PostPosted: 27/05/2018 13:01    Post subject: "Reset to factory settings" on an MP 377 Reply with quote

How do you do a "Reset to factory settings" on an MP 377 operator panel?
https://support.industry.siemens.com/cs/document/35677293/how-do-you-do-a-reset-to-factory-settings-on-an-mp-377-operator-panel
Code:

MP 377 operator panels with the Image version installed for WinCC flexible 2008 (Image version V01.00.02.00_01.83 and higher) have the new parameter "Prepare for Reset" that has to be taken into account when resetting to factory settings.
Below is a description of how to execute an "Update OS" for the MP 377 operator panel with the option "Reset to factory settings".
No.   Procedure
1   Requirements:
The operator panel is connected to a PC via a standard Ethernet cable and ProSave is installed on that PC.
Have the MAC address of you operator panel's Ethernet interface ready.
The MAC address
- is displayed in the "PROFINET" dialog in the Control Panel.
- is displayed briefly when you switch on the operator panel.
- can be read off the back of the panel.
2   Procedure for setting the PG/PC interface:
In the "Start > Control panel" menu on the configuration PC you select the "Set PG/PC interface" command.
In the "Access Point of the Application" area you select "S7ONLINE (STEP7) -> TCP/IP".
In the "Interface Parameter Assignment Used:" area you select the interface connected to the operator panel.
Confirm your entries.
3   Procedure for resetting to factory settings:
Start the ProSave software on the PC via the Start menu.
Enter the operator panel type in the "General" tab.
Select "Ethernet" for the connection.
Enter an IP address.
(The PC's IP address and the IP address used for the MP 377 must be in the same subnetwork)

Note
There might be address conflicts if you enter the incorrect IP address.

Do not use any dynamic IP configuration for "Reset to factory settings". Enter a unique IP address of the same subnetwork in which the PC is located. ProSave assigns the specified address to the operator panel for the duration of the update process.
If you have already used the operator panel with WinCC flexible or ProSave, for "Reset to factory settings" you should use the IP address already used.

Switch to the "OS Update" tab.
Check the "Reset to factory settings" check box. An input field is displayed for the MAC address.
Enter the operator panel's MAC address in the input field.
Under "Image path" you select the operator panel image file "*.img".
The operator panel image files are located in the Installation folder of WinCC flexible under "WinCC flexible Images" and on the WinCC flexible Installation CD. If the operator panel image file opens successfully, information on the operator panel image version is displayed in the output area.
On the PC you start "Reset to factory settings" with the "Update OS" button.
In the Control Panel you open the "OP Properties" dialog and select the "Device" tab.
Click the "Reboot" button. This opens a query dialog box.
Click the "Prepare for Reset" button.
The update is started.
During the update of the operating system a status displayed is shown that indicates the progress of the process.

4   Result
A message is displayed upon successful completion of the operating system update.
There is no longer any project on the operator panel.
The factory settings have been restored.
Note
You might have to recalibrate the touch screen after restoring the factory settings.
Back to top
View user's profile Send private message
mark11
Member
Member


Joined: 30 Mar 2014
Posts: 114

PostPosted: 27/05/2018 13:05    Post subject: Which version of Image corresponding version of ProTool Reply with quote

Which version of Image of the relevant operator panels can be used for the corresponding version of ProTool?
https://support.industry.siemens.com/cs/document/28263711/which-version-of-image-of-the-relevant-operator-panels-can-be-used-for-the-corresponding-version-of-protool
When configuring Windows-based operator panels with ProTool, only one specific version of Image of the relevant operator panel can be used, regardless of the version of ProTool.
Operating system update/Reset to factory settings HMI Panels "Reset to factory settings" on an MP 377
The version specification in the name of the Image file (e.g. "MP370_V6_2.img") abstracts the version of ProTool. The precis version of the Image can be determined with ProSave or PTUpdate - see Fig. 01.
https://support.industry.siemens.com/cs/attachments/28263711/ProTool_Image_Versions_e.pdf
Back to top
View user's profile Send private message
mark11
Member
Member


Joined: 30 Mar 2014
Posts: 114

PostPosted: 27/05/2018 13:09    Post subject: connections in WinCC flexible? Reply with quote

What connections are there between the version designations in WinCC flexible?
https://support.industry.siemens.com/cs/document/21742389/what-connections-are-there-between-the-version-designations-in-wincc-flexible
Through the introduction of different new operator panels and configuration software, only specific versions of the software can be used to configure the operator panels.
Operating system update/Reset to factory settings HMI Panels "Reset to factory settings" on an MP 377
When creating a project or changing the type of operator panel in WinCC flexible 2005 and higher, you can specify the default (current) version of the operator panel (specify the version of the operator panel).
By way of example, Fig. 02 shows an MP370 Touch version 7.1.0.0 selected for WinCC flexible 2005.
Operating system update/Reset to factory settings HMI Panels "Reset to factory settings" on an MP 377
Configuration of the operator panels also depends on the edition of the Engineering Software. For example, the MP377 can be configured as from WinCC flexible 2008 and only with the Standard or Advanced edition of WinCC flexible.
https://support.industry.siemens.com/cs/attachments/21742389/WinCC_flexible_Version_e.xls
Back to top
View user's profile Send private message
mark11
Member
Member


