MODBUS FOR S7 1200

 
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> Simatic Automation Systems
View previous topic :: View next topic  
Author Message
venza
Junior
Junior


Joined: 24 Nov 2015
Posts: 3

PostPosted: 29/05/2017 04:32    Post subject: MODBUS FOR S7 1200 Reply with quote

Hi everyone
I have plc s7 1200 (1214C-DC/DC/DC), module RS 485 communication vs DANFOSS VLT 2800 via MODBUS. My problems START/STOP inverter, change frequency inverter, read frequency, error inverter from HMI.
I have read manual, settings all parameter need for communication Modbus. But i don't know holding register for start/stop. I've trial value 047F for address 40001, 400001, 40002, 400002, 40003, 400003, 40004, 400004, 40005, 400005 but i can't run inverter.
When i trial 403020 ( This is parameter 302. If parameter=0 stop, = 7 start. But i think that it wrong address.
Please help me for holding register address VLT 2800.
Thanks!
_________________
vz
Back to top
View user's profile Send private message
sask
Junior 2
Junior 2


Joined: 16 Aug 2016
Posts: 24

PostPosted: 29/05/2017 09:22    Post subject: Re: MODBUS FOR S7 1200 Reply with quote

venza wrote:
Hi everyone
I have plc s7 1200 (1214C-DC/DC/DC), module RS 485 communication vs DANFOSS VLT 2800 via MODBUS. My problems START/STOP inverter, change frequency inverter, read frequency, error inverter from HMI.
I have read manual, settings all parameter need for communication Modbus. But i don't know holding register for start/stop. I've trial value 047F for address 40001, 400001, 40002, 400002, 40003, 400003, 40004, 400004, 40005, 400005 but i can't run inverter.
When i trial 403020 ( This is parameter 302. If parameter=0 stop, = 7 start. But i think that it wrong address.
Please help me for holding register address VLT 2800.
Thanks!

Registers are as
Code:
50000 Input data: Frequency converter control word register (CTW).   
ex: 047C hex = Start / 043C hex = Ramp stop   
50010 Input data: Bus reference register (REF).      
100% = 4000 hex / 16384 dec   
... ...                  
50200 Output data: Frequency converter status word register (STW).                  
50210 Output data: Frequency converter main actual value register (MAV).      


Take a look a complete description
[URL=https://userscloud.com/ioknlih6ypwh]DanfossFC102.rar - 1.0 MB[/URL]
Back to top
View user's profile Send private message
venza
Junior
Junior


Joined: 24 Nov 2015
Posts: 3

PostPosted: 30/05/2017 15:40    Post subject: Reply with quote

Hi Sack!
Thank You reply!.
Danfoss FC102 i have finished operation good. But Danfoss VLT 2800 different vs FC 102. I have tried address 50000& 50010 with value 047C unsuccessful. :weep: :weep:
_________________
vz
Back to top
View user's profile Send private message
sask
Junior 2
Junior 2


Joined: 16 Aug 2016
Posts: 24

PostPosted: 30/05/2017 16:29    Post subject: Reply with quote

venza wrote:
Hi Sack!
Thank You reply!.
Danfoss FC102 i have finished operation good. But Danfoss VLT 2800 different vs FC 102. I have tried address 50000& 50010 with value 047C unsuccessful. :weep: :weep:


What is exactly the type? You have to know if use FC101, 102 or 103>>????
Back to top
View user's profile Send private message
venza
Junior
Junior


Joined: 24 Nov 2015
Posts: 3

PostPosted: 31/05/2017 03:59    Post subject: MODBUS FOR S7 1200 Reply with quote

Hi Sask!
Inverter Danfoss: T/C: VLT 2815PT4B20SBR0DBF00A00C1, S/N: 448500A326, P/N: 178B8580, 1,5KW. INPUT 3x380V 3.2 A, OUTPUT: 3PHASE, 3.7A.
PLC: 1214C DC/DC/DC 6ES7214-1AG40-0XB0, MODULE: CM 1241 6ES7241-1CH32-0XB0, BUS CONNECT: 6ES7972-0BB52-0XA0.
Setting inverter parameter: P500 =1, P501 =5, P561 =3, P570 =2, P571 =100.
Hardware inverter connect 68, 69.
Please help me![/img]
_________________
vz
Back to top
View user's profile Send private message
sask
Junior 2
Junior 2


