PostPosted: 09/10/2012 11:57    Post subject: Help: Siemens Sinamics CU305 PN boot fails Reply with quote

Hello all!

I'm requesting for help with a brand new Siemens Sinamics CU305 PN control unit with PROFINET interface. At power-up, the status LEDs randomly blink a while with red and yellow colours. After a minute or so, both the RDY and COM LEDs start blinking red at a constant rate. Nothing else happens.

I'm unable to connect to the control unit with a null modem cable through the RS232 interface.

Any suggestions, please?
Back to top
View user's profile Send private message
seamen
Junior
Junior


Joined: 09 Oct 2012
Posts: 6

PostPosted: 12/10/2012 13:28    Post subject: Reply with quote

Thank you for your prompt answer!

Unfortunately, the link provided for the latest firmware actually points to GSDML file used for fieldbus configuration, not to drive firmware image.

I was unable to locate any firmwares from the Siemens site. Do you know where I can download them?
Back to top
View user's profile Send private message
seamen
Junior
Junior


Joined: 09 Oct 2012
Posts: 6

PostPosted: 17/10/2012 08:47    Post subject: Reply with quote

Thank you for the link, but unfortunately this time it points to SINAMICS MICROMASTER STARTER, which is a Windows software, and not the drive firmware. As I am unable to connect to the drive using the STARTER software, it is no use to me.

Regarding the connections, I am not exactly sure what you mean by that, but I've connected the power supply to the control unit (+24V) and a null modem cable for RS232, nothing else.

Are there some other connections I should make?
Back to top
View user's profile Send private message
seamen
Junior
Junior


Joined: 09 Oct 2012
Posts: 6

PostPosted: 22/10/2012 10:38    Post subject: Reply with quote

Thank you for the information, but I'm not sure if it applies to my CU305 which has a Secure Digital (SD) memory card slot, and NOT CompactFlash (CF).

Are there any tools for SD cards?
Back to top
View user's profile Send private message
rott
Senior
Senior


Joined: 23 Aug 2011
Posts: 2266

PostPosted: 22/10/2012 22:07    Post subject: Reply with quote

seamen wrote:
Thank you for the information, but I'm not sure if it applies to my CU305 which has a Secure Digital (SD) memory card slot, and NOT CompactFlash (CF).

Are there any tools for SD cards?

seaman,

-Is the first time you are booting the system?...or after a time the system broken down???
-External 24V power supply is required for operation.
-The CU305 has a DRIVE-CLiQ interface. You may connect exactly one of the following components to this interface:? SMI motor ? 1 encoder of type SMC10, SMC20, SMC30, SME20 or SME25
-Further components or connections to the DRIVE-CLiQ interface are not permitted and lead to errors in the drive system.
-the IP address is not stored permanently. The IP address entry is lost after POWER ON/OFF. If the IP address is to be stored in a non-volatile memory, the address must be assigned using the Primary Setup Tool (PST).
-A PROFINET interface with 2 ports is integrated in the CU305 PN module.
The ports must not be interconnected in such a way that a ring topology is created.
-put a picture with what exactly what's writing on the SD card.
-If you are using one CPU, p8929 is 1 and when the system is booting SINAMICS is waiting a confirmation telegram from CPU.
-Are you using Failsafe..?? because when the system is booting, p8929 is 2 and SINAMICS S recognizes that PROFINET telegrams from 2 controls are expected, and structures the communication according to the configuration in HW Config.
- p8929 PN Number of remote controllers must be 1 or 2 accordingly.
- p9601 SI enable, functions integrated in the drive (CPU 1)
-the memory is a SanDisk (SD) and is compatible with MMC but has greater capacity and speed...
Tell me more and all about and maybe we discover the cause....
Back to top
View user's profile Send private message
seamen
Junior
Junior


Joined: 09 Oct 2012
Posts: 6

PostPosted: 26/10/2012 13:02    Post subject: Reply with quote

I'm sorry if my questions seem vague. I appreciate the time and effort you have used to help me.

Primary Setup Tool says "No station was detected on the network." Even though I have connected the PC and the CU305 PN by an Ethernet cable. Is that normal?

Answers to your previous questions below:
- This is the first time I'm booting the system. It has not worked ever before.
- Power is connected.
- Drive-cliq is NOT connected (not needed).
- One Ethernet port is connected.
- The SD card has the text "Siemens MMC V 04.01.00.02" on it.
- I have not been able to set any parameters.
- Failsafe is not used (to my knowledge). :unsure:
Back to top
View user's profile Send private message
seamen
Junior
Junior


Joined: 09 Oct 2012
Posts: 6

PostPosted: 30/10/2012 16:17    Post subject: Reply with quote

rott, thanks for you help!

I used PST4.1 on Win7 with the DLC protocol installed, but was not able to see the CU305 PN device, nor any other devices for that matter.
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> Drives & Inverters All times are GMT + 2 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group
Fa-ti si tu propriul forum GRATUIT, pe www.myforum.ro