Joined: 30 Mar 2014
Posts: 114

PostPosted: 27/05/2018 13:11    Post subject: USB Recovery (Reset to factory) 2nd Generation Basic Panels Reply with quote

USB Recovery (Reset to factory) Mode for 2nd Generation Basic Panels
https://support.industry.siemens.com/cs/document/109744950/usb-recovery- (reset-to-factory)-mode-for-2nd-generation-basic-panels
This software enables you to do a reset to factory settings for your Basic Panel 2nd Generation.
Code:
This software has been released for the following devices:

KTP400 Basic
KTP700 Basic / KTP700 Basic DP
KTP900 Basic
KTP1200 Basic / KTP1200 Basic DP

How to do a reset to factory settings for your Basic Panel 2nd Generation
Requirements
The USB stick have to be provided in FAT32 format.
The USB stick have to be provided with USB version 2.0 or lower.
The HMI device image file must be provided with Version V14.
Procedure

Unpack the file "Basic2nd_Recovery_System.zip" directly on the USB Stick into the main directory.
Copy the suitable HMI device image file into the path "SIMATIC.HMI\Recovery\" on the USB stick (file type "*.fwf").
Note: You can find the HMI device image file under
"Programs\Siemens\Automation\Portal V14\Data\Hmi\Transfer\14.0\Images".

Shut down the HMI device.
Plug the USB stick into the USB interface of the HMI device
Switch on the HMI device.
To reset the HMI device to the factory settings, press the button "START RECOVERY (..3..)" three times and follow the instructions shown on the display. At the end of the recovery process, remove the USB stick and press the "REBOOT" button.

[URL=https://www.file-upload.net/download-13153980/Basic2nd_Recovery_System.zip.html]Basic2nd_Recovery_System.zip[/URL]
Back to top
View user's profile Send private message
ALooser
Junior 2
Junior 2


Joined: 26 Oct 2018
Posts: 37

PostPosted: 13/06/2019 20:36    Post subject: How do you backup/restore with a Windows-based panel? Reply with quote

How do you backup/restore with a Windows-based panel?
https://support.industry.siemens.com/cs/document/28928853/how-do-you-backup-restore-with-a-windows-based-panel

1. Backup/Restore with ProSave
With ProSave you have a convenient option of central archiving even without ProTool or WinCC flexible. This provides you with a quick way of starting up again after a system failure or replacement of devices. The backed-up data is transferred to the new target device and the autentic status thus restored.
https://support.industry.siemens.com/cs/attachments/21907703/21907703_Back_transfer_description_e.pdf
https://support.industry.siemens.com/cs/attachments/21907703/21907703_Back_transfer_devices_e.pdf
It is not possible to load and edit a backup file in ProTool or WinCC flexible. The file can only be reloaded to the original or another panel via a restore with ProSave.
Note
Operator panel TP070 does not support backup/restore with ProSave.

=====================================
1.Preparations for Backup/Restore
Depending on the operator panel, you can use one of the following connections for a backup/restore with ProSave:
- Serial (over RS232/PPI multimaster cable) 6ES7 901-3CB30-0AX0
- Serial (over USB-PPI cable) 6ES7 901-3DB30-0XA0
- Serial (over RS232 / zero modem cable) *) 6ES7 901-1BF00-0XA0
- MPI / PROFIBUS DP
- Ethernet
- USB (host-to-host cable) information in
https://support.industry.siemens.com/cs/attachments/19142034/USB_Transfer_V1_0_e.pdf
*)You can create the zero modem cable (6ES7 901-1BF00-0XA0) yourself. More information is available in
https://support.industry.siemens.com/cs/attachments/21401061/Panel_Kommunikation_Steckerbelegung_T1_01_e.pdf
Operating system update/Reset to factory settings HMI Panels "Reset to factory settings" on an MP 377
01
If you do not have ProTool or WinCC flexible, you can also download ProSave independently - see
https://support.industry.siemens.com/cs/document/10347815/servicetool-simatic-prosave

ProSave allows a complete backup directly from the panel including the configuration. The backup created can then be loaded back into the original or an identical device.
Connect the PC with the panel and put it the panel in Transfer mode. If not configured, you can put the panel in this mode by switching the power off and on again. For this you must select and hold the Transfer button when you restart the panel.

