Prosoft PLX 31 Port Configuration

 
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> ALLEN-BRADLEY(Rockwell Automation) Reg. U
View previous topic :: View next topic  
Author Message
mohamedsamy9393
Junior
Junior


Joined: 30 Mar 2020
Posts: 3

PostPosted: 04/04/2020 12:14    Post subject: Prosoft PLX 31 Port Configuration Reply with quote

Dear All,
I'm trying to connect this gateway Prosoft PLx31 to my PLC 1756 using ethernet/ip and then from the gateway to DCS using modbus tcp/ip
The question is I have only one ethernet port in the gateway , How can I connect the PLC to this port and again from the same port to the DCS, Must I have a switch ? [url=http://www.99poze.ro/p/7ef6f0f9040a3b9bf1d18f61bb697dd1.jpg]Prosoft PLX 31 Port Configuration Prosoft PLX 31 Port Configuration[/url]+
[url=http://www.99poze.ro/p/4827ea4adef0effe3adb1a3a559f59d2.jpg]Prosoft PLX 31 Port Configuration Prosoft PLX 31 Port Configuration[/url]+
_________________
Mohamed Samy
Back to top
View user's profile Send private message
wildpikachu
Junior 2
Junior 2


Joined: 16 Jul 2015
Posts: 34

PostPosted: 07/04/2020 10:44    Post subject: Reply with quote

Hi mohamedsamy9393.

the single port on the PLC31-EIP-MBTCP will handle both the Ethernet IP and the Modbus TCP/IP traffic. so yes you will need an Ethernet switch and I would recommend you use a managed Ethernet switch and enable IGMP snooping as is recommended by the ODVA for Ethernet IP networks. If you only have a very small number of Ethernet IP devices then a un-managed switch should work okay but I would not recommend it.

Cheers.
Guy

P.S. here is a youtube link with training for the PLX31-EIP-MBTCP: https://www.youtube.com/watch?v=4tlab2xW7VE
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> ALLEN-BRADLEY(Rockwell Automation) Reg. U All times are GMT + 2 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group
Fa-ti si tu propriul forum GRATUIT, pe www.myforum.ro