Logix Controller 5571 USB Connect Problem

 
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> ALLEN-BRADLEY(Rockwell Automation) Reg. U
View previous topic :: View next topic  
Author Message
SohrabB
Junior 2
Junior 2


Joined: 04 May 2012
Posts: 29

PostPosted: 26/08/2017 12:13    Post subject: Logix Controller 5571 USB Connect Problem Reply with quote

Hi, Everyone Can you help me?

I have for connect USB to Logix Controller 5571 in Windows 7 x64 and Windows 10 Enterprise x64 (USB connect 3 second and disconnect for 45 second and repeat again)

RSLinx Classic Status: Comm. error 01E00204 (45 Second)

RSLinx Classic Status: Major Fault (3 Second)

Thanks
Back to top
View user's profile Send private message
beatrice
Junior
Junior


Joined: 25 Aug 2017
Posts: 8

PostPosted: 26/08/2017 13:47    Post subject: Re: Logix Controller 5571 USB Connect Problem Reply with quote

SohrabB wrote:
Hi, Everyone Can you help me?

I have for connect USB to Logix Controller 5571 in Windows 7 x64 and Windows 10 Enterprise x64 (USB connect 3 second and disconnect for 45 second and repeat again)

RSLinx Classic Status: Comm. error 01E00204 (45 Second)

RSLinx Classic Status: Major Fault (3 Second)

Thanks


put exactly the type for firmware upgrade./..
Back to top
View user's profile Send private message
SohrabB
Junior 2
Junior 2


Joined: 04 May 2012
Posts: 29

PostPosted: 26/08/2017 18:15    Post subject: Re: Logix Controller 5571 USB Connect Problem Reply with quote

beatrice wrote:
SohrabB wrote:
Hi, Everyone Can you help me?

I have for connect USB to Logix Controller 5571 in Windows 7 x64 and Windows 10 Enterprise x64 (USB connect 3 second and disconnect for 45 second and repeat again)

RSLinx Classic Status: Comm. error 01E00204 (45 Second)

RSLinx Classic Status: Major Fault (3 Second)

Thanks


put exactly the type for firmware upgrade./..


Thanks
The firmware is installed by the company and its Rev. is 20.011.59.
After power on without SD Cart:
TEST -> WAIT -> TEST -> CHRG -> PASS -> REV. 20.011.59
and repeat again.
Back to top
View user's profile Send private message
beatrice
Junior
Junior


Joined: 25 Aug 2017
Posts: 8

PostPosted: 26/08/2017 18:59    Post subject: Re: Logix Controller 5571 USB Connect Problem Reply with quote

SohrabB wrote:
beatrice wrote:
SohrabB wrote:
Hi, Everyone Can you help me?

I have for connect USB to Logix Controller 5571 in Windows 7 x64 and Windows 10 Enterprise x64 (USB connect 3 second and disconnect for 45 second and repeat again)

RSLinx Classic Status: Comm. error 01E00204 (45 Second)

RSLinx Classic Status: Major Fault (3 Second)

Thanks


put exactly the type for firmware upgrade./..


Thanks
The firmware is installed by the company and its Rev. is 20.011.59.
After power on without SD Cart:
TEST -> WAIT -> TEST -> CHRG -> PASS -> REV. 20.011.59
and repeat again.


What type...??? and what version Studio ?
Back to top
View user's profile Send private message
SohrabB
Junior 2
Junior 2


Joined: 04 May 2012
Posts: 29

PostPosted: 26/08/2017 19:38    Post subject: Re: Logix Controller 5571 USB Connect Problem Reply with quote

beatrice wrote:
SohrabB wrote:
beatrice wrote:
SohrabB wrote:
Hi, Everyone Can you help me?

I have for connect USB to Logix Controller 5571 in Windows 7 x64 and Windows 10 Enterprise x64 (USB connect 3 second and disconnect for 45 second and repeat again)

RSLinx Classic Status: Comm. error 01E00204 (45 Second)

RSLinx Classic Status: Major Fault (3 Second)

Thanks


put exactly the type for firmware upgrade./..


Thanks
The firmware is installed by the company and its Rev. is 20.011.59.
After power on without SD Cart:
TEST -> WAIT -> TEST -> CHRG -> PASS -> REV. 20.011.59
and repeat again.


