Posted: 20/08/2015 20:11 Post subject: Routing between PG/PC and MICROMASTER does not work |
|
|
MICROMASTER (MM4):
Routing between PG/PC and MICROMASTER does not work although the PG/PC interface is set to ISO-Industrial Ethernet.
What can I do? |
|
| Back to top |
|
 |
gert Member 3


Joined: 02 Jan 2015 Posts: 645
|
Posted: 20/08/2015 20:17 Post subject: Re: Routing between PG/PC and MICROMASTER does not work |
|
|
| garmon wrote: | MICROMASTER (MM4):
Routing between PG/PC and MICROMASTER does not work although the PG/PC interface is set to ISO-Industrial Ethernet.
What can I do? |
To allow communication with Routing change the PG/PC Interface to "TCP/IP".
Open NetPro in your project.
Ensure that your MICROMASTER and your PG/PC is connected-up as shown in the diagram
Next, your PG/PC must be assigned as shown in the next three screen shots.
Note: Please ensure that the checkmark for "Active" is set.
Right mouse click on PG/PC an choose assign PG/PC.
Choose your TCP/IP interface in tab assignment.
Checkmark S7ONLINE Access and confirm with Ok.
Now, the ROUTING should be active (this is shown by the yellow line).
 |
|