Mail s7-1200

 
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> Simatic Automation Systems
View previous topic :: View next topic  
Author Message
touma02
Junior
Junior


Joined: 16 Jul 2012
Posts: 9

PostPosted: 12/09/2015 11:25    Post subject: Mail s7-1200 Reply with quote

Hello

Is it possible to send value of word like mw100 in mail?

If yes, how you use tm-mail for this ?

Thx
Back to top
View user's profile Send private message
kaka
Member
Member


Joined: 16 Mar 2014
Posts: 154

PostPosted: 12/09/2015 13:21    Post subject: Re: Mail s7-1200 Reply with quote

touma02 wrote:
Hello

Is it possible to send value of word like mw100 in mail?

If yes, how you use tm-mail for this ?

Thx

The TM_MAIL instruction sends an e-mail using SMTP (Simple Mail Transfer Protocol) by means of TCP/IP over the Industrial Ethernet connection of the CPU. You need an Ethernet-based internet connection or a TeleService adapter for the connection with telephone network lines.
https://support.industry.siemens.com/cs/document/67262019/how-do-you-parameterize-the-%22tm_mail%22-instruction-to-send-e-mails-with-the-simatic-s7-1200
Back to top
View user's profile Send private message
touma02
Junior
Junior


Joined: 16 Jul 2012
Posts: 9

PostPosted: 12/09/2015 15:39    Post subject: Reply with quote

It'is not an answer of my question...
Back to top
View user's profile Send private message
tecnoplc
Junior 2
Junior 2


Joined: 03 Feb 2016
Posts: 40
Location: Spain

PostPosted: 03/02/2016 08:52    Post subject: Reply with quote

please if someone knows the answer for this ítem, Write the solution. I am very interested in.
thank you.
_________________
_______________________________________
Programming PLC and HMI
www.tecnoplc.com
Back to top
View user's profile Send private message Send e-mail
kaka
Member
Member


Joined: 16 Mar 2014
Posts: 154

PostPosted: 23/02/2016 21:09    Post subject: Reply with quote

touma02 wrote:
It'is not an answer of my question...


you do not read with attention ...
Mail s7-1200 Re: Mail s7-1200

On Inputs of the "TMAIL_C" instruction

you have ATTACHMENT Variant E-mail attachment (optional)

Reference to a byte/word/double word field (ArrayOfByte, ArrayOfWord, ArrayOfDWors) with a maximum length of 64 kbyte.
If no value is assigned, the e-mail is sent without an attachment.

What you need to do is to move your values (remember max 64 KBytes) from MW100 to array of word and in attachment put the pointer to that area....


Last edited by kaka on 07/06/2018 16:24; edited 1 time in total
Back to top
View user's profile Send private message
kaka
Member
Member


Joined: 16 Mar 2014
Posts: 154

PostPosted: 06/03/2016 13:54    Post subject: Sending of Emails to SMTP Server with a S7-CPU Reply with quote

Sending of Emails to SMTP Server with a S7-CPU
https://support.industry.siemens.com/cs/document/46817803/sending-of-emails-to-smtp-server-with-a-s7-cpu

With the help of a FB PN_Mail (FB490) function block, emails can be sent to any SMTP server from
S7-300/400 CPUs
ET200S/IM151 distributed I/Os
ET200PRO/IM154-8 CPUs
WinAC computers such as SIMATIC Microbox PCs

Mail s7-1200 Re: Mail s7-1200

Triggering the sending can be made dependent on any system events (variable states, error messages, expiry of deadlines). In the attachment of the mails up to 64kByte binary data can be transmitted. For the secure authentication the established SMTP-AUTH method is used.

Note
For the S7-1200 and the S7-1500, instructions for the use of the CPUs are provided already by STEP 7 as SMTP client.


