Posted: 26/09/2016 07:33 Post subject: I/O Module 1769-IQ6XOW4 Series B Revision 1.1 |
|
|
I have one doubt pls tell some tips or guidens,
Iam using this I/O module, but in the RSlogix 5000 my controller is Compactlogix 1769-L32E and i selected the 1769-IQ6XOW4 Series B I/O module. In this I/O module properties there is only revision 2&3. There is no revision 1. In this problem there is any errors or faults are occurs or not...?
I connected this i/o module with rev.2.1 configuration and i connected a push button in the Input pins and I programmed for this Input and i download it, After to change the PROG mode to REM RUN mode and if i pressing the push button in my I/O module the input pin 1 turns Orange light. if i released the push button it turns off. But the controller has faulted.(i.e; Fault occurs- Controller fault) Fault type-03 and Code-23
cause:At least one required connection was not established before going to Run mode.
Recovery method:Wait for the controller I/O light to turn green before changing to Run mode.
But there is no green light indication in my I/O module 1769-IQ6XOW4 Series B Revision 1.1.
Is there any IO Module Revision problem or not...
How to rectify this fault.... please tell some suggestion...
Reply as soon as Possible... |
|
| Back to top |
|
 |
LarsKBH Junior

Joined: 01 Apr 2012 Posts: 13
|
Posted: 26/09/2016 12:43 Post subject: |
|
|
| Did you remember 1769-ECR Endcab? |
|
| Back to top |
|
 |
Kali Rajan Junior

Joined: 26 Sep 2016 Posts: 6
|
Posted: 26/09/2016 14:48 Post subject: |
|
|
| Yes, I know i used this END Cover... even i have this problem...what i do....? |
|
| Back to top |
|
 |
valz Member 3


Joined: 26 Jul 2015 Posts: 771
|
Posted: 26/09/2016 18:00 Post subject: |
|
|
| If you have 1769 analog modules on the bus that are receiving external power, check to be sure the power selector is set for External. |
|
| Back to top |
|
 |
Kali Rajan Junior

Joined: 26 Sep 2016 Posts: 6
|
Posted: 27/09/2016 06:20 Post subject: |
|
|
Valz,
I have connected an analog input module 1769-IF8 in the same bus. before the DIO module. And iam using 1769-PB4 power supply. |
|
| Back to top |
|
 |
LarryX Junior

Joined: 14 Aug 2014 Posts: 4
|
Posted: 28/09/2016 17:04 Post subject: Re: I/O Module 1769-IQ6XOW4 Series B Revision 1.1 |
|
|
| Kali Rajan wrote: | I have one doubt pls tell some tips or guidens,
Iam using this I/O module, but in the RSlogix 5000 my controller is Compactlogix 1769-L32E and i selected the 1769-IQ6XOW4 Series B I/O module. In this I/O module properties there is only revision 2&3.
There is no revision 1.
In this problem there is any errors or faults are occurs or not...?
I connected this i/o module with rev.2.1 configuration . |
Disable Keying for this module. |
|
| Back to top |
|
 |
|