What type...??? and what version Studio ?


RSLogix Studio5000 v30.00.00 full license.
Back to top
View user's profile Send private message
beatrice
Junior
Junior


Joined: 25 Aug 2017
Posts: 8

PostPosted: 26/08/2017 21:48    Post subject: Reply with quote

CPU Type?
Back to top
View user's profile Send private message
SohrabB
Junior 2
Junior 2


Joined: 04 May 2012
Posts: 29

PostPosted: 26/08/2017 22:16    Post subject: Reply with quote

beatrice wrote:
CPU Type?


Logix5571 or 1756-L71 /B
Back to top
View user's profile Send private message
beatrice
Junior
Junior


Joined: 25 Aug 2017
Posts: 8

PostPosted: 26/08/2017 22:38    Post subject: Reply with quote

SohrabB wrote:
beatrice wrote:
CPU Type?


Logix5571 or 1756-L71 /B

Tell to the guys from the company that they did not update firmware... and they did a dirty job.....
The latest version of firmware for 1756-L71 /B for Studio 30 is here .. .
Download and upgrade yourself............or tell to that guys they are underrated....
[URL=https://userscloud.com/p7ypib87w4mr]1756-L71_30.012.dmk - 2.5 MB[/URL]
[URL=https://userscloud.com/pj5k1h567mke]1756-L71_B_30.012.pdf - 122 KB[/URL]
Back to top
View user's profile Send private message
SohrabB
Junior 2
Junior 2


Joined: 04 May 2012
Posts: 29

PostPosted: 26/08/2017 23:39    Post subject: Reply with quote

beatrice wrote:
SohrabB wrote:
beatrice wrote:
CPU Type?


Logix5571 or 1756-L71 /B

Tell to the guys from the company that they did not update firmware... and they did a dirty job.....
The latest version of firmware for 1756-L71 /B for Studio 30 is here .. .
Download and upgrade yourself............or tell to that guys they are underrated....
[URL=https://userscloud.com/p7ypib87w4mr]1756-L71_30.012.dmk - 2.5 MB[/URL]
[URL=https://userscloud.com/pj5k1h567mke]1756-L71_B_30.012.pdf - 122 KB[/URL]


Thanks

I can not connect to the CPU with USB. How can i update it?
Back to top
View user's profile Send private message
banguy
Member junior
Member junior


Joined: 01 Mar 2017
Posts: 59

PostPosted: 27/08/2017 19:26    Post subject: Allen-Bradley CompactLogix Firmware Upgrade Reply with quote

this is some help not necessary for this cae
[URL=https://userscloud.com/8j4lfs0g3wr4]Allen-Bradley 5370 L3 PLC IP Addressing.pdf - 219 KB[/URL]
[URL=https://userscloud.com/bv8kf5g0jf2t]Allen-Bradley CompactLogix Firmware Upgrade.pdf - 287 KB[/URL]
[URL=https://userscloud.com/7vwkqmcqnehl]Allen-Bradley CompactLogix L2 PLC Connect.pdf - 176 KB[/URL]
Back to top
View user's profile Send private message
SohrabB
Junior 2
Junior 2


Joined: 04 May 2012
Posts: 29

PostPosted: 27/08/2017 20:19    Post subject: Re: Allen-Bradley CompactLogix Firmware Upgrade Reply with quote

banguy wrote:
this is some help not necessary for this cae
[URL=https://userscloud.com/8j4lfs0g3wr4]Allen-Bradley 5370 L3 PLC IP Addressing.pdf - 219 KB[/URL]
[URL=https://userscloud.com/bv8kf5g0jf2t]Allen-Bradley CompactLogix Firmware Upgrade.pdf - 287 KB[/URL]
[URL=https://userscloud.com/7vwkqmcqnehl]Allen-Bradley CompactLogix L2 PLC Connect.pdf - 176 KB[/URL]


Thank you for your cooperation.

