
| drendgrave wrote: | 6SL3054-0TA01-1BA0 - kard
6SL3040-1MA00-0AA0 - Control unit |
How can you replace the SINAMICS CU320 with the CU320-2 in a Technology CPU project with S7 Technology?
As from version V4.2 SP1 of S7 Technology you have the option of automatically replacing the SINAMICS device version and characteristic in an existing S7 Technology project.
https://support.industry.siemens.com/cs/document/58805543/how-can-you-replace-the-sinamics-cu320-with-the-cu320-2-in-a-technology-cpu-project-with-s7-technology
Mark the required SINAMICS drive in the tree view and select the pop-up menu "Target device > Upgrade device version/characteristic". \
Then select the required characteristic from the list of available SINAMICS characteristics.
Then select the required firmware version from the list of available device versions.
Finally, click the "Upgrade" button to replace the SINAMICS control unit in the S7 Technology project with the version selected.
For being successful with the following hardware:
6SL3054-0TA01-1BA0
SINAMICS S120 CF card V4.3 SP2 perform.
SINAMICS S120 COMPACTFLASH CARD WITH FIRMWARE OPTION PERFORMANCE-EXTENSION 1 INCLUDING CERTIFICATE OF LICENCE V4.3 SP2
6SL3040-1MA00-0AA0
SINAMICS S120 CONTROL UNIT CU320-2 PB
SINAMICS CONTROL UNIT CU320-2 DP WITH PROFIBUS INTERFACE WITHOUT COMPACT FLASH CARD.
The SINAMICS Control Unit CU320-2 DP (6SL3040-1MA00-0AA0) is not supported by S7-Technology up to and including version V4.1 SP1. It is only possible to configure this SINAMICS Control Unit as from version V4.2.
proceed:
Download S7 Technology V4.2.
https://userscloud.com/y881qfpya8gf/SIMATIC_Technology_V4.2.part01.rar
https://userscloud.com/z6v68cxteji8/SIMATIC_Technology_V4.2.part02.rar
https://userscloud.com/8h96qpn6hmu3/SIMATIC_Technology_V4.2.part03.rar
https://userscloud.com/kkooqwlr52oz/SIMATIC_Technology_V4.2.part04.rar
https://userscloud.com/hj4j1qwqtwgc/SIMATIC_Technology_V4.2.part05.rar
https://userscloud.com/xovmn1g98dgu/SIMATIC_Technology_V4.2.part06.rar
https://userscloud.com/y00fo6vanrvv/SIMATIC_Technology_V4.2.part07.rar
https://userscloud.com/5qs5f6xz65ru/SIMATIC_Technology_V4.2.part08.rar
https://userscloud.com/n8sagx0pe127/SIMATIC_Technology_V4.2.part09.rar
https://userscloud.com/z6vimyeg3ipg/SIMATIC_Technology_V4.2.part10.rar
https://userscloud.com/p56htirhi71k/SIMATIC_Technology_V4.2.part11.rar
https://userscloud.com/hxn4y0g2qln3/SIMATIC_Technology_V4.2.part12.rar
https://userscloud.com/qdhkslczjuoa/SIMATIC_Technology_V4.2.part13.rar
https://userscloud.com/1y9sy6oxuvpg/SIMATIC_Technology_V4.2.part14.rar
https://userscloud.com/umz1na9flhz6/SIMATIC_Technology_V4.2.part15.rar
https://userscloud.com/qk42lz7vczve/SIMATIC_Technology_V4.2.part16.rar
https://userscloud.com/o8olrbnear7v/SIMATIC_Technology_V4.2.part17.rar
https://userscloud.com/t2lwd1zp1tlx/SIMATIC_Technology_V4.2.part18.rar
https://userscloud.com/s1oj5jarqbh1/SIMATIC_Technology_V4.2.part19.rar
Apply upgrade to S7 Technology V4.2 SP1 or higher
https://userscloud.com/mbhl356j5dah/S7_Technology_V42_SP1.part01.rar
https://userscloud.com/b0gze39xx9is/S7_Technology_V42_SP1.part02.rar
https://userscloud.com/f6piwclqv898/S7_Technology_V42_SP1.part03.rar
https://userscloud.com/5snurjfo9e8e/S7_Technology_V42_SP1.part04.rar
https://userscloud.com/ul785kzfphde/S7_Technology_V42_SP1.part05.rar
https://userscloud.com/etzze59rt68j/S7_Technology_V42_SP1.part06.rar
https://userscloud.com/0t62cnkctb6d/S7_Technology_V42_SP1.part07.rar
https://userscloud.com/9qqv9nt5mzgs/S7_Technology_V42_SP1.part08.rar
https://userscloud.com/vz216rdkvp03/S7_Technology_V42_SP1.part09.rar
https://userscloud.com/3e6igei3j2b7/S7_Technology_V42_SP1.part10.rar
Copy the firmware on Flashcard (unrar the file from file inside and copy to CF plus copy the license )
https://userscloud.com/h03e2q6bqwza/sinamics_s120_firmware_V4.3.2.rar
Insert on CU and main supply up (could be only the +24V DC Supply) and ..hope it works... try to connect and
good luck.
