reading HART variables through SFC58 & SFC59

 
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> Simatic Automation Systems
View previous topic :: View next topic  
Author Message
mmohamed15
Junior
Junior


Joined: 13 Feb 2012
Posts: 18

PostPosted: 23/05/2016 12:41    Post subject: reading HART variables through SFC58 & SFC59 Reply with quote

Dear friends
does anyone have a sample program for reading HART variables as data records as descried in Siemens ET200M hart Manual
i can not use the hardware configured variables since this will exceed the 244 byte limitation of the ET200M allowed memory space
best regards
Mohamed
Back to top
View user's profile Send private message
kaminsky
Junior
Junior


Joined: 29 Apr 2016
Posts: 10

PostPosted: 23/05/2016 18:17    Post subject: Re: reading HART variables through SFC58 & SFC59 Reply with quote

mmohamed15 wrote:
Dear friends
does anyone have a sample program for reading HART variables as data records as descried in Siemens ET200M hart Manual
i can not use the hardware configured variables since this will exceed the 244 byte limitation of the ET200M allowed memory space
best regards
Mohamed

try this testbed
Code:
FUNCTION_BLOCK fbTestHartProt

VAR
  Command   : byte := B#16#FF; 
  BusyOut   : bool;
  BusyIn    : bool;
  LADDR     : dword;
  Index     : int;
  Valid     : bool;
  Done      : bool; 
  ErrorOut  : bool;
  ErrorIn   : bool;
  mStatusOut : array[1..4] of byte;
  StatusOut at mStatusOut : dword ;
  mStatusIn : array[1..4] of byte;
  StatusIn at mStatusIn : dword ;
  LenOut    : int;
  LenIn     : int;
  LenInRes  : int;
  BufferOut : array[0..240] of byte;
  BufferIn  : array[0..240] of byte;
END_VAR

// Forming a command according to document "ET 200M distributed I/O device
// HART analog modules" part 7.2.4

  BufferOut[0] := B#16#60; // in bits 0110_0000
  BufferOut[1] := B#16#05; // Number of preamble butes
  BufferOut[2] := B#16#01; // Universal HART Command - READ PRIMARY VARIABLE
 
// Calling SFB53 (WRREC) for writing a command

WRREC.dbWRREC(REQ := (Command = 1) // Entered from VAR-table
            ,ID := 512             // Configurated adress of module
            ,INDEX := 80           // Command for Channel 0
            ,LEN :=  3             // Number of writing bytes
            ,RECORD := BufferOut   // Pointer to command buffer
            );
 Done  := dbWRREC.DONE;            // OUT: BOOL
 BusyOut  := dbWRREC.BUSY;         // OUT: BOOL
 ErrorOut  := dbWRREC.ERROR;       // OUT: BOOL
 StatusOut  := dbWRREC.STATUS;     // OUT: DWORD

 if not BusyOut and (Command = 1) then
    Command := B#16#02;
 end_if;

// Calling SFB52 (RDREC) for reading a reply

RDREC.dbRDREC(REQ :=  (Command = 2) // Setted after function WRREC is ended
            ,ID :=  512           
            ,INDEX :=  81           // Reply for Channel 0
            ,MLEN :=  7             // Number of reading bytes
            ,RECORD :=  BufferIn    // Pointer to reply buffer
            );
  Valid := DB52.VALID;              // OUT: BOOL
  BusyIn := DB52.BUSY;              // OUT: BOOL
  ErrorIn := DB52.ERROR;            // OUT: BOOL
  StatusIn := DB52.STATUS;          // OUT: DWORD
  LenInRes := DB52.LEN;             // OUT: INT
 
    if not BusyIn and (Command = 2) then
        Command := B#16#FF;
    end_if;
END_FUNCTION_BLOCK


DATA_BLOCK dbTestHartProt  fbTestHartProt
BEGIN
END_DATA_BLOCK


DATA_BLOCK dbRDREC  RDREC //DB of SFB52
BEGIN
END_DATA_BLOCK


DATA_BLOCK dbWRREC  WRREC //DB of SFB53
BEGIN
END_DATA_BLOCK


ORGANIZATION_BLOCK OB1

VAR_TEMP
    info : ARRAY[0..19] OF BYTE;
END_VAR
;
END_ORGANIZATION_BLOCK



ORGANIZATION_BLOCK OB35

VAR_TEMP
    info : ARRAY[0..19] OF BYTE;
END_VAR

 fbTestHartProt.dbTestHartProt();
 
END_ORGANIZATION_BLOCK
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> Simatic Automation Systems All times are GMT + 2 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group
Fa-ti si tu propriul forum GRATUIT, pe www.myforum.ro