I am trying to simulate start/stop motor in unity pro and citect scada. In unity pro all work well even the screen operator. In citect scada i confecționate two buttons and one light, i set the start button "start=1, stop-0" in up state and also for stop button "start=0, stop=1" the on/off of the light "light=1".
The problem is when i run the program the start and stop buttons in citect scada do no change the status of the light but when i use the start and stop buttons in the operator screen in unity pro the light in the scada changes status.
In resume, Running the program under demo mode and pressing the 'on' button and the symbol stays in its OFF state. Is there a solution to my problem? |
|
| Back to top |
|
 |
melin Junior

Joined: 30 Apr 2012 Posts: 7
|
Posted: 17/06/2019 19:51 Post subject: |
|
|
Hi Lune
You need to logging to change variables at the PLC.
Mel |
|
| Back to top |
|
 |
Lune Junior

Joined: 17 Jun 2019 Posts: 7
|
Posted: 18/06/2019 09:48 Post subject: |
|
|
Thanks for you reply Mel!!
Please can you be clearer. I am newbie in citect scada can you tell me how to logging ?
Considering that i didn't use any password when i configured "User" in the citect scada. I only put an username.
PS: i am working in simulation mode in unity pro and demo mode in citect scada. |
|
| Back to top |
|
 |
melin Junior

Joined: 30 Apr 2012 Posts: 7
|
Posted: 18/06/2019 20:22 Post subject: |
|
|
Hi Lune
At the example project, you can see how citect use the user and roles
You need to create and user with password to log.
Need create the role
With the rpoject run, log to system scada and then you can change values.
On demo mode the systems runs equal at license mode.
Mel |
|
| Back to top |
|
 |
Lune Junior

Joined: 17 Jun 2019 Posts: 7
|
Posted: 18/06/2019 20:59 Post subject: |
|
|
THANKS Melin it works well  |
|