Joined: 16 Aug 2016
Posts: 24

PostPosted: 31/05/2017 09:28    Post subject: Re: MODBUS FOR S7 1200 Reply with quote

venza wrote:
Hi Sask!
Inverter Danfoss: T/C: VLT 2815PT4B20SBR0DBF00A00C1, S/N: 448500A326, P/N: 178B8580, 1,5KW. INPUT 3x380V 3.2 A, OUTPUT: 3PHASE, 3.7A.
PLC: 1214C DC/DC/DC 6ES7214-1AG40-0XB0, MODULE: CM 1241 6ES7241-1CH32-0XB0, BUS CONNECT: 6ES7972-0BB52-0XA0.
Setting inverter parameter: P500 =1, P501 =5, P561 =3, P570 =2, P571 =100.
Hardware inverter connect 68, 69.
Please help me![/img]

You have to set all parameters
502 Coasting Stop
Serial port (SERIAL PORT) [1]
505 Start
Serial port (SERIAL PORT) [1]
506 Reverse
Serial port (SERIAL PORT) [1]
507 Selection of Setup
Serial communication (SERIAL PORT) [1]
508 Selection of preset ref.
Serial comunication (SERIAL PORT) [1]
512 Telegram Profile
FC protocol (FC PROTOCOL) [1]
561 Protocol
Modbus RTU [3]
570 Modbus parity and message framing
(EVEN/1 STOPBIT) [0]
(ODD/1 STOPBIT) [1]
✭(NO PARITY/1 STOPBIT) [2]
(NO PARITY/2 STOPBIT) [3]
571 Modbus communications timeout
100

■Parameter list with factory settings
PNU# | Parameter description | Factory setting | 4-setup | Conv.index | Data type
004 | Active Setup | setup 1 | No | 0 | 5

Data type: Data type shows the type and length of the telegram.
Data type Description
3 Integer 16
4 Integer 32
5 Unsigned 8
6 Unsigned 16
7 Unsigned 32
9 Text string
MODBUS FOR S7 1200 MODBUS FOR S7 1200
4-Setup:
’Yes’ means that the parameter can be programmed
individually in each of the four Setups, i.e. one single
parameter can have four different data values. No’
means that the data value will be the same in all Setups.

Procedure for initialization:
1. Select Initialization [3].
2. Disconnect the AC line voltage and wait until the
light in the display has disappeared.
3. Connect the AC line voltage.
4. An initialization is performed in all parameters
in all Setups, with the exception of parameters
500 Address, 501 Baudrate, 600-605 Operating
data and 615-617 Fault log.
✭

Read carefully
http://www.grievecorp.com/Product%20Information/Component%20PDF%20Files/DANFOSS%20VLT2800%20VFD%20MANUAL.pdf
http://www.tgraf.is/Files/Library/2ead5e86-a154-4484-9761-cb46e55f10ed.pdf
http://www.triem-group.com.ua/upload/iblock/836/project_manual_vlt_2800_eng.pdf
Check communication capabilities of your drive reading parameters
MODBUS FOR S7 1200 MODBUS FOR S7 1200

This is an example for a VLT but for PROFIBUS Control.
[URL=https://userscloud.com/f1g11e91969y]pcablockdescription.zip - 466 KB[/URL]
Back to top
View user's profile Send private message
6ES7214-1AG40-0XB0
Junior
Junior


Joined: 11 Dec 2017
Posts: 2

PostPosted: 11/12/2017 13:20    Post subject: Reply with quote

the answer so profession and detail, thanks
_________________
SIMATIC S7-1200, CPU 1214C, COMPACT CPU, DC/DC/DC, ONBOARD I/O: 14 DI 24V DC; 10 DO 24 V DC; 2 AI 0 – 10V DC, POWER SUPPLY: DC 20.4 – 28.8 V DC, PROGRAM/DATA MEMORY: 100 KB
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> Simatic Automation Systems All times are GMT + 2 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group
Fa-ti si tu propriul forum GRATUIT, pe www.myforum.ro