plc.myforum.ro Forum Index plc.myforum.ro
PLCs users www.plc.myforum.ro!
 
 FAQFAQ   SearchSearch   MemberlistMemberlist   UsergroupsUsergroups   RegisterRegister 
 ProfileProfile   Log in to check your private messagesLog in to check your private messages   Log inLog in 

Performance Data-Establishing PN response time

 
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> ROSIEMENS SIMATIC Automation Systems
View previous topic :: View next topic  
Author Message
gert
Member 3
Member 3
gert

Joined: 02 Jan 2015
Posts: 645

PostPosted: 24/01/2015 17:45    Post subject: Performance Data-Establishing PN response time Reply with quote

Determining the PN response time, the HMI update time and the HMI operating time for typical PROFINET IO configurations

Many applications require a quick response time via the distributed inputs and outputs. Apart from the PROFIBUS DP, SIMATIC also uses the PROFINET IO for quick and efficient data exchange between distributed I/O and S7 stations. With PROFINET IO, the Industrial Ethernet technology has now been introduced to the field level.
Typical PROFINET IO configurations consist of an IO controller with several IO devices, while additional loads such as programming devices (PG) or operator panels (OPs) or even additional S7 stations are used as data receiving stations on the Industrial Ethernet.

One of the most important questions arising in the course of configuration stil refers to the response times to be expected. It is mainly important when refitting from existing PROFIBUS DP systems to PROFINET IO:

How long does it take until a distributed output responds to a distributed input when
the processing is performed via the cyclic process image in OB1?
processing is performed via direct commands and the process alarm (OB40)?
processing is performed via a clock-synchronized interrupt (OB61)?
What fluctuations can occur?
What impact do IWLAN routes have?
To what extent does communication via PROFINET IO have an influence on the cycle time of the IO controller?
What update/operating time must be expected for the parallel operation of a panel on the controller?
What influence does a parallel cross-communication via various protocols (S7 communication, TCP/IP communication) have on the response time on the PN IO line?

With the use of Panel PCs, some further questions arise:

How do the response times behave, if a WinAC RTX as well as a WinCC flexible Runtime configuration run on a PanelPC?
What are the effects of a WinCC flexible Runtime configuration of a PanelPC on the times of additional TouchPanels?

The following screen shows the schematic layout of the measurement on a variant:
Performance Data-Establishing PN response time Performance Data-Establishing PN response time

To answer the above questions, Industry Automation and Customer Services carried out extensive measurements on typical configurations with SIMATIC components, which provide planning certainty for your plants:

Various IO controllers communicate with up to 60 I/O devices.
As an alternative, a programming device or up to 7 touch panels can be operated at the PN line of the IO controller.
The IO controller runs with a typical user program. In the programming device, the State function is active.
The IO controller can be cable-based if desired or connected via an IWLAN route or an IE/PB link with the distributed I/O.
Parallel to the IO communication a data communication of up to 8 receive S7 stations can take place.
The WinAC RTX and WinCC flexible Runtime configurations are simultaneously operated on a PanelPC.

Performance Data-Establishing PN response time Performance Data-Establishing PN response time

Access to the performance data
Click the respective version to go to the web interface of the performance data.
https://www.automation.siemens.com/perfdata/perfdata.aspx?lang=en&version=23
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> ROSIEMENS SIMATIC Automation Systems All times are GMT + 2 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group
Fa-ti si tu propriul forum GRATUIT, pe www.myforum.ro