I HAVE TSX MOMENTUM 171CCC96030 RUN IN POWER GENERATION
I WANT TO UPLOAD THE PROGRAM TO CHANGE OUTPUT POINT TO SPARE ONE DUE TO THE EXIST IS DAMAGE
I USED CONCEPT 2.6 BUT UPLOADED THE CONFIGURATION ONLY AND THE PROGRAM NOT UPLOADED
SO PLEASE HELP ,ANY WAY TO UPLOAD THE PROGRAM DUE TO NOT HAVE THE SOURCE OF THE PROGRAM |
|
| Back to top |
|
 |
Phillips12 Junior

Joined: 16 Oct 2018 Posts: 1
|
Posted: 29/10/2018 22:24 Post subject: |
|
|
Maybe PLC is set up as 171CCC96030-IEC if it is in a Power Generation Facility.
Did you "tell" Concept that it's an IEC 171CCC96030-IEC ?
You can upload/download to the PLC when you tell Concept that it's an IEC programming...
give a try... |
|