msi Junior

Joined: 23 May 2015 Posts: 5
|
Posted: 06/09/2017 20:51 Post subject: Problem at hitachi plc h-series |
|
|
Error 33 for plc h-702 :
error code:
User memory size error (checked when changed from STOP to RUN)-The user program size specified by the parameter is greater than the actual user
memory size. Check the user memory size and the program size set from the peripheral device. Correct the parameter and rerun
the program.
--
I changed the battery
Error reset is not possible
There is no way to communicate with the computer, when there is a 109
error communicate 109 : Not set baud rate
please help |
|
| Back to top |
|
 |
varan Member junior

Joined: 13 Feb 2016 Posts: 88
|
Posted: 06/09/2017 21:53 Post subject: Re: Problem at hitachi plc h-series |
|
|
| msi wrote: | Error 33 for plc h-702 :
error code:
User memory size error (checked when changed from STOP to RUN)-The user program size specified by the parameter is greater than the actual user
memory size. Check the user memory size and the program size set from the peripheral device. Correct the parameter and rerun
the program.
--
I changed the battery
Error reset is not possible
There is no way to communicate with the computer, when there is a 109
error communicate 109 : Not set baud rate
please help |
| Code: | | -The user program size specified by the parameter is greater than the actual user memory size. Check the user memory size and the program size set from the peripheral device. Correct the parameter and rerun the program. |
what is your first taught when read this?
Do you have room for a larger user memory size? |
|
| Back to top |
|
 |
msi Junior

Joined: 23 May 2015 Posts: 5
|
Posted: 07/09/2017 08:00 Post subject: |
|
|
The PLC program worked for a few years without any problems; This problem was caused after the bug in the battery was damaged.
No connection with CPU is possible, I tested it in several ways, it has no result. |
|
| Back to top |
|
 |
varan Member junior

Joined: 13 Feb 2016 Posts: 88
|
Posted: 07/09/2017 08:32 Post subject: |
|
|
| msi wrote: | The PLC program worked for a few years without any problems; This problem was caused after the bug in the battery was damaged.
No connection with CPU is possible, I tested it in several ways, it has no result. |
what cpu do you use? Read hardware manual how to proceed...
http://www.hitachi-ds.com/en/Products/Automation/PLC/Modular-Series/H-Series.html
 |
|
| Back to top |
|
 |
msi Junior

Joined: 23 May 2015 Posts: 5
|
Posted: 07/09/2017 10:04 Post subject: |
|
|
| varan wrote: | | msi wrote: | The PLC program worked for a few years without any problems; This problem was caused after the bug in the battery was damaged.
No connection with CPU is possible, I tested it in several ways, it has no result. |
what cpu do you use? Read hardware manual how to proceed...
http://www.hitachi-ds.com/en/Products/Automation/PLC/Modular-Series/H-Series.html
 |
H702 / CPU2-07H |
|
| Back to top |
|
 |
varan Member junior

Joined: 13 Feb 2016 Posts: 88
|
Posted: 07/09/2017 10:27 Post subject: |
|
|
proceed as in below
 |
|
| Back to top |
|
 |
msi Junior

Joined: 23 May 2015 Posts: 5
|
Posted: 07/09/2017 11:26 Post subject: |
|
|
| varan wrote: | proceed as in below
 |
Thanks for answering
Error 33 is displayed in all three modes (stup, run, ..).
one question:
Is the problem solved by changing ram2-16h? Program is not clean?
 |
|
| Back to top |
|
 |
varan Member junior

Joined: 13 Feb 2016 Posts: 88
|
Posted: 07/09/2017 14:59 Post subject: |
|
|
I understood that you do not use ROM Memory?
As long as you have a battery maybe have also a ROM on the cassette....I suppose...did you check-in..???
If you have not ROM then try to reload again the entire program as for RAM only procedure.(read manual)
If the error persists then replace RAM.
Memory Options RAM/ROM suitable and how to are as in below
You have to use a GPCL01H console for Initialization and re-run |
|