You can eventually upgrade firmware later than 4.3.2 if required
other firmware find on
https://userscloud.com/tfvurdc2rbgz/sinamics_s120_firmware_v2.4.1.rar
https://userscloud.com/tupkrfrzzpwy/sinamics_s120_firmware_V2.5.1.14.rar
https://userscloud.com/f4x3rc6afige/sinamics_s120_firmware_V2.5.1.16.rar
https://userscloud.com/3jc7gvouv01o/sinamics_s120_firmware_V2.5.1.rar
https://userscloud.com/psmbfwvno00j/sinamics_s120_firmware_V2.6.2.0.rar
https://userscloud.com/rou026ewa4jp/sinamics_s120_firmware_V2.6.2.13.rar
https://userscloud.com/y7fv2y8vi80j/sinamics_s120_firmware_V2.6.2.7.rar
https://userscloud.com/9arzh0chfbfo/sinamics_s120_firmware_V2.6.2.rar
https://userscloud.com/8vdxn86cgs6k/sinamics_s120_firmware_V4.4.0.4.rar
https://userscloud.com/trobv5t582hj/sinamics_s120_firmware_V4.5.0.2.rar
With the SP2, S7-Technology V4.2 will support the following
| Code: |
MICROMASTER 4st generation
SINAMICS DCM with firmware V1.1, V1.2 and V1.3
SIMATIC ET200S FC with firmware V1.0.x and V3.0.x
SIMATIC ET200pro FC with firmware V3.0.x
SINAMICS G110 with firmware V1.0.x and V1.1.x
SINAMICS G110D with firmware V3.3.x and V3.4
SINAMICS G120 with firmware V2.0.x, V2.1.x, V3.0.x, V3.1.x, V3.2.x, V4.2,V4.3.0, V4.3.2, V4.4 and V4.5
SINAMICS G120C with firmware V4.4 and V4.5
SINAMICS G120D with firmware V3.0.x, V3.1.x, V3.2.x and V4.5
SINAMICS G120P with firmware V4.2, V4.3.0, V4.3.2, V4.4 and V4.5
SINAMICS G120P BT with firmware V4.4.1 and V4.5
SINAMICS G130 with firmware V2.1.x, V2.2.x, V2.3.x, V2.4.x, V2.5.1, V2.6.1 and V2.6.2
SINAMICS G130 with firmware V4.3.1, V4.3.2, V4.4 and V4.5
SINAMICS G150 with firmware V2.1.x, V2.2.x, V2.3.x, V2.4.x, V2.5.1, V2.6.1 and V2.6.2
SINAMICS G150 with firmware V4.3.1, V4.3.2, V4.4 and V4.5
SINAMICS GM150 with firmware V2.5.1, V2.6.1 and V2.6.2
SINAMICS GM150 with firmware V4.3.1, V4.4.2 and V4.5
SINAMICS GL150 with firmware V2.5.1, V2.6.1 and V2.6.2
SINAMICS GL150 with firmware V4.3.1, V4.4.2 and V4.5
SINAMICS S110 with firmware V4.1, V4.3.1, V4.3.2 and V4.4
SINAMICS S120 with firmware V2.1.x, V2.2.x, V2.3.x, V2.4.x, V2.5.1, V2.6.1 and V2.6.2
SINAMICS S120 with firmware V4.3.1, V4.3.2, V4.4 and V4.5
SINAMICS S150 with firmware V2.1.x, V2.2.x, V2.3.x, V2.4.x, V2.5.1, V2.6.1 and V2.6.2
SINAMICS S150 with firmware V4.3.1, V4.3.2, V4.4 and V4.5
SINAMICS SL150 with firmware V4.3.1 V4.4.2 and V4.5
SINAMICS SM150 with firmware V4.4.2
SINAMICS SM150i with firmwareV2.4.x, V2.5.1, V2.6.2 and V4.5
SINAMICS MV with firmware V4.5 |
You can work also with STARTER 4.3.1 you probably working.
