PanelView Plus 700 (FW 6.10 ; FW 5.00) Runtime

 
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> ALLEN-BRADLEY(Rockwell Automation) Reg. U
View previous topic :: View next topic  
Author Message
vic2026
Junior
Junior


Joined: 13 Nov 2025
Posts: 5

PostPosted: 13/11/2025 23:24    Post subject: PanelView Plus 700 (FW 6.10 ; FW 5.00) Runtime Reply with quote

Context
Migrating an application from a PanelView Plus 700 (2711P-RP8D, FW 6.10.17.09) to an older PanelView Plus Logic Module (2711P-RP SER A REV B, FW 5.00.04.55 CPR9). The replacement unit is used but in good physical condition. Due to hardware limitations, it does not support firmware upgrades.
FactoryTalk View Studio Versions
- Tested on FTView Studio 11.0, 12.0, and 13.0.
- Only version 11.0 allowed successful Runtime export for FW 5.00.
Technical Steps
- Runtime Extraction (.MER) from PV 6.10
- Uploaded the .MER file (~3.3 MB) from the operational PanelView.
- Conversion to Editable Application
- Unlocked the .MER using non-standard methods.
- Restored and opened the project in FTView 11.0, 12.0, and 13.0.
- Runtime Generation for PV 5.00
- Exported explicitly as Runtime version 5.00 using FTView 11.0.
- Resulting .MER file size: ~2.7 MB.
- Field Download & Initial Test
- Application loads correctly on the replacement PanelView.
- GUI elements display properly.
- Issue: No communication with CompactLogix PLC (1769-L32E via Ethernet/IP).
Shortcut Configuration Issues
- In FactoryTalk View Studio:
- Cannot add a Local Adapter when editing the shortcut.
- Only the Ethernet Bridge (1769-L32E) with IP 192.168.1.10 appears.
- Unable to add the VA1769/A,3 ASCII module to the shortcut.
- On the physical PanelView:
- If the shortcut is deleted and recreated from the HMI interface:
- No option to add devices under Ethernet.
- Cannot create a new functional shortcut from runtime.
Communication Troubleshooting
- IP address is correctly configured and recognized on the network.
- Same IP settings as the previous PanelView.
- Tested with direct cables, crossover cables, and switches.
- Shortcut appears correctly, but no data exchange with PLC.
Questions
- Has anyone encountered similar issues when migrating to FW 5.00?
- Could this be a limitation of RSLinx Enterprise, Ethernet/IP driver, or shortcut compatibility?
- Does anyone have access to FactoryTalk View Studio 6.10.00 for deeper testing?
Any insights or suggestions would be greatly appreciated.
Back to top
View user's profile Send private message
semarif
Member
Member


Joined: 16 May 2012
Posts: 239

PostPosted: 14/11/2025 17:42    Post subject: Re: PanelView Plus 700 (FW 6.10 ; FW 5.00) Runtime Reply with quote

vic2026 wrote:
Questions
- Has anyone encountered similar issues when migrating to FW 5.00?
- Could this be a limitation of RSLinx Enterprise, Ethernet/IP driver, or shortcut compatibility?
- Does anyone have access to FactoryTalk View Studio 6.10.00 for deeper testing?
I haven't encountered any similar issues. A link to the older version of FT View ME 6.10 is in a private message.
Back to top
View user's profile Send private message
vic2026
Junior
Junior


Joined: 13 Nov 2025
Posts: 5

PostPosted: 28/11/2025 15:06    Post subject: Re: PanelView Plus 700 (FW 6.10 ; FW 5.00) Runtime Reply with quote

vic2026 wrote:
Context
Migrating an application from a PanelView Plus 700 (2711P-RP8D, FW 6.10.17.09) to an older PanelView Plus Logic Module (2711P-RP SER A REV B, FW 5.00.04.55 CPR9). The replacement unit is used but in good physical condition. Due to hardware limitations, it does not support firmware upgrades.
FactoryTalk View Studio Versions
- Tested on FTView Studio 11.0, 12.0, and 13.0.
- Only version 11.0 allowed successful Runtime export for FW 5.00.
Technical Steps
- Runtime Extraction (.MER) from PV 6.10
- Uploaded the .MER file (~3.3 MB) from the operational PanelView.
- Conversion to Editable Application
- Unlocked the .MER using non-standard methods.
- Restored and opened the project in FTView 11.0, 12.0, and 13.0.
- Runtime Generation for PV 5.00
- Exported explicitly as Runtime version 5.00 using FTView 11.0.
- Resulting .MER file size: ~2.7 MB.
- Field Download & Initial Test
- Application loads correctly on the replacement PanelView.
- GUI elements display properly.
- Issue: No communication with CompactLogix PLC (1769-L32E via Ethernet/IP).
Shortcut Configuration Issues
- In FactoryTalk View Studio:
- Cannot add a Local Adapter when editing the shortcut.
- Only the Ethernet Bridge (1769-L32E) with IP 192.168.1.10 appears.
- Unable to add the VA1769/A,3 ASCII module to the shortcut.
- On the physical PanelView:
- If the shortcut is deleted and recreated from the HMI interface:
- No option to add devices under Ethernet.
- Cannot confecționate a new functional shortcut from runtime.
Communication Troubleshooting
- IP address is correctly configured and recognized on the network.
- Same IP settings as the previous PanelView.
- Tested with direct cables, crossover cables, and switches.
- Shortcut appears correctly, but no data exchange with PLC.
Questions
- Has anyone encountered similar issues when migrating to FW 5.00?
- Could this be a limitation of RSLinx Enterprise, Ethernet/IP driver, or shortcut compatibility?
- Does anyone have access to FactoryTalk View Studio 6.10.00 for deeper testing?
Any insights or suggestions would be greatly appreciated.


issue resolved! Here’s how I got it working:

I went onsite and connected using my laptop running VMware 16 with FactoryTalk View ME v6.10.
In Communication Setup, I connected to the PLC and it auto-detected the controller and associated modules.
I selected the PLC, clicked Apply, then OK, and used Copy to Runtime.
Saved the project and generated a v5.00 runtime.

Then came the twist:

Using ME Transfer Utility, the replacement PV wasn’t recognized at first.
I rebooted the physical PC (Windows 11 Pro) where I had FT View ME v11 installed (v13 and v12 are isolated in other VMs).
From the physical machine, ME Transfer Utility finally detected the PV and I successfully downloaded the runtime.

Final surprise:

When I connected the PLC to the PV using a standard Ethernet cable — no communication.
Luckily, I had brought a crossover cable just in case… and boom, it worked instantly!
Installed the PV on the panel, ran tests, and everything’s communicating perfectly.

There are still a few minor things to improve on the machine (some servo drive tuning and cleanup), but the HMI-PLC link is solid now.
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> ALLEN-BRADLEY(Rockwell Automation) Reg. U All times are GMT + 2 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group
Fa-ti si tu propriul forum GRATUIT, pe www.myforum.ro