I can not connect with Ethernet and USB to controller (Controller is not accessibility).
is there any way to hardware reset for controller Logix5571? (same SLC 5/05 CPU)[url=http://www.girlshare.ro/3489916128.6]Logix5571_USB_error_1.jpg[/url][url=http://www.girlshare.ro/3489916129.7]Logix5571_USB_error_2.jpg[/url]
Picture 1 3 second Picture 2 45 secound
Back to top
View user's profile Send private message
SohrabB
Junior 2
Junior 2


Joined: 04 May 2012
Posts: 29

PostPosted: 28/08/2017 10:53    Post subject: Re: Allen-Bradley CompactLogix Firmware Upgrade Reply with quote

SohrabB wrote:
banguy wrote:
this is some help not necessary for this cae
[URL=https://userscloud.com/8j4lfs0g3wr4]Allen-Bradley 5370 L3 PLC IP Addressing.pdf - 219 KB[/URL]
[URL=https://userscloud.com/bv8kf5g0jf2t]Allen-Bradley CompactLogix Firmware Upgrade.pdf - 287 KB[/URL]
[URL=https://userscloud.com/7vwkqmcqnehl]Allen-Bradley CompactLogix L2 PLC Connect.pdf - 176 KB[/URL]


Thank you for your cooperation.

I can not connect with Ethernet and USB to controller (Controller is not accessibility).
is there any way to hardware reset for controller Logix5571? (same SLC 5/05 CPU)[url=http://www.girlshare.ro/3489916128.6]Logix5571_USB_error_1.jpg[/url][url=http://www.girlshare.ro/3489916129.7]Logix5571_USB_error_2.jpg[/url]
Picture 1 3 second Picture 2 45 secound


I solved my problem (Selector Switch Problem).

Thanks ..................
Back to top
View user's profile Send private message
beatrice
Junior
Junior


Joined: 25 Aug 2017
Posts: 8

PostPosted: 28/08/2017 16:24    Post subject: Reply with quote

Well ..good news...
I hoped that you did not mess up the processor....
for other users....

Normally through IP you have to do all of these..The IP address remains accessible...
For hardware Reset You need to disconnect the processor battery, CompactFlash card must be removed too. wait 30+ minutes, reconnect it, and hopefully you'll get your processor back!

The steps are as in manual:
If
You meet all of these conditions.
Quote:
•The controller has a memory card.
•The project on the memory card has a revision = 12.0.
•The project on the memory card has a Load Image option = On Power Up or On Corrupt Memory.
•A controller in service has a revision = 12.0.

Then
Update the firmware by using one of these options.
Quote:
•Memory card
•Logix Designer application
•ControlFLASH™ software (See the Important: note on the next page)


Follow this procedure to update the firmware and load the project by using the memory card.
Quote:
1.Install the card in the controller.
2.If the Load Image option = On Corrupt Memory and the controller contains a project,
before powering down,disconnect the battery or disengage the Energy Storage Module (ESM) from the controller.
3.Turn on or cycle power to the controller.


Follow this procedure if you use the Logix Designer application or ControlFLASH software to update the firmware.
Quote:
1.Remove the card from the controller.
This prevents the controller from setting the Load Image option of the memory card to User Initiated during the update.
2.After the firmware update is completed, store the project to the memory card.
This ensures that the revision of the project on the memory card matches the revision of the controller.


If You do not meet all of the preceding conditions
Update the firmware by using either:
Quote:
•Logix Designer application.
•ControlFLASH software. See the Important: note on the next page.

Take these precautions.
Quote:
•Before you update the firmware either:
- Remove the memory card from the controller.
- Check the Load Image option of the memory card.
If it is set to On Power Up or On Corrupt Memory, store the project with the Load Image option set to User Initiated.
Otherwise, a major fault may occur when you update the controller firmware.
This occurs because the On Power Up or On Corrupt Memory options cause the controller to load the project from the memory card.
The firmware mismatch after the load causes a major fault.
•After you update the firmware, store the project to the memory card to ensure the revision of the project on the memory card
matches the revision of the controller.

Important:
Make sure the SD card is unlocked if set to load On Power Up before using the ControlFLASH software.
otherwise, the updated data may be overwritten by firmware on the SD card. An error message appears.
See the ControlLogix System User Manual, publication 1756-UM001 before updating.
Also, while it is not required for operation, leave the SD card installed in the controller.

