milad2002b Junior

Joined: 04 Oct 2016 Posts: 11
|
Posted: 17/03/2017 00:33 Post subject: SICAM PAS Alarm logging |
|
|
Hello
I am trying to add alarm logging to my project in SCC.
I have imported tags from PAS. Now I have tags and messages in "AS Messages". A tag is automatically assigned for triggering alarms. "MSG_Queue_1013" with the type of "Raw data type" (Attached picture) Where can I modify this tag to define values that should trigger my tags?
Is there anything in PAS to define Trigger values or I have to modify MSG_Queue_1013 with a function in SCC?
[img]https://ibb.co/jgsGrF[/img]
[url]https://ibb.co/jgsGrF[/url] |
|
| Back to top |
|
 |
tekla Junior

Joined: 06 Mar 2017 Posts: 11
|
Posted: 18/03/2017 15:30 Post subject: Re: SICAM PAS Alarm logging |
|
|
| milad2002b wrote: | Hello
I am trying to add alarm logging to my project in SCC.
I have imported tags from PAS. Now I have tags and messages in "AS Messages". A tag is automatically assigned for triggering alarms. "MSG_Queue_1013" with the type of "Raw data type" (Attached picture) Where can I modify this tag to define values that should trigger my tags?
Is there anything in PAS to define Trigger values or I have to modify MSG_Queue_1013 with a function in SCC?
[img]https://ibb.co/jgsGrF[/img]
 |
Messages that communicate via raw data tags with the AS (Format DLL) are shown in the "AS messages" and are automatically generated by the processor.
For a specific tag you must define in Alarm logging on the specified Driver the tags you need.
Last edited by tekla on 19/03/2017 14:30; edited 1 time in total |
|
| Back to top |
|
 |
milad2002b Junior

Joined: 04 Oct 2016 Posts: 11
|
Posted: 18/03/2017 20:22 Post subject: Re: SICAM PAS Alarm logging |
|
|
| tekla wrote: | | milad2002b wrote: | Hello
I am trying to add alarm logging to my project in SCC.
I have imported tags from PAS. Now I have tags and messages in "AS Messages". A tag is automatically assigned for triggering alarms. "MSG_Queue_1013" with the type of "Raw data type" (Attached picture) Where can I modify this tag to define values that should trigger my tags?
Is there anything in PAS to define Trigger values or I have to modify MSG_Queue_1013 with a function in SCC?
[img]https://ibb.co/jgsGrF[/img]
[url]https://ibb.co/jgsGrF[/url] |
Messages that communicate via raw data tags with the AS (Format DLL) are shown in the "AS messages" and are automatically generated by the processor.
For a specific tag you must define in Alarm logging on the specified Driver the tags you need. |
Thank you
I have seen in SICAM SCC demo project and other projects that they used just this tag for alarm logging (one tag for all alarms with prefix MSG_QUEUE_...)
I have another problem: All single point indications that come from SICAM PAS to SICAM SCC are 1 and 2 (instead of 0 and 1) so I must use analog alarms! How can I change PAS to have 0 and 1 for single points? |
|
| Back to top |
|
 |
sentron Junior

Joined: 27 Dec 2016 Posts: 2
|
Posted: 19/03/2017 15:36 Post subject: Re: SICAM PAS Alarm logging |
|
|
| milad2002b wrote: | | tekla wrote: | | milad2002b wrote: | Hello
I am trying to add alarm logging to my project in SCC.
I have imported tags from PAS. Now I have tags and messages in "AS Messages". A tag is automatically assigned for triggering alarms. "MSG_Queue_1013" with the type of "Raw data type" (Attached picture) Where can I modify this tag to define values that should trigger my tags?
Is there anything in PAS to define Trigger values or I have to modify MSG_Queue_1013 with a function in SCC?
[img]https://ibb.co/jgsGrF[/img]
[url]https://ibb.co/jgsGrF[/url] |
Messages that communicate via raw data tags with the AS (Format DLL) are shown in the "AS messages" and are automatically generated by the processor.
For a specific tag you must define in Alarm logging on the specified Driver the tags you need. |
Thank you
I have seen in SICAM SCC demo project and other projects that they used just this tag for alarm logging (one tag for all alarms with prefix MSG_QUEUE_...)
I have another problem: All single point indications that come from SICAM PAS to SICAM SCC are 1 and 2 (instead of 0 and 1) so I must use analog alarms! How can I change PAS to have 0 and 1 for single points? |
If you are using SICAM SCC V9.00 read how to făurite correct Alarm Logging on SCC on Manual
[URL=https://userscloud.com/u82lmhu51qnu]scc_b.pdf - 12.8 MB[/URL]
If you are using older versions then you have to produse a program in the PLC to fabricate a secondary buffer to storage the buffer of all modules, and send this buffer to WinCC via B_SEND.
In the WinCC you realizate a Raw Tag to receive this buffer and lucrate a script to analyze this tag. This script should analyze the change of messages (received by Raw Tag) and using APIs
- MSRTStartMsgService;
- MSRTCreateMsg;
- MSRTStopMsgService.
of WinCC setting the status and the timestamp of messages. |
|
| Back to top |
|
 |
milad2002b Junior