Now the panel is in Transfer mode and ready for backup/restore.
If you want to make a restore, you can jump directly to Point 3 "Restore".
====================================
2.Backup
Open ProSave and select the correct panel in the "General" tab.
Operating system update/Reset to factory settings HMI Panels "Reset to factory settings" on an MP 377
02
Select the connection between the PC and the panel, serial (over RS232 / zero modem cable), for example.
Define the connection parameters, for example COM1 with a baud rate of 38400 for the serial connection.
Note:
In USB connections (host-to-host cable) and serial connections over USB-PPI cable, you cannot define additional connection parameters.

Switch to the "Backup" tab, select the path and specify a file name, "C:\panel.psb", for example. Under the "Data type" you define the type of backup to be created.
Note:
The file extension ".psb" is necessary, because only this file type can be loaded for a restore.
Operating system update/Reset to factory settings HMI Panels "Reset to factory settings" on an MP 377
03
When everything is set, you trigger the backup procedure with "Start Backup".
Note:
If the connection is interrupted, it might be because another software, virus scanner or power management, for example, is accessing the COM interface. Therefore, make sure that any such software is terminated before restarting.
Once the backup has been completed, the file created can now be loaded back into a device of the same type or back into the original device, as required.
===============================================
3.Restore
First put your panel in Transfer mode as described in Point 1 and set up the connection to the PC.
Select the appropriate operator panel and connection type in the "General" tab - see Fig. 02.
If possible, define the connection parameters.
Switch to the "Restore" tab in ProSave.
Open your ".psb-file" and transfer the loading procedure by clicking "Start Restore".
Operating system update/Reset to factory settings HMI Panels "Reset to factory settings" on an MP 377
04
After successful transfer of data to your panel, this is now ready to be integrated in your system after startup.

Note:
The panel has exactly the same connection parameters as the panel from which the backup originates. Make sure that both panels are not in the same system, in order to avoid connection problems.
===============================================
2. Backup/Restore with a memory card
During saving (backup), the operating system, applications and data are copied from the internal flash memory of the operator panel to the memory card.
When you restore, the flash memory of the operator panel is deleted after a prompt. Then the data backed up on the memory card is copied to the internal flash memory.
Requirements
The operator panel supports the Backup/Restore function.
A memory card is available in the operator panel with sufficient free space.
Which operator panels support backup/restore with a memory card are given in
https://support.industry.siemens.com/cs/document/21907703/how-do-you-back-transfer-the-projects-of-an-operator-panel-and-what-should-you-watch-out-for
Use of the backup/restore function depends on the operator panel. In the following we will be considering operator panels of the 177, 277 and 377 series. For other operator panels - in particular for older operator panels - please refer to the relevant manuals for the procedure.
No. Procedure
1 Preparation

Start the operator panel and open the "Control Panel".
Slot the memory card into the operator panel.
Open the "Backup/Restore" menu in the "Control Panel".
Operating system update/Reset to factory settings HMI Panels "Reset to factory settings" on an MP 377
05
If you only want to make a restore, you can jump directly to Point 3 "Restore".
=============================================
2 Backup
Click the "Backup" button in "Backup/Restore" dialog.
Operating system update/Reset to factory settings HMI Panels "Reset to factory settings" on an MP 377
06
Note
Figure 06 shows the "Backup/Restore" dialog of an operator panel with Windows CE 5.0.

