im41449 Junior

Joined: 16 Mar 2013 Posts: 10
|
Posted: 22/07/2013 13:07 Post subject: REDUNDANCY MODULE 1756-RM2 |
|
|
I'm trying to add redundancy module 1756-rm2 in rslogix 5000 io configuration, but when I press on "New module" list doesn't contain this product number. Im using Rslogix 5000 v20.01
What should I do? Please help |
|
| Back to top |
|
 |
brehoh Junior

Joined: 05 Jul 2012 Posts: 6
|
Posted: 22/07/2013 19:46 Post subject: |
|
|
im having the same problem right now, my suggest to upgrade the firmware and using Redundancy Module Config Tool, for now, im still searching the tools too, u can have it easyly when u have legal account to upgrade eds files etc, im using 1756-RM/B the firmware in compact flash v12 only have eds for 1756-RM/B and im still looking the eds right now
hope can hellp u even for a little |
|
| Back to top |
|
 |
im41449 Junior

Joined: 16 Mar 2013 Posts: 10
|
Posted: 22/07/2013 21:20 Post subject: |
|
|
I got eds here and redundancy works great even without putting the module in RSlogix 5000 configuration tree.
http://www.ab.com/networks/eds/cgi-bin/search.cgi?network_type=ControlNet,
but
I need to put RM2 module in configuration tree to do MSG instruction for program executed redundancy switchover ("Browse for the path to the 1756-RM or 1756-RMXT redundancy module." page 172 of 1756-um535_-en-p.pdf manual) |
|
| Back to top |
|
 |
im41449 Junior

Joined: 16 Mar 2013 Posts: 10
|
Posted: 24/07/2013 15:06 Post subject: |
|
|
Putting the path as: 1, number of 1756-RM2 module slot
makes it work, so for RM-2 module in slot 3 you would have to put 1, 3
Now I have another question, do I need both 1756-RMC1 fiber optic redundancy cables? Switchover works with only one but there is a red LED blinking on ch2. Putting both cables makes ch2 blink in green. |
|
| Back to top |
|
 |
messer Senior

Joined: 08 Mar 2012 Posts: 2059 Location: Europe
|
Posted: 24/07/2013 20:32 Post subject: |
|
|
| im41449 wrote: | Putting the path as: 1, number of 1756-RM2 module slot
makes it work, so for RM-2 module in slot 3 you would have to put 1, 3
Now I have another question, do I need both 1756-RMC1 fiber optic redundancy cables? Switchover works with only one but there is a red LED blinking on ch2. Putting both cables makes ch2 blink in green. |
Did you read this:
https://hotfile.com/dl/235810201/5a560cd/1756-in092_-en-p.rar.html |
|