PostPosted: 17/03/2017 00:33    Post subject: SICAM PAS Alarm logging Reply with quote

Hello

I am trying to add alarm logging to my project in SCC.

I have imported tags from PAS. Now I have tags and messages in "AS Messages". A tag is automatically assigned for triggering alarms. "MSG_Queue_1013" with the type of "Raw data type" (Attached picture) Where can I modify this tag to define values that should trigger my tags?

Is there anything in PAS to define Trigger values or I have to modify MSG_Queue_1013 with a function in SCC?

[img]https://ibb.co/jgsGrF[/img]
[url]https://ibb.co/jgsGrF[/url]
Back to top
View user's profile Send private message
tekla
Junior
Junior


Joined: 06 Mar 2017
Posts: 11

PostPosted: 18/03/2017 15:30    Post subject: Re: SICAM PAS Alarm logging Reply with quote

milad2002b wrote:
Hello

I am trying to add alarm logging to my project in SCC.

I have imported tags from PAS. Now I have tags and messages in "AS Messages". A tag is automatically assigned for triggering alarms. "MSG_Queue_1013" with the type of "Raw data type" (Attached picture) Where can I modify this tag to define values that should trigger my tags?

Is there anything in PAS to define Trigger values or I have to modify MSG_Queue_1013 with a function in SCC?

[img]https://ibb.co/jgsGrF[/img]
SICAM PAS Alarm logging SICAM PAS Alarm logging


Messages that communicate via raw data tags with the AS (Format DLL) are shown in the "AS messages" and are automatically generated by the processor.
For a specific tag you must define in Alarm logging on the specified Driver the tags you need.


Last edited by tekla on 19/03/2017 14:30; edited 1 time in total
Back to top
View user's profile Send private message
milad2002b
Junior
Junior


Joined: 04 Oct 2016
Posts: 11

PostPosted: 18/03/2017 20:22    Post subject: Re: SICAM PAS Alarm logging Reply with quote

tekla wrote:
milad2002b wrote:
Hello

I am trying to add alarm logging to my project in SCC.

I have imported tags from PAS. Now I have tags and messages in "AS Messages". A tag is automatically assigned for triggering alarms. "MSG_Queue_1013" with the type of "Raw data type" (Attached picture) Where can I modify this tag to define values that should trigger my tags?

Is there anything in PAS to define Trigger values or I have to modify MSG_Queue_1013 with a function in SCC?

[img]https://ibb.co/jgsGrF[/img]
[url]https://ibb.co/jgsGrF[/url]


Messages that communicate via raw data tags with the AS (Format DLL) are shown in the "AS messages" and are automatically generated by the processor.
For a specific tag you must define in Alarm logging on the specified Driver the tags you need.


Thank you
I have seen in SICAM SCC demo project and other projects that they used just this tag for alarm logging (one tag for all alarms with prefix MSG_QUEUE_...)
I have another problem: All single point indications that come from SICAM PAS to SICAM SCC are 1 and 2 (instead of 0 and 1) so I must use analog alarms! How can I change PAS to have 0 and 1 for single points?
Back to top
View user's profile Send private message
sentron
Junior
Junior


Joined: 27 Dec 2016
Posts: 2

PostPosted: 19/03/2017 15:36    Post subject: Re: SICAM PAS Alarm logging Reply with quote

milad2002b wrote:
tekla wrote:
milad2002b wrote:
Hello

I am trying to add alarm logging to my project in SCC.

I have imported tags from PAS. Now I have tags and messages in "AS Messages". A tag is automatically assigned for triggering alarms. "MSG_Queue_1013" with the type of "Raw data type" (Attached picture) Where can I modify this tag to define values that should trigger my tags?

Is there anything in PAS to define Trigger values or I have to modify MSG_Queue_1013 with a function in SCC?

[img]https://ibb.co/jgsGrF[/img]
[url]https://ibb.co/jgsGrF[/url]


Messages that communicate via raw data tags with the AS (Format DLL) are shown in the "AS messages" and are automatically generated by the processor.
For a specific tag you must define in Alarm logging on the specified Driver the tags you need.


Thank you
I have seen in SICAM SCC demo project and other projects that they used just this tag for alarm logging (one tag for all alarms with prefix MSG_QUEUE_...)
I have another problem: All single point indications that come from SICAM PAS to SICAM SCC are 1 and 2 (instead of 0 and 1) so I must use analog alarms! How can I change PAS to have 0 and 1 for single points?



If you are using SICAM SCC V9.00 read how to făurite correct Alarm Logging on SCC on Manual

[URL=https://userscloud.com/u82lmhu51qnu]scc_b.pdf - 12.8 MB[/URL]

If you are using older versions then you have to produse a program in the PLC to fabricate a secondary buffer to storage the buffer of all modules, and send this buffer to WinCC via B_SEND.
In the WinCC you realizate a Raw Tag to receive this buffer and lucrate a script to analyze this tag. This script should analyze the change of messages (received by Raw Tag) and using APIs
- MSRTStartMsgService;
- MSRTCreateMsg;
- MSRTStopMsgService.
of WinCC setting the status and the timestamp of messages.
Back to top
View user's profile Send private message
milad2002b
Junior
Junior


Joined: 04 Oct 2016
Posts: 11

PostPosted: 20/03/2017 07:51    Post subject: Re: SICAM PAS Alarm logging Reply with quote

sentron wrote:
milad2002b wrote:
tekla wrote:
milad2002b wrote:
Hello

I am trying to add alarm logging to my project in SCC.