The SD card saves extended diagnostic information that you can send to Rockwell Automation that provides enhanced diagnostics of your controller application and firmware should circumstances require this data.
Back to top
View user's profile Send private message
SohrabB
Junior 2
Junior 2


Joined: 04 May 2012
Posts: 29

PostPosted: 28/08/2017 17:29    Post subject: Reply with quote

beatrice wrote:
Well ..good news...
I hoped that you did not mess up the processor....
for other users....

Normally through IP you have to do all of these..The IP address remains accessible...
For hardware Reset You need to disconnect the processor battery, CompactFlash card must be removed too. wait 30+ minutes, reconnect it, and hopefully you'll get your processor back!

The steps are as in manual:
If
You meet all of these conditions.
Quote:
•The controller has a memory card.
•The project on the memory card has a revision = 12.0.
•The project on the memory card has a Load Image option = On Power Up or On Corrupt Memory.
•A controller in service has a revision = 12.0.

Then
Update the firmware by using one of these options.
Quote:
•Memory card
•Logix Designer application
•ControlFLASH™ software (See the Important: note on the next page)


Follow this procedure to update the firmware and load the project by using the memory card.
Quote:
1.Install the card in the controller.
2.If the Load Image option = On Corrupt Memory and the controller contains a project,
before powering down,disconnect the battery or disengage the Energy Storage Module (ESM) from the controller.
3.Turn on or cycle power to the controller.


Follow this procedure if you use the Logix Designer application or ControlFLASH software to update the firmware.
Quote:
1.Remove the card from the controller.
This prevents the controller from setting the Load Image option of the memory card to User Initiated during the update.
2.After the firmware update is completed, store the project to the memory card.
This ensures that the revision of the project on the memory card matches the revision of the controller.


If You do not meet all of the preceding conditions
Update the firmware by using either:
Quote:
•Logix Designer application.
•ControlFLASH software. See the Important: note on the next page.

Take these precautions.
Quote:
•Before you update the firmware either:
- Remove the memory card from the controller.
- Check the Load Image option of the memory card.
If it is set to On Power Up or On Corrupt Memory, store the project with the Load Image option set to User Initiated.
Otherwise, a major fault may occur when you update the controller firmware.
This occurs because the On Power Up or On Corrupt Memory options cause the controller to load the project from the memory card.
The firmware mismatch after the load causes a major fault.
•After you update the firmware, store the project to the memory card to ensure the revision of the project on the memory card
matches the revision of the controller.

Important:
Make sure the SD card is unlocked if set to load On Power Up before using the ControlFLASH software.
otherwise, the updated data may be overwritten by firmware on the SD card. An error message appears.
See the ControlLogix System User Manual, publication 1756-UM001 before updating.
Also, while it is not required for operation, leave the SD card installed in the controller.

The SD card saves extended diagnostic information that you can send to Rockwell Automation that provides enhanced diagnostics of your controller application and firmware should circumstances require this data.


I installed RSLogix Studio 5000 v20.01.01 software as a result of the version matching problem (for solved firmware matching).
everything is good But controller gives the following message (LED OK is RED):
" Major Fault T01: C60 Non-recoverable "
Can you help me to solve the problem?
The project is installed in controller is locked (Is not my project and I have not project source).[url=http://www.girlshare.ro/3489916860.1]Logix5571_Protected.jpg[/url]
" Major Fault T01: C60 Non-recoverable " (<- I solved this Problem)
Back to top
View user's profile Send private message
beatrice
Junior
Junior


Joined: 25 Aug 2017
Posts: 8

PostPosted: 30/08/2017 08:32    Post subject: Reply with quote

Regarding Error 1443-80043B02
Logix Controller 5571 USB Connect Problem Logix Controller 5571 USB Connect Problem


This error is tied to SQL Server Database Mirroring error 1443 – Connection Handshake Failed
STATUS_AUTHENTICATION_FIREWALL_FAILED

Check your firewall and make modifications for this certificate ...
you act as an administrator?
Your computer is an a domain?
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> ALLEN-BRADLEY(Rockwell Automation) Reg. U All times are GMT + 2 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group
Fa-ti si tu propriul forum GRATUIT, pe www.myforum.ro