Posted: 16/12/2012 07:13 Post subject: PNP Sourcing Input with PNP type dispozitiv |
|
|
As i know PNP Souching input need to connect with NPN dispozitiv to make use of it...
Currently the supplier provided PNP type instrument with my PNP sourching Input module.
How do i make use of it? It's the only way to change the Instrument to NPN type? |
|
| Back to top |
|
 |
messer Senior

Joined: 08 Mar 2012 Posts: 2059 Location: Europe
|
Posted: 17/12/2012 21:16 Post subject: Re: PNP Sourcing Input with PNP type dispozitiv |
|
|
| chuahyc wrote: | As i know PNP Souching input need to connect with NPN instrument to make use of it...
Currently the supplier provided PNP type instrument with my PNP sourching Input module.
How do i make use of it? It's the only way to change the Instrument to NPN type? |
Your question is a little confused just for me....
Regarding Defining Sinking & Sourcing I/O you can find some information here...
http://www.vr.ncue.edu.tw/esa/C_8051/Defining%20Sinking%20%20Sourcing%20IO.pdf
http://www.engr.siu.edu/staff/spezia/Web438B/Lecture%20Notes/ET438B-9.pdf
In general, a sinking input is one that needs to be pulled up towards the positive supply to be true.
And a sourcing input is one that needs to be pulled toward ground to be true.
So a Sourcing output would normally be used with a sinking input and vice versa.
A sourcing circuit would be drawn as voltage->switch->load->ground.
A sinking circuit would be drawn as Voltage->load->switch->ground.
This all assumes positive logic.
A Sensor Wiring with Sinking/Sourcing can be seen here:
http://engineeronadisk.com/V2/book_implementation/engineeronadisk-92.html |
|