STEP7 V5.5
https://support.industry.siemens.com/cs/attachments/46817803/46817803_SMTP_Mailversand_DOKU_V15_en.pdf
https://support.industry.siemens.com/cs/attachments/46817803/46817803_SMTP-Mailversand_CODE_15.zip

STEP7 V12
https://support.industry.siemens.com/cs/attachments/46817803/46817803_SMTP_Mail_DOKU_V12_V1_0_en.pdf
https://support.industry.siemens.com/cs/attachments/46817803/46817803_SMTP_V12_CODE_V1_0.zip


Last edited by kaka on 07/06/2018 16:24; edited 1 time in total
Back to top
View user's profile Send private message
kaka
Member
Member


Joined: 16 Mar 2014
Posts: 154

PostPosted: 04/01/2018 13:05    Post subject: TMAIL_C instruction to send e-mails withS7-1200 and S7-1500 Reply with quote

How do you parameterize the "TMAIL_C" instruction to send e-mails with the SIMATIC S7-1200 and S7-1500?

https://support.industry.siemens.com/cs/document/67262019/
Using the "TMAIL_C" instruction to send e-mails with the SIMATIC S7-1200 and SIMATIC S7-1500.

The "TMAIL_C" instruction uses the SMTP (Simple Mail Transfer Protocol) to send an e-mail via the Ethernet interface of the S7-1200 > V4.0 or a communications processor (CP).

Using the "TMAIL_C" instruction, with version V4.0 and higher you can send e-mails via Secure Communication through the Ethernet interface of the following modules:
CP 1543-1 V2.0
CP 1542SP-1 IRC V1.0
CP 1543SP-1 V1.0
CP 1243-1 V2.1 and higher
CP 1242-7 GPRS V2 V2.1 and higher
CP 1243-7 LTE V2.1 and higher
CP 1243-8 V2.1 and higher

Via the system data type "TMAIl_V4_SEC", "TMAIL_V6_SEC" or "TMAIL_QDN_SEC" you define the data necessary for sending the e-mail including the TCP port of the e-mail server.
For the sake of compatibility you can also use the previous system data types "TMAIL_V4", "TMAIL_V6" and "TMAIL_FQDN". In this case you can also send an e-mail via the Ethernet interfaces of the CPUs and the Ethernet interface of the CP 1543-1.
Hardware requirements
In this example an e-mail is sent via an Ethernet-based internet connection. The following hardware components are used:
S7-1200 CPU
DSL router for access to the internet
The figure below shows the call of the "TMAIL_C" instruction including instance data block DB1 and an example of how to parameterize the inputs and outputs of the "TMAIL_C" instruction.

Mail s7-1200 Re: Mail s7-1200
Mail s7-1200 Re: Mail s7-1200
Mail s7-1200 Re: Mail s7-1200
Mail s7-1200 Re: Mail s7-1200
Mail s7-1200 Re: Mail s7-1200
Note
In the CPU you must activate the router and set the correct IP address of the router. Otherwise the CPU cannot reach the public IP address of the e-mail server.
Via the Ethernet interface of the CPU the TMAIL_C instruction can communicate with an e-mail server using SMTP via Port 25. The assigned port number cannot be changed.
Via the CP the "TMAIL_C" instruction can establish a secure connection (SNMP over TSL) to an e-mail server.

In company networks which only permit internet access by proxy and usually block all the other ports including Port 25, you cannot use the "TMAIL_C" instruction to establish a connection to external e-mail servers via the Ethernet interface of the CPU . It must be possible to communicate externally over the TCP Port 25.
You can establish a connection through SMTP with an internal e-mail server and let the internal server manage the current security extensions required to forward e-mails via the internet to an external e-mail server.
Alternatively you can use a CP to establish a secure connection (SMTP over TSL) to an e-mail server with the "TMAIL_C" instruction.
https://support.industry.siemens.com/cs/document/46817803/sending-emails-to-smtp-servers-with-an-s7-cpu

Note
You should always implement Defense in Depth before connecting a CPU to the internet.
In the Security Siemens Operational Guidelines we give clear recommendations about how to act when connecting control components with office servers, in this example the e-mail server . It might be necessary to use a DMZ solution.

Further Information
Detailed information about the "TMAIL_C" instruction is available in the manual "STEP 7 Professional V14 SP1"
STEP 7 Professional V14 SP1
https://support.industry.siemens.com/cs/attachments/109747136/STEP_7_Professional_V14_1_enUS_en-US.pdf


Last edited by kaka on 07/06/2018 16:25; edited 1 time in total
Back to top
View user's profile Send private message
grig100
Member 3
Member 3
grig100

Joined: 01 Jan 2015
Posts: 752

PostPosted: 06/04/2018 19:57    Post subject: parameterize the "TMAIL_C" instruction S7-1200 an Reply with quote

How do you parameterize the "TMAIL_C" instruction to send e-mails with the SIMATIC S7-1200 and S7-1500?
https://support.industry.siemens.com/cs/document/67262019/
Using the "TMAIL_C" instruction to send e-mails with the SIMATIC S7-1200 and SIMATIC S7-1500.

