allvaro Junior 2

Joined: 14 Sep 2012 Posts: 26 Location: Brasil
|
Posted: 29/10/2012 15:11 Post subject: Networking from DH485 to Ethernet |
|
|
Hi
Is it possible to set up a networking PLC SLC500 DH485 to Ethernet ? How
thanks |
|
| Back to top |
|
 |
Carlos Member

Joined: 07 Jan 2012 Posts: 138
|
Posted: 30/10/2012 00:07 Post subject: |
|
|
not.
this port is not Ethernet...
only DH or RS232
(with hardware but in this time do not know the reference of the card but I know, it is quite expensive) |
|
| Back to top |
|
 |
allvaro Junior 2

Joined: 14 Sep 2012 Posts: 26 Location: Brasil
|
Posted: 30/10/2012 11:15 Post subject: |
|
|
But Is there anything a converter from DH485 to Ethernet ?
There is a converter DF1 to Ethernet model:1761-NET-ENI
Regards
Alvaro |
|
| Back to top |
|
 |
allvaro Junior 2

Joined: 14 Sep 2012 Posts: 26 Location: Brasil
|
Posted: 30/10/2012 23:55 Post subject: |
|
|
Messer, thanks
I found the price 1761-NET-ENI in Brazil is R$2000,00 I believe that EtherNet/IP Client/Server Communications Module
and
DH-485 to EtherNet/IP Communication Module
it are too expensive, but I think better to change the CPUs
I am going to try this solucions.
Thanks |
|
| Back to top |
|
 |
neuhauser Junior

Joined: 20 Jan 2012 Posts: 6
|
Posted: 02/11/2012 02:57 Post subject: |
|
|
If you don't need a lot of I/O you could take a look at the Micrologix 1400. Has 2 serial and one 100 mhz ethernet I/P port. I/O can be expanded locally. Uses Logix 500 software.
Can do Modbus messaging also. I am using some for Modbus 485 rtu to PLC 5 ethernet bridges. Also has dublu int's. |
|
| Back to top |
|
 |
allvaro Junior 2

Joined: 14 Sep 2012 Posts: 26 Location: Brasil
|
Posted: 02/11/2012 10:34 Post subject: |
|
|
| I have 18 SLC500 05/03. It to change the CPU for me don´t the soluction because the price |
|
| Back to top |
|
 |
neuhauser Junior

Joined: 20 Jan 2012 Posts: 6
|
Posted: 03/11/2012 04:42 Post subject: |
|
|
You could set up a 1400 as a data server for the DH485 network. Would most likely be cheaper than a prosoft bridge or any of the other bridges out there. (Have had some bad experiences with several.) Use a AIC to link one of the serial ports to the DH485 and pull - push data through the ethernet with a simple program in the micro.
There aren't any real cheap solutions out there. The only other solutions off the top of my head is to:
1. replace one of the 5/03s with a 5/05 (expensive) or
2. find a old pc and a serial pic or usb adapter and us it as a data server with RSLinx. I actually did this around 15 years ago with a 5/03. Not the fastest thing out there but it works. |
|
| Back to top |
|
 |
Carlos Member

Joined: 07 Jan 2012 Posts: 138
|
Posted: 03/11/2012 16:24 Post subject: |
|
|
| allvaro wrote: | | I have 18 SLC500 05/03. It to change the CPU for me don´t the soluction because the price |
(allvaro, rockwell is good but too expensive, you have to opt for a cheaper brand of hardware and I will not talk about omron or Siemens because it is too expensive... but Unitronics eg, very cheap and has modules for all query.
Please note: I am not a reseller, you understand ...
hug)
allvaro, rockwell é bom mas demasiado caro, tens de optar por uma marca de hardware mais barata e nem vou falar de omron ou siemens mas por ex unitronics, muito barato e tem modulos para tudo, consulta.
Atenção eu não sou revendedor, entendes...
abraço |
|
| Back to top |
|
 |
allvaro Junior 2

Joined: 14 Sep 2012 Posts: 26 Location: Brasil
|
Posted: 03/11/2012 16:43 Post subject: |
|
|
neuhauser
Do you know if I can to connect direct my CPUs DH485? Without I to use a 1747-AIC Coupler converter between CPUs? |
|
| Back to top |
|
 |
neuhauser Junior

Joined: 20 Jan 2012 Posts: 6
|
Posted: 04/11/2012 04:11 Post subject: |
|
|
| AB claims that the DH485 port will not directly drive a multi-drop network by it's self. |
|
| Back to top |
|
 |
allvaro Junior 2

Joined: 14 Sep 2012 Posts: 26 Location: Brasil
|
Posted: 07/11/2012 10:43 Post subject: |
|
|
Can I to connect two PLC in the 1747-AIC-Coupler? Device has two ports J1-CPU and J2-peripheral.
Thanks |
|
| Back to top |
|
 |
KNodecker Junior

Joined: 25 Nov 2012 Posts: 1
|
Posted: 25/11/2012 23:59 Post subject: |
|
|
There certainly are solutions out there. Check out:
http://www.gatewayinterfaces.com
http://www.gatewaytech1000.com
http://www.gateway-1000.com
These sites provide more information from Gateway Tech's solutions to your problem. Hopefully they'll help. |
|