PostPosted: 27/08/2016 17:39    Post subject: S5 IP266 positioning module program transfer Reply with quote

Hi Guys,

I need to back up (transfer) the parameters from an S5 IP266 positioning module. I have a copy of the COM266 software (although it is in German language), however when I try to connect/go online I get error F53 (no communication)! I am using the standard cable that works ok for the CPU!

Is there a different cable I need ?
:weep:
Back to top
View user's profile Send private message
keke
Member junior
Member junior


Joined: 02 Aug 2015
Posts: 53
Location: Traore

PostPosted: 27/08/2016 19:08    Post subject: Re: S5 IP266 positioning module program transfer Reply with quote

jacko15 wrote:
Hi Guys,

I need to back up (transfer) the parameters from an S5 IP266 positioning module. I have a copy of the COM266 software (although it is in German language), however when I try to connect/go online I get error F53 (no communication)! I am using the standard cable that works ok for the CPU!

Is there a different cable I need ?
:weep:

There are two types of S5 programming cable.
1. One draws power from the programming port,
2.The second needs a separate power supply.
The power is needed to drive the RS-232 to current-loop converter electronics.

The CPU has a pin which supplies power to the programming cable.
Many of the I/O modules do not and IP 266 don't make exception.
Or make yourself one (see picture) which works or buy one adapter with independent source for loop.
S5 IP266 positioning module program transfer Re: S5 IP266 positioning module program transfer
Do not make the connection in RED otherwise have problems.
Good luck.
Back to top
View user's profile Send private message
jacko15
Junior
Junior


Joined: 06 Oct 2014
Posts: 9

PostPosted: 29/08/2016 20:59    Post subject: adapter Reply with quote

Thanks Keke, I have a current loop unit from a Toshiba PLC project, I'll try to adapt it or build the circuit you provided.

Cheers :smile:
Back to top
View user's profile Send private message
jacko15
Junior
Junior


Joined: 06 Oct 2014
Posts: 9

PostPosted: 31/08/2016 18:11    Post subject: com246 com266 Reply with quote

Anyone know where I can get a copy of siemens S5 com246 & com266 in English?
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> SIMATIC Automation Systems -Reg.U All times are GMT + 2 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group
Fa-ti si tu propriul forum GRATUIT, pe www.myforum.ro