=============================================
2.1 Backup - operator panels with one interface for memory cards
With operator panels with only one interface for memory cards, the memory card is automatically searched for.
a) Memory card detected
If the backup is successful, the "Backup successfully completed." dialog opens.
Acknowledge the dialog with "OK".
If there is already an old backup on the memory card, a message is issued on the operator asking whether or not you want to delete the old backup.
Acknowledge the message with "Yes" if you want to delete the old backup and făcute a new one.
Acknowledge the message with "No" if you do not want to delete the old backup and want to interrupt the current backup procedure. Acknowledge the interrupt with "OK".
A warning is displayed if the available memory is insufficient.
Use an appropriate memory card or delete all the unnecessary data in the Windows CE Explorer.
b) Memory card not detected
If there is a defective memory card in the operator panel, or none at all, then the following message is displayed.
Operating system update/Reset to factory settings HMI Panels "Reset to factory settings" on an MP 377
07
Click "OK" to close the warning.
Click "OK" to acknowledge the "Backup interrupted" message.
Repeat the procedure using an appropriate memory card.
2.2 Backup - operator panels with multiple interfaces for memory cards
In the case of operator panels with multiple interfaces for memory cards, you can select the memory card explicitly on the operator panel - see Fig. 8.
In the list box - see Fig. 08 - you select the required memory card and then click the "Start Backup" button.
Warning - possible loss of data!
When you first use a memory card, the operator panel prompts you to format it.
Click the "ESC" button to abort the formatting procedure.
If no memory card is slotted or the memory card is defective, then no memory card is displayed.
In this case, slot a memory card that functions into the operator panel.
Operating system update/Reset to factory settings HMI Panels "Reset to factory settings" on an MP 377
08
If the message is displayed indicating that a higher storage capacity is required, then proceed as follows:
Click "OK" to acknowledge the message and thus interrupt the backup.
Slot a memory card with the higher storage capacity into the operator panel.
Start the backup again.
If there is already an old backup on the memory card, you get a message asking you whether this backup should be overwritten.
Acknowledge the message with "Yes" if you want to delete the old backup and create a new one.
Acknowledge the message with "No" if you do not want to delete the old backup and want to interrupt the current backup procedure. Acknowledge the interrupt with "OK".
The backup is completed when the "Backup successfully completed..." message is displayed.
Acknowledge the message with "OK".
Remove the memory card from the operator panel.
3 Restore
Click the "Restore" button in the "Backup/Restore" dialog - see Fig. 06.
Operating system update/Reset to factory settings HMI Panels "Reset to factory settings" on an MP 377
09
Note
Figure 09 shows the "Backup/Restore" dialog of an operator panel with Windows CE 3.0.
=============================================
3.1 Restore - operator panels with one interface for memory cards
In the case of operator panels with only one interface for memory cards, you can do a restore only via that interface.
a) Memory card detected
If the memory card is detected, a message is displayed asking whether the restore procedure should be continued. Here, all the data of the flash will be deleted on the operator panel.
Acknowledge the message with "Yes" if you want to start the restore.
Acknowledge the message with "No" and then the following message with "OK" if you want to abort the restore.
Once the flash has been deleted and the Windows CE image has been successfully restored, you must reboot the operator panel.
Acknowledge the message with "OK".
Note
Do not remove the memory card from the operator panel during the restart!
As soon as the restore has been successfully completed, a message is displayed prompting you to remove the memory card from the operator panel.
Remove the memory card from the operator panel.
Acknowledge removal of the memory and reboot with "OK".
b) Memory card not detected
If there is a defective memory card in the operator panel, or none at all, then the following message is displayed.
Operating system update/Reset to factory settings HMI Panels "Reset to factory settings" on an MP 377
10
Slot an appropriate memory card into the operator panel and acknowledge this with "OK" if you want to execute the restore.
Click the "X" if you want to abort the restore procedure.
3.2 Restore - operator panels with multiple interfaces for memory cards
In the case of operator panels with multiple interfaces for memory cards, you can select the memory card explicitly on the operator panel - see Fig. 1.
In this case, you select the memory card that contains the backup.
If no memory card is slotted or the memory card is defective or the memory card contains no backup, then no memory card is displayed.
In this case, slot a memory card that functions and which contains a backup of the operator panel into the operator panel.
Only storage media containing a backup is detected.
Then click the "Start Restore" button.
If multiple external storage media with a backup are slotted on one operator panel, data restore is not possible.
Remove all the external storage media units that contain a backup and are not relevant and then click the "Refresh" button.
Alternatively you can abort the restore procedure by clicking the "Cancel" button.
Operating system update/Reset to factory settings HMI Panels "Reset to factory settings" on an MP 377
11
Once the data to be restored has been checked, a prompt is displayed querying whether you want to start Restore and in doing so whether you want to delete all the data on the flash.
Acknowledge the message with "Yes" if you want to start the restore.
Acknowledge the message with "No" and then the following message with "OK" if you want to abort the restore.
The restore is completed when the "Restore successfully finished..." message is displayed.
Click "OK" to acknowledge the message and restart the operator panel.
Additional Keywords
OP73, TP070, TP170, TP177, Mobile Panel170, Mobile Panel177, Mobile Panel277, OP77A, OP77B, TP170A, TP170B, TP177A, TP177B, OP170B, OP177, TP270, TP277, OP270, OP277, MP270, MP270B, MP277, MP370, MP377, Linux-based operator panels

Which external storage media can you use with the current SIMATIC panels and which memory card interfaces do they have?
https://support.industry.siemens.com/cs/document/21847868/which-external-storage-media-can-you-use-with-the-current-simatic-panels-and-which-memory-card-interfaces-do-they-have

How do you backup/restore with a Comfort Panel?
https://support.industry.siemens.com/cs/document/58876345/how-do-you-backup-restore-with-a-comfort-panel

How do you back transfer the projects of an operator panel and what should you watch out for?
https://support.industry.siemens.com/cs/document/21907703/how-do-you-back-transfer-the-projects-of-an-operator-panel-and-what-should-you-watch-out-for

https://megaupload.nz/U6L0jfv1n8/SIMATIC_ProSave_V15_1_exe
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> ROSIEMENS SIMATIC HMI All times are GMT + 2 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group
Fa-ti si tu propriul forum GRATUIT, pe www.myforum.ro