Problems Rslinx opc server error

 
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> ALLEN-BRADLEY(Rockwell Automation)
View previous topic :: View next topic  
Author Message
ksxs01
Junior
Junior


Joined: 15 Nov 2015
Posts: 4

PostPosted: 26/01/2017 08:05    Post subject: Problems Rslinx opc server error Reply with quote

Hello there..
Someone can help me.. I cant comunicate rslinx opc server with fluidsim (simulations for practice).

I have installed rslogix 8.40 and rslinx classic 2.57.
W7 Professional x32

before, its works fine, now i have this problem with opc server..

Problems Rslinx opc server error Problems Rslinx opc server error

Problems Rslinx opc server error Problems Rslinx opc server error


Thankyou
Back to top
View user's profile Send private message
arthur
Junior
Junior


Joined: 25 Jan 2017
Posts: 2

PostPosted: 26/01/2017 09:10    Post subject: Reply with quote

Other computer connection
You must have RSLinx Pro or Gateway to use OPC with RS Linx. If the OPC client is on a remote or different PC than the RSLinx OPC Server, than they must have RS Linx Gateway version installed. This is a licensing requirement by Rockwell.

Local connection
1. Open the Properties of the Data Collector Fluidsim.
2. Go to the Extended Properties tab.
3. Set the "Connect In-Process" property to True. Click OK.

Or Fluidsim Interface for OPC DA, causes the interface to treat all OPC Servers as remote connections even if "/SERVER=LocalHost::OPCServerName" is specified. The RSLinx OPCServer is one of the OPC Servers that does not allow remote connections, which is why the error "CoCreateInstanceEx: 80040112 Class is not licensed for use" is seen. Note this will happen with any OPC Server that does not allow remote connections.

Try to manually add the two leading colon characters before the OPC Server name. For example, set the /SERVER argument to this:

/SERVER=::OPCServerName

This can be done by editing the .BAT file or by adding the additional parameter in the Fluidsim Interface Configuration and removing the entry from the OPCInt > OPC Server tab.
Back to top
View user's profile Send private message
ksxs01
Junior
Junior


Joined: 15 Nov 2015
Posts: 4

PostPosted: 28/01/2017 23:23    Post subject: Reply with quote

I downloaded rslinx classic gateway 2.54 and works fine now.

Thank you arthur
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> ALLEN-BRADLEY(Rockwell Automation) All times are GMT + 2 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group
Fa-ti si tu propriul forum GRATUIT, pe www.myforum.ro