GX Works3 Simple PLC Communication Error Indicator

 
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> Other PLCs
View previous topic :: View next topic  
Author Message
xcyong89
Junior
Junior


Joined: 22 Sep 2018
Posts: 14

PostPosted: 06/11/2022 07:52    Post subject: GX Works3 Simple PLC Communication Error Indicator Reply with quote

Hi,

I have setup the Simple PLC communication in RJ71C24 (Channel 2) for communication between Mitsubishi IQ-R series PLC (Mosbus RTU Master) and multi drop Modbus RS485 Slave devices. The Simple PLC Communication Setting shows below:

GX Works3 Simple PLC Communication Error Indicator GX Works3 Simple PLC Communication Error Indicator

Just wonder is there any communication error flag to indicate communication fail for each communication request in Simple PLC communication ?
Back to top
View user's profile Send private message
Antterra
Junior
Junior


Joined: 27 Sep 2022
Posts: 4

PostPosted: 06/11/2022 19:23    Post subject: Calculation procedure for 16-bit CRC (for MODBUS) Reply with quote

Calculation procedure for 16-bit CRC (for MODBUS)
This is an error check method to be used when data are transmitted/received with the RTU mode of the MODBUS protocol.
The data length of CRC is fixed to 2 bytes (16 bits), and the CRC is calculated every 1 byte (8 bits) from the start of the
calculating range according to the following procedure.
1. Load a 16-bit register whose bits are all '1'.
2. Exclusive OR (XOR) the first 1 byte (8 bits) of the calculating range with 8 bits in above 1.
3. Shift the result of the step 2. for one bit right.
4. If the least significant bit in above 2. is '1', exclusive OR (XOR) the result of 3. with the generator polynomial (A001H). If
the least significant bit is '0', shift the result of step 3. one bit right (operation described in 3.) without the exclusive OR
(XOR) operation.
5. Repeat steps 3. and 4. for 8 times.
6. Exclusive OR (XOR) the result of the above 5 with the next 1 byte (8 bits).
7. Repeat step 3 through 6 until all bytes have been processed. The final result is CRC value.
8. The CRC value is stored in a packet in the order of lower 8 bits  upper 8 bits.
page543
https://terabox.com/s/1BEg_81f_HyxPk9oChR7k9w
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> Other PLCs All times are GMT + 2 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group
Fa-ti si tu propriul forum GRATUIT, pe www.myforum.ro