abousna Junior

Joined: 09 Mar 2019 Posts: 1
|
Posted: 09/03/2019 14:43 Post subject: problem in plc cj2m-cpu12 |
|
|
hello dears
I have a machine with plc cj2m-cpu12
suddenly the machine stop running and plc error led flashing as shown in the video
https://youtu.be/zMe5YTh2qzA
please advise me ?? |
|
| Back to top |
|
 |
TatumO Junior

Joined: 04 Jul 2018 Posts: 3
|
Posted: 09/03/2019 17:05 Post subject: |
|
|
As I see the ERH and RUN indicators on the Deosebit I/O Unit are lit.
In that case the singular I/O refreshing is not being performed for the Unit from the CPU Unit (CPU Unit monitoring error).
Remedy:
Change the bit corresponding to the unit number to 0 to enable cyclic refreshing, or make sure that the Unit is refreshed from
the program using IORF or FIORF at least once every 11 s. |
|