lebou Junior

Joined: 09 Apr 2016 Posts: 10 Location: Senegal
|
Posted: 27/09/2016 17:04 Post subject: How to upload or download on IC695CPE310 |
|
|
Hi All
I 'm using Proficy machine Edition on my Rx3i PLC in our Processing plant and I have an issue :from my workstation if I try to go on line everything is fine except logic NE (not equal).Now I cannot upload from the Controller to my workstation .The CPU used is IC695CPE310
Did someone can help me of upload procedure
For more if I am pinging it replies very well
Thanks in advance _________________ Trying to iimprove my knowlege on PLC and sharing my knowlege with people |
|
| Back to top |
|
 |
kanton Junior

Joined: 20 Sep 2016 Posts: 15
|
Posted: 27/09/2016 18:43 Post subject: Re: How to upload or download on IC695CPE310 |
|
|
| lebou wrote: | Hi All
I 'm using Proficy machine Edition on my Rx3i PLC in our Processing plant and I have an issue :from my workstation if I try to go on line everything is fine except logic NE (not equal).Now I cannot upload from the Controller to my workstation .The CPU used is IC695CPE310
Did someone can help me of upload procedure
For more if I am pinging it replies very well
Thanks in advance |
https://www.youtube.com/watch?v=qq8bOv7v-D4
It is recommended that when downloading, the boxWrite ALL items to flash
memory should be checked.
The green diamond at the bottom of the window should have a red "X" on top of it and "Logic NE" should show in the window to the right of the green diamond. In order to run this program, the changes must be downloaded into the PLC. The changes you just made were not
actually entered into the PLC memory. Click on the Download icon (green arrow beneath a paper sheet) and then the Run icon (right-pointing triangle). If a “Start Controller” window pops up, select “Outputs Enabled” and then OK. The right box along the bottom of the window should
show a green diamond and "Logic EQ".
Try the input switches in various combinations and observe the output. Also observe the changing status of ladder components on the screen. Energized or true conditions cause the elements to be highlighted (green) on the ladder diagram. Note that if SW3 is off, and SW4 is on, the second contact does not highlight, but the “SW4” changes to green to indicate that the switch is on, even though power is not flowing through the contact, due to SW3 being open. |
|
| Back to top |
|
 |
lebou Junior

Joined: 09 Apr 2016 Posts: 10 Location: Senegal
|
Posted: 30/09/2016 11:28 Post subject: How to upload or download on IC695CPE310 |
|
|
Hi
Please could you give more explanation about the swiches SW3 and SW4 where are they .My big issue is to upload an program from the CPU
Thanks in advance _________________ Trying to iimprove my knowlege on PLC and sharing my knowlege with people |
|
| Back to top |
|
 |
kastrol Junior


Joined: 12 Dec 2016 Posts: 7
|
Posted: 22/12/2016 10:11 Post subject: Re: How to upload or download on IC695CPE310 |
|
|
| lebou wrote: | Hi
Please could you give more explanation about the swiches SW3 and SW4 where are they .My big issue is to upload an program from the CPU
Thanks in advance |
this is for help?
IC695CPE305 How-to Troubleshoot Proficy Machine Edition Training GE Rx3i CPU PLC Tutorial
https://www.youtube.com/watch?v=5HkK5QgYI7w |
|
| Back to top |
|
 |
kanton Junior

Joined: 20 Sep 2016 Posts: 15
|
Posted: 22/12/2016 11:31 Post subject: Re: How to upload or download on IC695CPE310 |
|
|
| lebou wrote: | Hi
Please could you give more explanation about the swiches SW3 and SW4 where are they .My big issue is to upload an program from the CPU
Thanks in advance |
The above explanations was made not to make that only one modification on the program at a time. But you cannot probably makes modifications on program and then download to PLC as you are in running with PLC. This is a known bugs that the guys from GE always gave a wrong response.
If you are connected thru a switch try to avoid and see if can connect.
Connect directly to ETM port. If don't work you have a BIG PROBLEM.
It happens the check equality does not work since it sees a different data as being not equal even right after doing a download to PLC.
One solution could be to use a spare part CPU, make upload if you have the original program, check upload download if works and replace the actual PLC. |
|
| Back to top |
|
 |
|