Fault clearing in have1756-16F & 1756-IF16H card ?

 
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> ALLEN-BRADLEY(Rockwell Automation) Reg. U
View previous topic :: View next topic  
Author Message
gspatil555
Junior
Junior


Joined: 11 Nov 2016
Posts: 1

PostPosted: 11/11/2016 08:47    Post subject: Fault clearing in have1756-16F & 1756-IF16H card ? Reply with quote

I [img]have1756-16F & 1756-IF16H[/img] analog input module connected to my contrologics 5572 controller. there is only single sensor connected few days ago & it the channel where sensor is connected was showing data without any channel fault but others were showing channel fault even if now sensors are connected & no data is coming ...checked with mA source then in 1756- IF16 the channel 0 to channel 8 (total 9) channels are showing data in the system & The 1756-16H hart card is not showing any data for new sensor it is also showing channel fault.It is even not showing any reading when connected to mA source.
I have checked wiring it is as per single ended configuration & in module properties I have selected the same.

How should I clear this fault ? What was the reason behind it...Dear friends plz give your valuable suggessions.[/img]
Back to top
View user's profile Send private message
dd
Junior 2
Junior 2
dd

Joined: 27 Sep 2016
Posts: 31

PostPosted: 11/11/2016 13:02    Post subject: Re: Fault clearing in have1756-16F & 1756-IF16H card ? Reply with quote

gspatil555 wrote:
I [img]have1756-16F & 1756-IF16H[/img] analog input module connected to my contrologics 5572 controller. there is only single sensor connected few days ago & it the channel where sensor is connected was showing data without any channel fault but others were showing channel fault even if now sensors are connected & no data is coming ...checked with mA source then in 1756- IF16 the channel 0 to channel 8 (total 9) channels are showing data in the system & The 1756-16H hart card is not showing any data for new sensor it is also showing channel fault.It is even not showing any reading when connected to mA source.
I have checked wiring it is as per single ended configuration & in module properties I have selected the same.

How should I clear this fault ? What was the reason behind it...Dear friends plz give your valuable suggessions.[/img]


Did you check jumpers iRTN-RNT maybe you are not on current output mode..
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> ALLEN-BRADLEY(Rockwell Automation) Reg. U All times are GMT + 2 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group
Fa-ti si tu propriul forum GRATUIT, pe www.myforum.ro