If you do not have please let me know.
PS:
I've read your posting on PM.
Try however to install Technology 4.2 because from Simatic Manager you can test more options for connecting using this environment.
It could be another problem....
What version of Simatic NET do you use because the latest versions exclude some CPs like CP5611 and older from support on communications.
Normally you have to use Step7 any version, Simatic NET until V8.0 with upgrades.
What CP do you use on your PG?
try to load v4.3.2 firmware and if do not work you have a big problem with CU230. |
|
| Back to top |
|
 |
drendgrave Junior

Joined: 03 Mar 2016 Posts: 11
|
Posted: 01/04/2016 23:09 Post subject: STARTUP Sinamic s120 |
|
|
Thanks a lot for so substantial answer. I use a STARTER version 4.4.1.
I tried to connect through LAN, PROFIBUS and RS232. No effect.
I will report about results on your recommendations. |
|
| Back to top |
|
 |
drendgrave Junior

Joined: 03 Mar 2016 Posts: 11
|
Posted: 02/04/2016 12:04 Post subject: STARTUP Sinamic s120 |
|
|
Hi! I think:
1. initially the control unit is delivered from plant without insertion;
2. communication(LAN-cross cabel, PROFIBUS- adapter MPI/,RS232) in online between the notebook r and the control unit is possible only after loading of an insertion RDY=ON RED, COM and OPT=OFF. |
|
| Back to top |
|
 |
rott Senior

Joined: 23 Aug 2011 Posts: 2266
|
Posted: 02/04/2016 15:22 Post subject: Re: STARTUP Sinamic s120 |
|
|
| drendgrave wrote: | Hi! I think:
1. initially the control unit is delivered from plant without insertion;
2. communication(LAN-cross cabel, PROFIBUS- adapter MPI/,RS232) in online between the notebook r and the control unit is possible only after loading of an insertion RDY=ON RED, COM and OPT=OFF. |
Connect with an Ethernet crossover cable CU with your PG
Assign to PG/PC IP address 169.254.11.1 /255.255.0.0
Set PG Interface to TCPIP...and eventually restart PC
The factory setting of the internal Ethernet interface X127 of the Control Unit is 192.254.11.22 for this type of CU.
Apply +24VDC to CU click online interface in STARTER.
Run Command Prompt Start->Programs->Accessories and and command >/...../..>ping tell me what you see?
If you need to put another address you can use PST (Primary Setup Tool)
Assigning the IP address and the name via STARTER or PST (node initialization).
The Ethernet interface must be initialized so that the STARTER can establish communication. Selecting online mode in STARTER
You can use the PST initialization tool (Primary Setup Tool) to assign an IP address and a name to the Ethernet interface.
�œ Connect the PG/PC and CU 320-2 using an Ethernet cable.
�œ Switch on the Control Unit.
�œ Start the Primary Setup Tool (on the STARTER CD).
�œ Settings -> Network card -> Select the network card
�œ Network -> Search (or F5)
�œ Select the Ethernet device -> Module -> Assign name -> Enter the station name -> OK
�œ Module -> Load
�œ Network -> Search (or F5)
�œ Select "Int. Ethernet interface" under the Ethernet device -> Assign IP address -> Enter
the IP address (factory setting 169.254.11.22) -> Enter the subnet mask (255.255.0.0).
The subnet masks must match before STARTER can be run.
�œ Module -> Load
Note
The IP address and device name for the Control Unit are stored on the memory card (nonvolatile).
Tell me what you see after ping....
By the way..what adapter do you use for PROFIBUS between PG and CU? |
|
| Back to top |
|
 |
drendgrave Junior

Joined: 03 Mar 2016 Posts: 11
|
Posted: 04/04/2016 09:31 Post subject: STARTUP Sinamic s120 |
|
|
Good day!