I have imported tags from PAS. Now I have tags and messages in "AS Messages". A tag is automatically assigned for triggering alarms. "MSG_Queue_1013" with the type of "Raw data type" (Attached picture) Where can I modify this tag to define values that should trigger my tags?

Is there anything in PAS to define Trigger values or I have to modify MSG_Queue_1013 with a function in SCC?

[img]https://ibb.co/jgsGrF[/img]
[url]https://ibb.co/jgsGrF[/url]


Messages that communicate via raw data tags with the AS (Format DLL) are shown in the "AS messages" and are automatically generated by the processor.
For a specific tag you must define in Alarm logging on the specified Driver the tags you need.


Thank you
I have seen in SICAM SCC demo project and other projects that they used just this tag for alarm logging (one tag for all alarms with prefix MSG_QUEUE_...)
I have another problem: All single point indications that come from SICAM PAS to SICAM SCC are 1 and 2 (instead of 0 and 1) so I must use analog alarms! How can I change PAS to have 0 and 1 for single points?



If you are using SICAM SCC V9.00 read how to lucrate correct Alarm Logging on SCC on Manual

[URL=https://userscloud.com/u82lmhu51qnu]scc_b.pdf - 12.8 MB[/URL]

If you are using older versions then you have to create a program in the PLC to produse a secondary buffer to storage the buffer of all modules, and send this buffer to WinCC via B_SEND.
In the WinCC you făcute a Raw Tag to receive this buffer and create a script to analyze this tag. This script should analyze the change of messages (received by Raw Tag) and using APIs
- MSRTStartMsgService;
- MSRTCreateMsg;
- MSRTStopMsgService.
of WinCC setting the status and the timestamp of messages.


Thank you for your help
Let me give you an example
For example I want to have alarm when
Relay_fail = 1
Or
OC_OPERATED =1
Or
TCS_OK=0
Where should I set these 0 and 1 values?

Thanks
Back to top
View user's profile Send private message
banguy
Member junior
Member junior


Joined: 01 Mar 2017
Posts: 59

PostPosted: 20/03/2017 11:02    Post subject: Re: SICAM PAS Alarm logging Reply with quote

milad2002b wrote:
Hello

I am trying to add alarm logging to my project in SCC.

I have imported tags from PAS. Now I have tags and messages in "AS Messages". A tag is automatically assigned for triggering alarms. "MSG_Queue_1013" with the type of "Raw data type" (Attached picture) Where can I modify this tag to define values that should trigger my tags?

Is there anything in PAS to define Trigger values or I have to modify MSG_Queue_1013 with a function in SCC?

[img]https://ibb.co/jgsGrF[/img]
[url]https://ibb.co/jgsGrF[/url]


Please upload SICAM PAS and SICAM SCC?
Back to top
View user's profile Send private message
milad2002b
Junior
Junior


Joined: 04 Oct 2016
Posts: 11

PostPosted: 20/03/2017 11:15    Post subject: Re: SICAM PAS Alarm logging Reply with quote

banguy wrote:


Please upload SICAM PAS and SICAM SCC?



SICAM SCC 8.03 and SICAM PAS 8.06

[url]https://mega.nz/#F!9V4QDaha!wKMz_LslhVTmPWL_sZpnpw[/url]

If anybody has version 9 please upload it
Back to top
View user's profile Send private message
banguy
Member junior
Member junior


Joined: 01 Mar 2017
Posts: 59

PostPosted: 22/03/2017 07:43    Post subject: Re: SICAM PAS Alarm logging Reply with quote

milad2002b wrote:
banguy wrote:


Please upload SICAM PAS and SICAM SCC?



SICAM SCC 8.03 and SICAM PAS 8.06

[url]https://mega.nz/#F!9V4QDaha!wKMz_LslhVTmPWL_sZpnpw[/url]

If anybody has version 9 please upload it


Thank you
Back to top
View user's profile Send private message
banguy
Member junior
Member junior


Joined: 01 Mar 2017
Posts: 59

PostPosted: 21/05/2018 18:35    Post subject: SICAM PAS / PQS V8.11 update Reply with quote

SICAM PAS / PQS V8.11
https://support.industry.siemens.com/cs/document/109757831/

SICAM SCC 8.03 and SICAM PAS 8.06
Code:
https://mega.nz/#F!9V4QDaha!wKMz_LslhVTmPWL_sZpnpw


Update Packages for V8.0 Installations and latest Hotfix
https://support.industry.siemens.com/cs/attachments/109757831/readme_b.pdf
https://support.industry.siemens.com/cs/attachments/109757831/SICAM_PAS_PQS_V8.xx_to_V8.11_Update.zip
https://support.industry.siemens.com/cs/attachments/109757831/SICAM_PAS_V811_SecureCom.zip
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> Simatic Automation Systems All times are GMT + 2 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group
Fa-ti si tu propriul forum GRATUIT, pe www.myforum.ro