Solved: OPC syntax for direct reading from Siemens drives

 
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> Drives & Inverters
View previous topic :: View next topic  
Author Message
SKV77
Junior
Junior


Joined: 03 Aug 2024
Posts: 8

PostPosted: 25/12/2024 20:31    Post subject: Solved: OPC syntax for direct reading from Siemens drives Reply with quote

Solved: Tag syntax for direct reading parameters from Siemens drives to OPC via Profibus

Drives: Simoreg 6RA70, Simovert 6SE70, MicroMaster 4, Simodrive POSMO, Sinamics G120/S120.

1) Reading of parameters from any Siemens drive with ProfiDrive.ProfilServer
Software: [Simatic Net 2008 + ProfilServer from Lenze Engineer] or Simatic Net 2005 (OPC does not work with Drive Monitor 5.4.2, but ProfilServer included)
OPC: ProfiDrive.ProfilServer

Tag syntax examples:
OPC_SimaticNET_PD/DP2___brd2_seg0_dev3_/ParI13D2
OPC_SimaticNET_PD/DP2___brd2_seg0_dev3_/ParI964S0D2

brd2 = CP Profibus in slot 2 of Station Configuration Editor
seg0 = always 0
dev3 = drive DP-address

ParI13 = parameter r13, no indexes
ParI964S0 = parameter r964.1 (S0 =Index 1, S1 =Index 2, …)
D2 = data type Signed Integer16
Table of data types in Simatic Net Manual 2005_Vol.2 «mn_opc2_76», page 68.

2) Reading of parameters from G120 (from FW 4.6)/S120 with Unspecified S7 Connection
Unspecified S7 Connection must be created in Net Pro for OPC server.
OPC: OPC.SimaticNet

Tag syntax example:
S7:[S7 connection_1]DB2,W1024,1

S7 connection_1 = accurate name of S7 connection
DB2 = parameter r2
W = data type Unsigned Integer16
1024 = axis * offset 1024 + index = 1*1024+0
(S120 included up to 4 axises)
Table of data types in Simatic Net Manual 2005_Vol.2 «mn_opc2_76», page 89.

3) Reading cyclical PZD words from any Siemens drive
Drive must be added on bus in HW Config, in drive slot 1 - PKW module, in drive slot 2 - Universal module with defined Input address area (up to 16 words).
OPC: OPC.SimaticNet

Tag syntax example:
DP:[CP 5611]Slave3_EW8,1

CP 5611 = accurate name of CP Profibus
Slave3 = drive DP-address
E (or I) = Input area
W = data type Unsigned Integer16
8 = addressing: word PZD1 started from byte 8 (PZD1 =8, PZD2 =10, ..., PZD16 =38)
Here is possible flexible reading of any bit, byte, word, dword.
Table of data types in Simatic Net Manual 2005_Vol.2 «mn_opc2_76», page 31.
**
- Last Drive Monitor 5.5.2 has not connection via OPC. Drive Monitor 5.4.2 has it.
- Only one identity of Drive Monitor can be running at the PC.
- Drive Monitor can connect via USS (COM1..4), via OPC.SimaticNet.PD (Profibus, Access point S7 Online = PC internal), and via Profibus (opening from Simatic Manager + Drive ES, Access point S7 Online = Profibus).
- To one drive can simultaneously connect 2 PCs with Drive Monitor: PC1 via USS, PC2 via OPC.SimaticNet.PD or via Profibus.
- All listed Siemens drives can directly connect with Simatic OP paneles via Profibus. Addresing is similar with OPC Unspecified S7 connection, but without offset 1024.
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> Drives & Inverters All times are GMT + 2 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group
Fa-ti si tu propriul forum GRATUIT, pe www.myforum.ro