PostPosted: 30/08/2017 12:50    Post subject: 'SelfDiagnosis:Value OS Handle Count of station OS.Handles Reply with quote

HELLO
MY SYSTEM IS PCS7 V8.0
WINDOWS IS SERVER 2008 R2
ERROR in my plant the messages on the one of SERVER'S

'SelfDiagnosis:Value OS Handle Count of station OS.Handles violated the HIGH warning limit "

it was shown and i check the Taskmanager of Windows,a program about 22,500 Handles and unistall this program

And that

reset the Alarm's from Alarm logging wincc
But there is still this message
I am seeing and sort Task Manager but
Handles Not having high value(about 1,000)
PLEASE HELP ME FOR THIS ERROR

LINK PICTURE OF THIS ERROR:[url]https://ibb.co/eX76U5[/url]
Back to top
View user's profile Send private message
dll
Junior 2
Junior 2


Joined: 31 Mar 2017
Posts: 39

PostPosted: 30/08/2017 13:55    Post subject: Re: 'SelfDiagnosis:Value OS Handle Count of station OS.Handl Reply with quote

rayen_6827 wrote:
HELLO
MY SYSTEM IS PCS7 V8.0
WINDOWS IS SERVER 2008 R2
ERROR in my plant the messages on the one of SERVER'S

'SelfDiagnosis:Value OS Handle Count of station OS.Handles violated the HIGH warning limit "

it was shown and i check the Taskmanager of Windows,a program about 22,500 Handles and unistall this program

And that

reset the Alarm's from Alarm logging wincc
But there is still this message
I am seeing and sort Task Manager but
Handles Not having high value(about 1,000)
PLEASE HELP ME FOR THIS ERROR

LINK PICTURE OF THIS ERROR:[url]https://ibb.co/eX76U5[/url]

What is the Message Class ...???? everything come from PLC?
'SelfDiagnosis:Value OS Handle Count of station OS.Handles 'SelfDiagnosis:Value OS Handle Count of station OS.Handles
Back to top
View user's profile Send private message
rayen_6827
Member junior
Member junior


Joined: 21 Jun 2013
Posts: 67

PostPosted: 31/08/2017 09:50    Post subject: Reply with quote

yes this error stay on the server and not acknowlege i send link this error you can see this
class this massege:plc process ..
Back to top
View user's profile Send private message
dll
Junior 2
Junior 2


Joined: 31 Mar 2017
Posts: 39

PostPosted: 31/08/2017 10:01    Post subject: Reply with quote

rayen_6827 wrote:
yes this error stay on the server and not acknowlege i send link this error you can see this
class this massege:plc process ..


well..you have not access or just stick arround...
I ask exactly what is the issue of this alarm.. PLC process... has more than 50 process issued by PLC..
When ask something ..give all information if you need an answer,,,
anyway this has nothing to do with the server computer..Task manager and..so on..
You have problem with a PLC CPU...determine which has issued this alarm...and what System Alarm issued this....
Back to top
View user's profile Send private message
rayen_6827
Member junior
Member junior


Joined: 21 Jun 2013
Posts: 67

PostPosted: 01/09/2017 09:13    Post subject: Reply with quote

hello
thank you for reply the question me
the information

message no:1012703


class:PLC process control system messages


Self-diagnostics: Value @7%s@ of station @10%s@ violated the HIGH warning limit.

I do not know why the alarms were issued.
Back to top
View user's profile Send private message
dll
Junior 2
Junior 2


Joined: 31 Mar 2017
Posts: 39

PostPosted: 01/09/2017 20:13    Post subject: Reply with quote

rayen_6827 wrote:
hello
thank you for reply the question me
the information

message no:1012703

class:PLC process control system messages

Self-diagnostics: Value @7%s@ of station @10%s@ violated the HIGH warning limit.
I do not know why the alarms were issued.


I supposed you have an Engineering Station for going online with every PLC....?
Or if not then with a PG go to connect to every PLC and enter online....
You must have the original project or eventually can upload from CPU->PG
After entering online test CPU messages for every PLC..
How:
1. Select the S7 station in the Component View of the SIMATIC Manager.
Right-click to open the pop-up menu and select "PLC > CPU Messages".
A diagnostics program opens, which can be used to view and test the CPU messages.
'SelfDiagnosis:Value OS Handle Count of station OS.Handles 'SelfDiagnosis:Value OS Handle Count of station OS.Handles

Check which of the PLC bursts self diagnostic messages...and why....
Good luck!
Back to top
View user's profile Send private message
rayen_6827
Member junior
Member junior


Joined: 21 Jun 2013
Posts: 67

PostPosted: 02/09/2017 15:53    Post subject: Reply with quote

hello

i can connet to plc with Engineering station and i check the massege on the cpu i dont see any fault
this error on the server you can see the down link diagnostic picture of wincc
https://ibb.co/gtcz4F
Back to top
View user's profile Send private message
dll
Junior 2
Junior 2


Joined: 31 Mar 2017
Posts: 39

PostPosted: 02/09/2017 22:30    Post subject: Reply with quote

rayen_6827 wrote:
hello

i can connet to plc with Engineering station and i check the massege on the cpu i dont see any fault
this error on the server you can see the down link diagnostic picture of wincc
https://ibb.co/gtcz4F


While you keep posting a picture from 5 months ago you cannot solve the problem.
Check every PLC diagnostic message and after that we can discuss.
OK?
Back to top
View user's profile Send private message
rayen_6827
Member junior
Member junior


Joined: 21 Jun 2013
Posts: 67

PostPosted: 03/09/2017 04:56    Post subject: Reply with quote

Five months !!!

It happened on 4_7_2017, about two months ago
At the same time, I checked out the CPU, and I did not have Fault

I can say that this error is probably due to many alarms that were created at once
Or
That's a lot of cpu usage in a moment
But everything is natural right now, but the error is still there
Back to top
View user's profile Send private message
dll
Junior 2
Junior 2


Joined: 31 Mar 2017
Posts: 39

PostPosted: 03/09/2017 22:07    Post subject: Reply with quote

rayen_6827 wrote:
Five months !!!

It happened on 4_7_2017, about two months ago
At the same time, I checked out the CPU, and I did not have Fault

I can say that this error is probably due to many alarms that were created at once
Or
That's a lot of cpu usage in a moment
But everything is normal right now, but the error is still there

Make this Alarm with Acknowledge Properties ,(as you see Default is UN-Acknowledge) acknowledge this and then see if this Alarm is still pending.
If yes, that means you have to verify every PLC and findout what is the cause of new Alarm.
If not, that means that indeed the Alarm has gone....
Then eventually you can setback as UN-Acknowledge for not make acknowledgments by mistake...
'SelfDiagnosis:Value OS Handle Count of station OS.Handles 'SelfDiagnosis:Value OS Handle Count of station OS.Handles
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> Simatic Automation Systems All times are GMT + 2 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group
Fa-ti si tu propriul forum GRATUIT, pe www.myforum.ro