PostPosted: 19/07/2018 16:39    Post subject: Profibus address mapping Reply with quote

Hello everyone,

Is there a way to map out an existing profibus network?

Thanks


Last edited by AutoKal on 29/07/2018 02:54; edited 1 time in total
Back to top
View user's profile Send private message
scooby
Member
Member


Joined: 25 Aug 2013
Posts: 238
Location: Dunquerque

PostPosted: 19/07/2018 18:51    Post subject: Re: Profibus address mapping Reply with quote

AutoKal wrote:
Hello everyone,

Is there a way to map out an existing profibus network?
I have a C200HW-PRM21 with 6 slaves and I need to change three of the slaves and for that I need to know which memory areas/address each one of the slaves is using.

Thanks


The default mapping of areas onto the PLC memory is the same default mapping as
used in the CJ1W-DRM21 Devicenet Master/Slave Unit and in the CJ1W-PRM21
PROFIBUS Master unit. Care should be taken to avoid data overlap, if such a Unit is
part of the same PLC CPU system as the CJ1W-PNT21 PROFINET IO Controller Unit
Mapping Area Control Each mapping Area in the Allocation tab is equipped with four controls and an
information field located below the Area.
Note 1 When mapping, the modules are copied from the module list to the mapping
Area. The module list acts as a resource for the two Mapping Areas. To change
the mapping of a module drag and drop it from the module list to the Mapping
Area.
2 When adding or removing slaves and modules, while Auto Addressing has been
enabled, the modules in the Areas will be remapped, usually also resulting in I/O
data being re-mapped. Therefore it is recommended to define all slaves and modules,
before setting up the PLC memory mapping configuration.
Control Description
Area Selects the PLC memory area to which the associated
I/O Area will be mapped. Possible options are:
• Not Used (List must be empty).
• CIO
• DM
• WR
• HR
• EM Bank 0 to 12 (Decimal)
(See Note 1)
Start Address In this field the user can enter the start address in the PLC
memory of the mapped data block.


http://www.techtrends.ru/docs/omron/sistemy_avtomatizatsii/programmiruemye_logicheskie_kontrollery/modulnye_pls/cj1g_cj1h/cj1_communication_units/W12E-EN-01_CJ1W-PNT21_Operation_Manual.pdf
https://assets.omron.eu/downloads/manual/en/v11/w05e_cx-profibus_operation_manual_en.pdf
https://www.miel.si/wp-content/VsebinaPDF/W509-E2-01+CJ1W-PRM21+OperManual.pdf
try
https://www.file-upload.net/download-13236793/profitrace_v2_9_6.zip.html
https://www.file-upload.net/download-13236790/profitrace-v1-6-2.zip.html
https://www.file-upload.net/download-13236785/profitrace-v1-7-edu.zip.html
https://www.file-upload.net/download-13236805/profitrace-v297.zip.html

or
https://www.file-upload.net/download-13236837/cx-configurator_fdt_software_en.zip.html
Back to top
View user's profile Send private message
AutoKal
Member junior
Member junior


Joined: 29 Dec 2015
Posts: 105

PostPosted: 19/07/2018 19:08    Post subject: Reply with quote

Thanks scooby.
Back to top
View user's profile Send private message
loc
Member
Member


Joined: 17 Nov 2012
Posts: 168

PostPosted: 16/10/2021 05:10    Post subject: Re: Profibus address mapping Reply with quote

scooby wrote:
AutoKal wrote:
Hello everyone,

Is there a way to map out an existing profibus network?
I have a C200HW-PRM21 with 6 slaves and I need to change three of the slaves and for that I need to know which memory areas/address each one of the slaves is using.

Thanks


The default mapping of areas onto the PLC memory is the same default mapping as
used in the CJ1W-DRM21 Devicenet Master/Slave Unit and in the CJ1W-PRM21
PROFIBUS Master unit. Care should be taken to avoid data overlap, if such a Unit is
part of the same PLC CPU system as the CJ1W-PNT21 PROFINET IO Controller Unit
Mapping Area Control Each mapping Area in the Allocation tab is equipped with four controls and an
information field located below the Area.
Note 1 When mapping, the modules are copied from the module list to the mapping
Area. The module list acts as a resource for the two Mapping Areas. To change
the mapping of a module drag and drop it from the module list to the Mapping
Area.
2 When adding or removing slaves and modules, while Auto Addressing has been
enabled, the modules in the Areas will be remapped, usually also resulting in I/O
data being re-mapped. Therefore it is recommended to define all slaves and modules,
before setting up the PLC memory mapping configuration.
Control Description
Area Selects the PLC memory area to which the associated
I/O Area will be mapped. Possible options are:
• Not Used (List must be empty).
• CIO
• DM
• WR
• HR
• EM Bank 0 to 12 (Decimal)
(See Note 1)
Start Address In this field the user can enter the start address in the PLC
memory of the mapped data block.


http://www.techtrends.ru/docs/omron/sistemy_avtomatizatsii/programmiruemye_logicheskie_kontrollery/modulnye_pls/cj1g_cj1h/cj1_communication_units/W12E-EN-01_CJ1W-PNT21_Operation_Manual.pdf
https://assets.omron.eu/downloads/manual/en/v11/w05e_cx-profibus_operation_manual_en.pdf
https://www.miel.si/wp-content/VsebinaPDF/W509-E2-01+CJ1W-PRM21+OperManual.pdf
try
https://www.file-upload.net/download-13236793/profitrace_v2_9_6.zip.html
https://www.file-upload.net/download-13236790/profitrace-v1-6-2.zip.html
https://www.file-upload.net/download-13236785/profitrace-v1-7-edu.zip.html
https://www.file-upload.net/download-13236805/profitrace-v297.zip.html

or
https://www.file-upload.net/download-13236837/cx-configurator_fdt_software_en.zip.html


Please upload link of Profitrace software, thank! :-)
_________________
HELLO
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> OMRON All times are GMT + 2 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group
Fa-ti si tu propriul forum GRATUIT, pe www.myforum.ro