Ahmad233 Junior

Joined: 21 May 2017 Posts: 4
|
Posted: 30/05/2017 21:09 Post subject: Interfacing PLC B&R to Bosch Valve |
|
|
Hallo
I am new with CANopen and CAN bus.
I have a problem with old Bosch Valve controlled by B&R plc cp470.
PLC is empty .. but it is the same PLC which controlled previously this valve.
I need to change the control mode from CAN to analog.
Unfortunately less information I got to control this valve. I attached them.
I asked Bosch Rexroth and they know nothing about this valve.
I asked Moog and didn't get answer.
I asked B&R automation team and they answered that they don't know anything about this valve but they think that I need some IDs and In which format (CANopen? or pure CAN ids) is not documented.
[url=http://www.99poze.ro/p/1c767690ddf4da7d6e0d96227bec3639.jpg] [/url]+[url=http://www.99poze.ro/p/12000433f9e27a2f83f3bfe644985b78.jpg] [/url]+[url=http://www.99poze.ro/p/6596ded6b656694c26b92c7f1f1b0fa8.jpg] [/url]+ |
|
| Back to top |
|
 |
mukrish Junior

Joined: 29 May 2017 Posts: 19
|
Posted: 31/05/2017 11:55 Post subject: Re: Interfacing PLC B&R to Bosch Valve |
|
|
| Ahmad233 wrote: | Hallo
I am new with CANopen and CAN bus.
I have a problem with old Bosch Valve controlled by B&R plc cp470.
PLC is empty .. but it is the same PLC which controlled previously this valve.
I need to change the control mode from CAN to analog.
Unfortunately less information I got to control this valve. I attached them.
I asked Bosch Rexroth and they know nothing about this valve.
I asked Moog and didn't get answer.
I asked B&R automation team and they answered that they don't know anything about this valve but they think that I need some IDs and In which compus (CANopen? or pure CAN ids) is not documented.
[url=http://www.99poze.ro/p/1c767690ddf4da7d6e0d96227bec3639.jpg] [/url]+[url=http://www.99poze.ro/p/12000433f9e27a2f83f3bfe644985b78.jpg] [/url]+[url=http://www.99poze.ro/p/6596ded6b656694c26b92c7f1f1b0fa8.jpg] [/url]+ |
put the name of the valve |
|
| Back to top |
|
 |
Ahmad233 Junior

Joined: 21 May 2017 Posts: 4
|
Posted: 31/05/2017 14:40 Post subject: Re: Interfacing PLC B&R to Bosch Valve |
|
|
| mukrish wrote: | | Ahmad233 wrote: | Hallo
I am new with CANopen and CAN bus.
I have a problem with old Bosch Valve controlled by B&R plc cp470.
PLC is empty .. but it is the same PLC which controlled previously this valve.
I need to change the control mode from CAN to analog.
Unfortunately less information I got to control this valve. I attached them.
I asked Bosch Rexroth and they know nothing about this valve.
I asked Moog and didn't get answer.
I asked B&R automation team and they answered that they don't know anything about this valve but they think that I need some IDs and In which format (CANopen? or pure CAN ids) is not documented.
[url=http://www.99poze.ro/p/1c767690ddf4da7d6e0d96227bec3639.jpg] [/url]+[url=http://www.99poze.ro/p/12000433f9e27a2f83f3bfe644985b78.jpg] [/url]+[url=http://www.99poze.ro/p/6596ded6b656694c26b92c7f1f1b0fa8.jpg] [/url]+ |
put the name of the valve |
BOSCH valve model Nr:0 811 404 177 with Circuit Nr:0 811 405 172 -104[url=http://www.99poze.ro/p/d1bd9ac6b35a7954dac4cd24ff3f8278.jpg] [/url]+[url=http://www.99poze.ro/p/61e33a183fbc15e5feb32f8d6ce28e58.jpg] [/url]+
BOSCH Rexroth said:
"This was a special development from Bosch, not BoschRexroth."
I didn't find any manual for it.
I need an example to know how B&R PLC interfacing with another manufacture objects.. so I know what parameters I missed. |
|
| Back to top |
|
 |
mukrish Junior

Joined: 29 May 2017 Posts: 19
|
Posted: 12/06/2017 17:55 Post subject: |
|
|
After starting MoVaCo the following Menu will start
The bit rate and CANOpen node number (Node_ID) must be identical with the parameters which have been installed on the valve. Otherwise a communication with the valve is impossible.
Normally for valves and pumps with CAN interface the factory setting for bit rate is 500Kbit/s and the Node_ID is 127.
In case that the bit rate is known but not the Node _ID, the valve can be brought to send a boot-up message by turning the power OFF and ON.
This Boot-up message contain an information about the Node_ID (number)of the connected component.
|
|