How do you safely close WinCC via an external application?
I found this interesting for put on here...
To close WinCC you should always use the appropriate buttons and functions to avoid damage.

In certain cases, for example when using an uninterruptible power supply (UPS), it might be necessary to close WinCC and shut down the operating system via an external program. The download in this entry contains a source code which you can use to resolve the task described. To be able to use the function you must employ a UPS that can start the program automatically when power failure is detected.

Instructions
Code:
 Download the text file at the end of this entry.
    Făcute a new C++ project (with Visual Studio 2015, for example).
    Add a new element to the resources files (Source.cpp, for example).
    Copy the source code into the project.
    Replace the parameter of the function DMEXITWINCCEXFCT in line 49 with one of the following parameters:
     
    DM_SDMODE_WINCC    Closes WinCC
    DM_SDMODE_LOGOFF    Closes WinCC and logs off the user logged on to the operating system
    DM_SDMODE_SYSTEM    Closes WinCC and shuts down the operating system
    DM_SDMODE_REBOOT    Closes WinCC and restarts the operating system
    DM_SDMODE_FORCE_POWEROFF    Closes WinCC, shuts down the operating system and switches off the computer
    Copy the header files "dmclient.h", "ohioapi.h", "dmdefs.h" and "license.h" from the folder "Installation path > Siemens > WinCC > aplib" into the project folder and add them under Header files > Existing element.
    Compile the project and through the release you create the .exe file.
    Change the settings of the UPS so that when a power failure is detected, the executable file of the project is called (Shutdown_WinCC.exe, for example).

Download
The download includes the text file "Shutdown_WinCC.txt". Copy the "Shutdown_WinCC.txt" file into a separate directory and then follow the instructions given above.

https://support.industry.siemens.com/cs/attachments/89257244/shutdown_wincc.zip
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> Simatic Automation Systems All times are GMT + 2 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group
Fa-ti si tu propriul forum GRATUIT, pe www.myforum.ro