PostPosted: 28/09/2018 13:29    Post subject: M221 PROBLEM WITH I/O EXPANSION BUS Reply with quote

Hello!
I am using PLC TM221CE16R and SoMachine Basic v1.6. My PLC has firmware 1.6.0.1. I use analog expansion bus, input module TM3AI8. Everything was working fine for 2 hours until suddenly I got next message in SoMachine Basic: I/O expansion configured but is absent or inoperative. I/O expansion bus is not started.

Since then ERR LED is always blinking. I already tried deleting program, updating firmware, removing expansion module in configuration page, removing/adding physical module, selected module as Optional, removing battery - nothing helped. If I try removing application, ERR LED is still blinking. Seems like I can't delete previous program, something like config file is burned into PLC.

Can anybody please help me? It is really frustrating[url=http://www.99poze.ro/p/33e2aa2086d212e55834ef9267aae0b8.jpg]M221 PROBLEM WITH I/O EXPANSION BUS M221 PROBLEM WITH I/O EXPANSION BUS[/url]+[url=http://www.99poze.ro/p/a7a71dd2f63f75db42f2d7489d6a2380.jpg]M221 PROBLEM WITH I/O EXPANSION BUS M221 PROBLEM WITH I/O EXPANSION BUS[/url]+[url=http://www.99poze.ro/p/4302ea42402209adf3a1c9bde3502f27.jpg]M221 PROBLEM WITH I/O EXPANSION BUS M221 PROBLEM WITH I/O EXPANSION BUS[/url]+
Back to top
View user's profile Send private message
mikoian
Junior
Junior


Joined: 12 Jan 2018
Posts: 6

PostPosted: 28/09/2018 16:32    Post subject: PLC TM221CE16R Reply with quote

The CPU is PLC TM221CE16R
M221 PROBLEM WITH I/O EXPANSION BUS M221 PROBLEM WITH I/O EXPANSION BUS

Try extension modules for TM2 to check if works
M221 PROBLEM WITH I/O EXPANSION BUS M221 PROBLEM WITH I/O EXPANSION BUS

Code:
I/O expansion modules can be marked as optional in the configuration. The Optional module feature provides a more flexible configuration by the acceptance of the definition of modules that
are not physically attached to the logic controller. Therefore, a single application can support multiple physical configurations of I/O expansion modules, allowing a greater degree of scalability without the necessity of maintaining numeroase application files for the same application.
Without the Optional module feature, when the logic controller starts up the I/O expansion bus (following a power cycle, application download or initialization command), it compares the configuration defined in the application with the physical I/O modules attached to the I/O bus.
Among other diagnostics made, if the logic controller determines that there are I/O modules defined in the configuration that are not physically present on the I/O bus, an error is detected and the I/O bus does not start.
With the Optional module feature, the logic controller ignores the absent I/O expansion modules that you have marked as optional, which then allows the logic controller to start the I/O expansion bus.
The logic controller starts the I/O expansion bus at configuration time (following a power cycle, application download, or initialization command) even if optional expansion modules are not physically connected to the logic controller.
The following module types can be marked as optional:
 TM3 I/O expansion modules

%SW118 Logic controller status word
Bits 13 and 14 are pertinent to the I/O module status relative to the I/O bus.
Bit 13, if FALSE, indicates that there are mandatory modules as defined by the I/O expansion bus configuration that are absent or otherwise inoperative when the logic controller attempts to start the I/O expansion bus.
In this case, the I/O bus does not start.
Bit 14, if FALSE, indicates that one or more modules have ceased
communication with the logic controller after the I/O expansion bus is started.
This is the case whether an I/O expansion module is defined as mandatory or as an optional module but present at start-up.
%SW119 I/O expansion module configuration
Each bit, starting with bit 1 (bit 0 is reserved), is dedicated to a configured I/O expansion module and indicates whether the module is optional (TRUE) or mandatory (FALSE) when the controller attempts to start the I/O bus.
%SW120 I/O expansion module status
Each bit, starting with bit 1 (bit 0 is reserved), is dedicated to a configured
I/O expansion module and indicates the status of the module.
When the logic controller attempts to start the I/O bus, if the value of %SW120 is non-zero (indicating that an error is detected for at least one of the modules), the I/O expansion bus does not start unless the corresponding bit in %SW119 is set to TRUE (indicating the module is marked as an optional module).
When the I/O bus is started, if the value of %SW120 is modified by the system, it indicates that an error is detected on one or more I/O expansion modules (regardless of the Optional module feature).
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> Schneider_Electric Reg. U All times are GMT + 2 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group
Fa-ti si tu propriul forum GRATUIT, pe www.myforum.ro