SCU 22 problem

 
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> OMRON
View previous topic :: View next topic  
Author Message
romyrizky
Junior
Junior


Joined: 18 Jan 2017
Posts: 7
Location: Jakarta

PostPosted: 10/03/2017 09:44    Post subject: SCU 22 problem Reply with quote

hey, this is my first time using serial comunication unit in omron. have anyone give some example program and setting. using, TXDU and RXDU syntax. thanks :-)
_________________
Regards,

Romy
Back to top
View user's profile Send private message
tatami
Junior
Junior


Joined: 29 Jan 2017
Posts: 12

PostPosted: 10/03/2017 15:16    Post subject: Re: SCU 22 problem Reply with quote

romyrizky wrote:
hey, this is my first time using serial comunication unit in omron. have anyone give some example program and setting. using, TXDU and RXDU syntax. thanks :-)

find a simple instruction example
https://www.support-omron.fr/pdf/W336-E1-10+Serial_Communication+Operation_Manual.pdf
Back to top
View user's profile Send private message
romyrizky
Junior
Junior


Joined: 18 Jan 2017
Posts: 7
Location: Jakarta

PostPosted: 11/03/2017 06:50    Post subject: Re: SCU 22 problem Reply with quote

tatami wrote:
romyrizky wrote:
hey, this is my first time using serial comunication unit in omron. have anyone give some example program and setting. using, TXDU and RXDU syntax. thanks :-)

find a simple instruction example
https://www.support-omron.fr/pdf/W336-E1-10+Serial_Communication+Operation_Manual.pdf


i already following the manual step but there is no work. hemm,
_________________
Regards,

Romy
Back to top
View user's profile Send private message
tatami
Junior
Junior


Joined: 29 Jan 2017
Posts: 12

PostPosted: 11/03/2017 13:30    Post subject: Re: SCU 22 problem Reply with quote

romyrizky wrote:
tatami wrote:
romyrizky wrote:
hey, this is my first time using serial comunication unit in omron. have anyone give some example program and setting. using, TXDU and RXDU syntax. thanks :-)

find a simple instruction example
https://www.support-omron.fr/pdf/W336-E1-10+Serial_Communication+Operation_Manual.pdf


i already following the manual step but there is no work. hemm,


what exactly do you want to do?
Connect to CJ1W-SCU22 with what?
Give more detail.
More manuals you find on
https://www.lakewoodautomation.com/support/manuals.htm
https://www.myomron.com/index.php?article=1562&action=kb

Take care that the port on the CJ1 PLC is that the signal ground (SG) is on pin 9 of the connector, instead of pin 5, where all RS-232 cables expect it.
You will need to make/buy a cable that connects pin 9 on the controller to pin 5 of your device.

Also, RTS/CTS _ARE_ used by the controller. Put a jumper from pin 4 to pin 5 on the PLC end of your cable.

If you configure it in the setup, that should take care of it for you can change the configuration in your ladder logic using the STUP(237) instruction.
Back to top
View user's profile Send private message
romyrizky
Junior
Junior


Joined: 18 Jan 2017
Posts: 7
Location: Jakarta

PostPosted: 26/03/2017 08:11    Post subject: Re: SCU 22 problem Reply with quote

tatami wrote:
romyrizky wrote:
tatami wrote:
romyrizky wrote:
hey, this is my first time using serial comunication unit in omron. have anyone give some example program and setting. using, TXDU and RXDU syntax. thanks :-)

find a simple instruction example
https://www.support-omron.fr/pdf/W336-E1-10+Serial_Communication+Operation_Manual.pdf


i already following the manual step but there is no work. hemm,


what exactly do you want to do?
Connect to CJ1W-SCU22 with what?
Give more detail.
More manuals you find on
https://www.lakewoodautomation.com/support/manuals.htm
https://www.myomron.com/index.php?article=1562&action=kb

Take care that the port on the CJ1 PLC is that the signal ground (SG) is on pin 9 of the connector, instead of pin 5, where all RS-232 cables expect it.
You will need to make/buy a cable that connects pin 9 on the controller to pin 5 of your device.

Also, RTS/CTS _ARE_ used by the controller. Put a jumper from pin 4 to pin 5 on the PLC end of your cable.

If you configure it in the setup, that should take care of it for you can change the configuration in your ladder logic using the STUP(237) instruction.


THANKS a Lot, its already worked :-)
_________________
Regards,

Romy
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> OMRON All times are GMT + 2 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group
Fa-ti si tu propriul forum GRATUIT, pe www.myforum.ro