Setup modbus RTU in M221 PLC using Somachine Basic software

 
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> Schneider Electric
View previous topic :: View next topic  
Author Message
lrotk
Junior
Junior


Joined: 12 Jan 2016
Posts: 2

PostPosted: 12/01/2016 17:47    Post subject: Setup modbus RTU in M221 PLC using Somachine Basic software Reply with quote

I am developing a basic program for M221 PLC that gets a value from another PC software using RS232C connector and modbus RTU. I have setup Modbus protocol inside Somachine Basic software trought SL1 line but I am not able to see or config READ_VAR, WRITE_VAR... communication objects.

May I connect the cable between PC and PLC before developing anything? I have attached two captures of my program.

I would be very grateful if anyone can help/support me. Thanks in advance.

[url=http://www.99poze.ro/p/76452e87e3aedeaf92b08c984aa9dbd8.jpg]Setup modbus RTU in M221 PLC using Somachine Basic software Setup modbus RTU in M221 PLC using Somachine Basic software[/url]+[url=http://www.99poze.ro/p/bbadc27d50b992289dd87dd9522031c1.jpg]Setup modbus RTU in M221 PLC using Somachine Basic software Setup modbus RTU in M221 PLC using Somachine Basic software[/url]+
Back to top
View user's profile Send private message
lrotk
Junior
Junior


Joined: 12 Jan 2016
Posts: 2

PostPosted: 15/01/2016 17:58    Post subject: Reply with quote

Thanks zarzuela.

I found out a solution for solving the problem I have (communication objects do not show at SoMachine Basic software).

I was developing using a lower level that I actually needed for using communications library. So, I moved up this level to 4.0 at SoMachine Basic tasks and updated M221 controller. Then this problem was solved and I could use READ_VAR, WRITE_VAR, etc.
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> Schneider Electric All times are GMT + 2 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group
Fa-ti si tu propriul forum GRATUIT, pe www.myforum.ro