If the connection is possible, if the red LED flashes where from 2 Hz?
Thank. |
|
| Back to top |
|
 |
rott Senior

Joined: 23 Aug 2011 Posts: 2266
|
Posted: 04/04/2016 20:55 Post subject: Re: STARTUP Sinamic s120 |
|
|
| drendgrave wrote: | Good day!
If the connection is possible, if the red LED flashes where from 2 Hz?
Thank. |
Now I'm in a different location.
If you can wait few days I'll upload an image of CF for Sinamics S120. |
|
| Back to top |
|
 |
zurek17 Junior

Joined: 13 Apr 2016 Posts: 4 Location: Polska
|
Posted: 05/09/2016 14:04 Post subject: |
|
|
Hello,
Is it posssible to upload CF image for CU320? |
|
| Back to top |
|
 |
rott Senior

Joined: 23 Aug 2011 Posts: 2266
|
Posted: 16/10/2016 19:28 Post subject: |
|
|
| zurek17 wrote: | Hello,
Is it posssible to upload CF image for CU320? |
Be careful on handling licenses and firmware version on CF card.
You can use the Prameter 990x of the Control Unit to acknowledge the topology differences (that is, take serial number as a new target) and then save it back to the card.
| Code: | *** SINAMICS CF_M_S120 V04.05.00.29 (internal version V04.50.30.43) ***
- Unit Description V04.50.30.43
- UFTAB LV V04.50.30.43
- Firmware CU320/2-S120 (Release) V04.50.30.43
SI V04.50.30.34
SI-MM V04.50.30.41
- Text Description V04.50.30.43
- SYSTEM Description CU320/2 V04.50.30.43
- Realtime measurement CU320/2 V04.50.30.43
- Repository Italian PM S120 V04.50.30.43
- Repository French PM S120 V04.50.30.43
- Repository Spanish PM S120 V04.50.30.43
- Repository English PM S120 V04.50.30.43
- Repository German PM S120 V04.50.30.43
- Repository Chinese PM S120 V04.50.30.43
- Parameter Macros S120 V04.50.30.43
- PERFORMANCE V04.50.30.43
- Miscellaneous Text description V04.50.30.43
- Miscellaneous Repository Italian V04.50.30.43
- Miscellaneous Repository French V04.50.30.43
- Miscellaneous Repository Spanish V04.50.30.43
- Miscellaneous Repository English V04.50.30.43
- Miscellaneous Repository German V04.50.30.43
- Miscellaneous Repository Chinese V04.50.30.43
- Motordaten V04.50.30.43
- Memory allocation CU320/2 V04.50.30.43
- Repository Italian V04.50.30.43
- Repository French V04.50.30.43
- Repository Spanish V04.50.30.43
- Repository English V04.50.30.43
- Encoderdaten V04.50.30.43
- Repository German V04.50.30.43
- Repository Chinese V04.50.30.43
- Common files V04.50.30.43
- BICO V04.50.30.43
- Lagerdaten V04.50.30.43
- Delta PD V04.50.30.43
- Busprojektierung Profinet V04.50.30.43
- FW Voltage Sensing Module VSM10 (vsm.ufw) V04.50.30.31
- FW Terminal Module TM17 (tm17.ufw) V04.50.30.31
- FW Terminal Module TM15 (tm15.ufw) V04.50.30.31
- FW Sensor Module SMI20/SMExx, 6SL..0 (smi20x.ufw) V04.50.30.31
SI-MM V02.40.06.00
- FW Sensor Module SMI10, 6SL..0 (smi10x.ufw) V04.50.30.31
- FW Sensor Module SMC20, 6SL..1 (smc20x.ufw) V04.50.30.31
SI-MM V02.40.06.00
- FW Sensor Module SMC10, 6SL..0 (smc10x.ufw) V04.50.30.31
