lokesh321 Junior

Joined: 31 Aug 2017 Posts: 1
|
Posted: 31/08/2017 13:09 Post subject: PAC DRIVE C400 ERROR 113 |
|
|
HAI
WE HAVE A PAC DRIVE C400 CONTROLLER WHICH IS CONTROLLING 7 SERVO MOTORS IN OUR FILLING MACHINE THROUGH 7 MC4 AMPLIFIERS .
WE HAVE AN ERROR 113(BLEED FAILURE).
PLEASE LET ME KNOW HOW CAN I MEASURE THE BLEED RESISTANCE VALUE TO KNOW WHETHER THIS DEFECTIVE OR NOT IN INSTALLED PAC DRIVE _________________ Lokesh |
|
| Back to top |
|
 |
suomi Junior

Joined: 31 Mar 2017 Posts: 7
|
Posted: 31/08/2017 17:10 Post subject: Re: PAC DRIVE C400 ERROR 113 |
|
|
| lokesh321 wrote: | HAI
WE HAVE A PAC DRIVE C400 CONTROLLER WHICH IS CONTROLLING 7 SERVO MOTORS IN OUR FILLING MACHINE THROUGH 7 MC4 AMPLIFIERS .
WE HAVE AN ERROR 113(BLEED FAILURE).
PLEASE LET ME KNOW HOW CAN I MEASURE THE BLEED RESISTANCE VALUE TO KNOW WHETHER THIS DEFECTIVE OR NOT IN INSTALLED PAC DRIVE |
Check the resistance with an Ohm-meter after disconnecting or
error 113
113 Bleeder defective
Diagnostic class (standard): 1
Reaction (see 8.3 Reactions of "drives"): A
A defect in the bleeder was detected by the device.
▪ Wiring: The bleeder or the feed line has a short-circuit.
▶ Check the bleeder and feed lines.
▪ The bleeder has a wrong size (too low ohm value).
▶ Check the bleeder sizing (also refer to the project planning guide and technical
data).
▪ Hardware error: Bleeder defective.
▶ Measure the bleeder
▶ Replace bleeder if necessary.
▪ Hardware error: Device with internal bleeder is defective.
▶ Replace the device.
113 bleeder defective
diagnosis class (default): 1
quittable (default): yes
reaction: A
The brake resistor (bleeder) is checked for functionality.
Cause: Wiring: Short-circuit in bleeder or cable.
Solution: Check bleeder and cables.
Cause: Wrong dimensioning of bleeder (too low Ohm value).
Solution: Check bleeder dimensioning (see also Project Manual and
Technical Data).
Cause: Hardware error: Bleeder defective.
Solution: Measure brake resistance and exchange bleeder, if necessary.
Cause: Hardware error: Servo amplifier defective.
Solution: Exchange servo amplifier. |
|