REDUNDANCY MODULE 1756-RM2

 
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> ALLEN-BRADLEY(Rockwell Automation)
View previous topic :: View next topic  
Author Message
im41449
Junior
Junior


Joined: 16 Mar 2013
Posts: 10

PostPosted: 22/07/2013 13:07    Post subject: REDUNDANCY MODULE 1756-RM2 Reply with quote

I'm trying to add redundancy module 1756-rm2 in rslogix 5000 io configuration, but when I press on "New module" list doesn't contain this product number. Im using Rslogix 5000 v20.01
What should I do? Please help
Back to top
View user's profile Send private message
brehoh
Junior
Junior


Joined: 05 Jul 2012
Posts: 6

PostPosted: 22/07/2013 19:46    Post subject: Reply with quote

im having the same problem right now, my suggest to upgrade the firmware and using Redundancy Module Config Tool, for now, im still searching the tools too, u can have it easyly when u have legal account to upgrade eds files etc, im using 1756-RM/B the firmware in compact flash v12 only have eds for 1756-RM/B and im still looking the eds right now

hope can hellp u even for a little
Back to top
View user's profile Send private message
im41449
Junior
Junior


Joined: 16 Mar 2013
Posts: 10

PostPosted: 22/07/2013 21:20    Post subject: Reply with quote

I got eds here and redundancy works great even without putting the module in RSlogix 5000 configuration tree.
http://www.ab.com/networks/eds/cgi-bin/search.cgi?network_type=ControlNet,


but
I need to put RM2 module in configuration tree to do MSG instruction for program executed redundancy switchover ("Browse for the path to the 1756-RM or 1756-RMXT redundancy module." page 172 of 1756-um535_-en-p.pdf manual)
Back to top
View user's profile Send private message
im41449
Junior
Junior


Joined: 16 Mar 2013
Posts: 10

PostPosted: 24/07/2013 15:06    Post subject: Reply with quote

Putting the path as: 1, number of 1756-RM2 module slot
makes it work, so for RM-2 module in slot 3 you would have to put 1, 3


Now I have another question, do I need both 1756-RMC1 fiber optic redundancy cables? Switchover works with only one but there is a red LED blinking on ch2. Putting both cables makes ch2 blink in green.
Back to top
View user's profile Send private message
messer
Senior
Senior


Joined: 08 Mar 2012
Posts: 2059
Location: Europe

PostPosted: 24/07/2013 20:32    Post subject: Reply with quote

im41449 wrote:
Putting the path as: 1, number of 1756-RM2 module slot
makes it work, so for RM-2 module in slot 3 you would have to put 1, 3


Now I have another question, do I need both 1756-RMC1 fiber optic redundancy cables? Switchover works with only one but there is a red LED blinking on ch2. Putting both cables makes ch2 blink in green.

Did you read this:
https://hotfile.com/dl/235810201/5a560cd/1756-in092_-en-p.rar.html
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> ALLEN-BRADLEY(Rockwell Automation) All times are GMT + 2 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group
Fa-ti si tu propriul forum GRATUIT, pe www.myforum.ro