- OA-FBLOCKS CU320/2 Firmware (Release) V04.50.30.43
- OA-FBLOCKS Text Description Merge V04.50.30.43
- OA-FBLOCKS Text Description V04.50.30.43
- OA-FBLOCKS SD Merge CU320/2 V04.50.30.43
- OA-FBLOCKS System Description V04.50.30.43
- OA-FBLOCKS Repository Italian V04.50.30.43
- OA-FBLOCKS Repository French V04.50.30.43
- OA-FBLOCKS Repository Spanish V04.50.30.43
- OA-FBLOCKS Repository English V04.50.30.43
- OA-FBLOCKS Repository German V04.50.30.43
- OA-FBLOCKS Repository Chinese V04.50.30.43
- OA-FBLOCKS PD 000 V04.50.30.43
- OA-FBLOCKS Delta PD V04.50.30.43
- DCC Components V04.50.30.43
- GSD Profinet V04.50.30.43
- GSD Profibus Repository Italian V04.50.30.43
- GSD Profibus Repository French V04.50.30.43
- GSD Profibus Repository Spanish V04.50.30.43
- GSD Profibus Repository English V04.50.30.43
- GSD Profibus (+ Repository German) V04.50.30.43
- FW Sensor Module SMC10/SMI10, 6SL..3 (smx10d.ufw) V04.50.30.40
- FW Sensor Module SMI24, 6SL..3 (smi24d.ufw) V04.50.30.37
SI-MM V04.50.19.00
- FW Sensor Module SMI20/SMExx, 6SL..3 (smi20f.ufw) V04.70.35.08
SI-MM V04.70.02.00
- FW Sensor Module SME12x, 6SL..3 (sme12f.ufw) V04.70.35.08
SI-MM V04.70.02.00
- FW Sensor Module SMC20, 6SL..3 (smc20f.ufw) V04.70.35.08
SI-MM V04.70.02.00
- FW Decentral MM with TM function, S120M (s120m.ufw) V04.50.30.40
- FW Hub Module DME20 (dme20.ufw) V04.50.30.40
- FW PM340-Adapter D410 / CU310-2 (cu31x2.ufw) V04.50.30.40
SI V04.50.30.05
SI-MM V04.50.30.30
- FW Voltage Sensing Module VSM10 (vsm10d.ufw) V04.50.30.40
- FW Terminal Module TM54F (tm54f.ufw) V04.50.30.40
SI-MM V04.50.22.00
- FW Terminal Module TM41 (tm41d.ufw) V04.50.30.40
- FW Terminal Module TM31 (tm31d.ufw) V04.50.30.40
- FW Terminal Module TM150 (tm150.ufw) V04.50.30.40
- FW Terminal Module TM120 (tm120.ufw) V04.50.30.40
- FW Sensor Module SMC30 (smc30f.ufw) V04.50.30.40
- FW Chassis-MoMo / ALM / BLM / SLM (psad.ufw) V04.50.30.40
SI V04.50.30.05
SI-MM V04.50.30.30
- FW Chassis-MoMo / ALM / BLM / SLM (psadf.ufw) V04.50.30.40
SI V04.50.30.05
SI-MM V04.50.30.30
- FW Hub Module DMC20 (dmc20.ufw) V04.50.30.40
- FW PM340-Adapter CUA32 (cua32.ufw) V04.30.28.00
SI V04.30.14.00
SI-MM V04.30.15.00
- FW PM340-Adapter CUA32X (cua32x.ufw) V04.50.30.40
SI V04.50.30.05
SI-MM V04.50.30.30
- FW PM340-Adapter CUA31 (cua31x.ufw) V04.40.23.13
SI V04.40.23.04
SI-MM V04.40.23.04
- FW PM340-Adapter CUA31 (cua31f.ufw) V04.50.30.40
SI V04.50.30.05
SI-MM V04.50.30.30
- FW Booksize SMM / ALM / BLM / SLM (abo.ufw) V04.50.30.40
SI V04.50.30.05
SI-MM V04.50.30.30
- FW Booksize SMM / ALM / BLM / SLM (abohf.ufw) V04.50.30.40
- FW Booksize DMM (abo2.ufw) V04.50.30.40
SI V04.50.30.05
SI-MM V04.50.30.30
- CBE20_4 PROFINET V13.01.38.00
- CBE20_3 PROFINET V13.01.33.00
- CBE20_2 PROFINET V13.01.53.00
- CBE20_1 PROFINET V13.01.33.00
- AOP Firmware SOC2 V04.05.16.00 |
[URL=https://userscloud.com/13rtyr1sr5uh]SINAMICS CF_M_S120 V04.05.00.29.img - 977.5 MB[/URL] |
|
| Back to top |
|
 |
|