The "TMAIL_C" instruction uses the SMTP (Simple Mail Transfer Protocol) to send an e-mail via the Ethernet interface of the S7-1200 > V4.0 or a communications processor (CP).
Using the "TMAIL_C" instruction, with version V4.0 and higher you can send e-mails via Secure Communication through the Ethernet interface of the following modules:
Code:
   CP 1543-1 V2.0
    CP 1542SP-1 IRC V1.0
    CP 1543SP-1 V1.0
    CP 1243-1 V2.1 and higher
    CP 1242-7 GPRS V2 V2.1 and higher
    CP 1243-7 LTE V2.1 and higher
    CP 1243-8 V2.1 and higher

Via the system data type "TMAIl_V4_SEC", "TMAIL_V6_SEC" or "TMAIL_QDN_SEC" you define the data necessary for sending the e-mail including the TCP port of the e-mail server.
For the sake of compatibility you can also use the previous system data types "TMAIL_V4", "TMAIL_V6" and "TMAIL_FQDN". In this case you can also send an e-mail via the Ethernet interfaces of the CPUs and the Ethernet interface of the CP 1543-1.

Hardware requirements
In this example an e-mail is sent via an Ethernet-based internet connection. The following hardware components are used:
S7-1200 CPU
DSL router for access to the internet
The figure below shows the call of the "TMAIL_C" instruction including instance data block DB1 and an example of how to parameterize the inputs and outputs of the "TMAIL_C" instruction.

Note
In the CPU you must activate the router and set the correct IP address of the router. Otherwise the CPU cannot reach the public IP address of the e-mail server.
Via the Ethernet interface of the CPU the TMAIL_C instruction can communicate with an e-mail server using SMTP via Port 25. The assigned port number cannot be changed.
Via the CP the "TMAIL_C" instruction can establish a secure connection (SNMP over TSL) to an e-mail server.
Mail s7-1200 Re: Mail s7-1200
Mail s7-1200 Re: Mail s7-1200
Mail s7-1200 Re: Mail s7-1200
Mail s7-1200 Re: Mail s7-1200

In company networks which only permit internet access by proxy and usually block all the other ports including Port 25, you cannot use the "TMAIL_C" instruction to establish a connection to external e-mail servers via the Ethernet interface of the CPU . It must be possible to communicate externally over the TCP Port 25.
You can establish a connection through SMTP with an internal e-mail server and let the internal server manage the current security extensions required to forward e-mails via the internet to an external e-mail server.
Alternatively you can use a CP to establish a secure connection (SMTP over TSL) to an e-mail server with the "TMAIL_C" instruction.

The application example "Send e-mails to SMTP server with an S7-CPU" describes the following tasks :
Code:
   Configure the Jana Server as internal mail server to forward an e-mail to an external mail server.
    Establish a secure connection (SMTP over TSL) to an e-mail server via the CP.

https://support.industry.siemens.com/cs/attachments/46817803/46817803_EMail_with_CP1543-1_en.pdf
https://support.industry.siemens.com/cs/attachments/46817803/46817803_smtp-mailversand_code_v10.zip
Note
You should always implement Defense in Depth before connecting a CPU to the internet.
In the Security Siemens Operational Guidelines we give clear recommendations about how to act when connecting control components with office servers, in this example the e-mail server . It might be necessary to use a DMZ solution.
https://support.industry.siemens.com/cs/document/46817803/

Further Information
More information is available in the STEP 7 (TIA Portal) manual under Description of TMAIL_C (S7-1200, S7-1500).
https://support.industry.siemens.com/cs/mdm/109755202?c=85840577163&lc=en-WW
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> Simatic Automation Systems All times are GMT + 2 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group
Fa-ti si tu propriul forum GRATUIT, pe www.myforum.ro