Joined: 04 Oct 2016 Posts: 11
|
Posted: 20/03/2017 07:51 Post subject: Re: SICAM PAS Alarm logging |
|
|
| sentron wrote: | | milad2002b wrote: | | tekla wrote: | | milad2002b wrote: | Hello
I am trying to add alarm logging to my project in SCC.
I have imported tags from PAS. Now I have tags and messages in "AS Messages". A tag is automatically assigned for triggering alarms. "MSG_Queue_1013" with the type of "Raw data type" (Attached picture) Where can I modify this tag to define values that should trigger my tags?
Is there anything in PAS to define Trigger values or I have to modify MSG_Queue_1013 with a function in SCC?
[img]https://ibb.co/jgsGrF[/img]
[url]https://ibb.co/jgsGrF[/url] |
Messages that communicate via raw data tags with the AS (Format DLL) are shown in the "AS messages" and are automatically generated by the processor.
For a specific tag you must define in Alarm logging on the specified Driver the tags you need. |
Thank you
I have seen in SICAM SCC demo project and other projects that they used just this tag for alarm logging (one tag for all alarms with prefix MSG_QUEUE_...)
I have another problem: All single point indications that come from SICAM PAS to SICAM SCC are 1 and 2 (instead of 0 and 1) so I must use analog alarms! How can I change PAS to have 0 and 1 for single points? |
If you are using SICAM SCC V9.00 read how to lucrate correct Alarm Logging on SCC on Manual
[URL=https://userscloud.com/u82lmhu51qnu]scc_b.pdf - 12.8 MB[/URL]
If you are using older versions then you have to create a program in the PLC to produse a secondary buffer to storage the buffer of all modules, and send this buffer to WinCC via B_SEND.
In the WinCC you făcute a Raw Tag to receive this buffer and create a script to analyze this tag. This script should analyze the change of messages (received by Raw Tag) and using APIs
- MSRTStartMsgService;
- MSRTCreateMsg;
- MSRTStopMsgService.
of WinCC setting the status and the timestamp of messages. |
Thank you for your help
Let me give you an example
For example I want to have alarm when
Relay_fail = 1
Or
OC_OPERATED =1
Or
TCS_OK=0
Where should I set these 0 and 1 values?
Thanks |
|
| Back to top |
|
 |
banguy Member junior

Joined: 01 Mar 2017 Posts: 59
|
Posted: 20/03/2017 11:02 Post subject: Re: SICAM PAS Alarm logging |
|
|
| milad2002b wrote: | Hello
I am trying to add alarm logging to my project in SCC.
I have imported tags from PAS. Now I have tags and messages in "AS Messages". A tag is automatically assigned for triggering alarms. "MSG_Queue_1013" with the type of "Raw data type" (Attached picture) Where can I modify this tag to define values that should trigger my tags?
Is there anything in PAS to define Trigger values or I have to modify MSG_Queue_1013 with a function in SCC?
[img]https://ibb.co/jgsGrF[/img]
[url]https://ibb.co/jgsGrF[/url] |
Please upload SICAM PAS and SICAM SCC? |
|
| Back to top |
|
 |
milad2002b Junior

Joined: 04 Oct 2016 Posts: 11
|
Posted: 20/03/2017 11:15 Post subject: Re: SICAM PAS Alarm logging |
|
|
| banguy wrote: |
Please upload SICAM PAS and SICAM SCC? |
SICAM SCC 8.03 and SICAM PAS 8.06
[url]https://mega.nz/#F!9V4QDaha!wKMz_LslhVTmPWL_sZpnpw[/url]
If anybody has version 9 please upload it |
|
| Back to top |
|
 |
banguy Member junior

Joined: 01 Mar 2017 Posts: 59
|
Posted: 22/03/2017 07:43 Post subject: Re: SICAM PAS Alarm logging |
|
|
| milad2002b wrote: | | banguy wrote: |
Please upload SICAM PAS and SICAM SCC? |
SICAM SCC 8.03 and SICAM PAS 8.06
[url]https://mega.nz/#F!9V4QDaha!wKMz_LslhVTmPWL_sZpnpw[/url]
If anybody has version 9 please upload it |
Thank you |
|
| Back to top |
|
 |
banguy Member junior

Joined: 01 Mar 2017 Posts: 59
|
Posted: 21/05/2018 18:35 Post subject: SICAM PAS / PQS V8.11 update |
|
|
SICAM PAS / PQS V8.11
https://support.industry.siemens.com/cs/document/109757831/
SICAM SCC 8.03 and SICAM PAS 8.06
| Code: | | https://mega.nz/#F!9V4QDaha!wKMz_LslhVTmPWL_sZpnpw |
Update Packages for V8.0 Installations and latest Hotfix
https://support.industry.siemens.com/cs/attachments/109757831/readme_b.pdf
https://support.industry.siemens.com/cs/attachments/109757831/SICAM_PAS_PQS_V8.xx_to_V8.11_Update.zip
https://support.industry.siemens.com/cs/attachments/109757831/SICAM_PAS_V811_SecureCom.zip |
|
| Back to top |
|
 |
|