Posted: 12/08/2019 21:34 Post subject: Need help with .MER file |
|
|
Hello everyone!
I'm currently working on a project using Allen Bradley ControlLogix that controls a compressor, we want to add some valves to the program and its HMI.
The problem is that, when looking for the HMI, we only found a .MER file, we couldn't open it with RSview.. it could be opened using FactoryTalk View SE, but only for visualizing not for editing.
The question is, could we actually edit the .MER file in order to add something? or is it only for visualizing?
Alternatively, we're thinking about creating a new HMI, but which will not incule all the details of the autentic one.. because our biggest problem right now is that we're running out of time..
(Just to mention, I'm new to AB and RsLogix5000)
Any help or suggestion would be greatly appreciated.
Thank you |
|
| Back to top |
|
 |
pointgrey Member

Joined: 13 Jul 2014 Posts: 140
|
Posted: 12/08/2019 23:32 Post subject: |
|
|
| .MER file is Rockwell panel view run time application. You can use "application manager for machine edition" to restore and edit the run time application. |
|
| Back to top |
|
 |
ldgo14 Junior

Joined: 06 Aug 2019 Posts: 3
|
Posted: 13/08/2019 00:14 Post subject: |
|
|
| pointgrey wrote: | | .MER file is Rockwell panel view run time application. You can use "application manager for machine edition" to restore and edit the run time application. |
Thank you for your reply!
I tried to use the application manager as you said but unfortunately I got the following message: "This runtime application file was saved in an older format that does not support conversion to a development application."
So I guess there's no chance to restore it..
Thank you again I appreciate your help. |
|
| Back to top |
|
 |
extra21 Junior

Joined: 09 Jul 2019 Posts: 1
|
Posted: 13/08/2019 14:32 Post subject: |
|
|
| pointgrey wrote: | | .MER file is Rockwell panel view run time application. You can use "application manager for machine edition" to restore and edit the run time application. |
https://theautomationblog.com/how-to-edit-a-panelview-plus-viewme-mer-runtime-file/ |
|
| Back to top |
|
 |
ldgo14 Junior

Joined: 06 Aug 2019 Posts: 3
|
Posted: 13/08/2019 19:12 Post subject: |
|
|
| extra21 wrote: | | pointgrey wrote: | | .MER file is Rockwell panel view run time application. You can use "application manager for machine edition" to restore and edit the run time application. |
https://theautomationblog.com/how-to-edit-a-panelview-plus-viewme-mer-runtime-file/ |
Thank you so much for your help it worked for me! |
|