Posted: 21/08/2015 21:51 Post subject: How do you load the WinCC Runtime Advanced configuration |
|
|
How do you load the WinCC Runtime Advanced configuration into the HMI without a direct data connection?
If there is no data connection between the Engineering and the Runtime PC, you can transfer the Runtime data to the Runtime PC via a USB stick, for example.
Right-click WinCC Runtime Advanced and select "Compile > Software (rebuild all)".
In the project folder of the WinCC (TIA Portal) project you open the folder "IM > HMI".
Open the folder with the most recent time stamp.
Open the "Generates" folder.
Copy the files to the Runtime PC using a USB stick, for example.
Open the WinCC Runtime Loader on the Runtime PC via "Start > Siemens Automation > Runtime Systems > WinCC Runtime Advanced > WinCC Runtime Loader".
Click "Settings".
Under "Autostart configuration" you specify the path in which you want to have the Runtime data stored.
 |
|