DriveExecutive PowerFlex Drive Firmware Flashing Procedure
1. If you do not already have a ControlFlash file for the Powerflex 700VC, now would be the time to go get one from the Web Updates site. Save the ControlFlash file to your hard drive somewhere, perhaps on your desktop. Dublu click to start up the ControlFlash file. Hit "Next", "Accept" the license agreement, then "Next" again to allow the ControlFlash program to install on your machine. Hit "Yes", then "Next", then "Yes" again, making sure the checkbox is ticked to start ControlFlash when done.
DriveExecutive PowerFlex Drive Firmware Flashing Procedure DriveExecutive PowerFlex Drive Firmware Flashing Procedure
2.Start the DriveExecutive program. Click the icon to connect to the drive.
DriveExecutive PowerFlex Drive Firmware Flashing Procedure DriveExecutive PowerFlex Drive Firmware Flashing Procedure
3. Select the path that your drive is connected with. It should look similar to the image below. The connection listed is for a DPI connection with an Anacanda.
DriveExecutive PowerFlex Drive Firmware Flashing Procedure DriveExecutive PowerFlex Drive Firmware Flashing Procedure
4. The PowerFlex 700VC should now be connected. The parameters will update themselves on the screen.
DriveExecutive PowerFlex Drive Firmware Flashing Procedure DriveExecutive PowerFlex Drive Firmware Flashing Procedure
5. Click on the properties button, which looks like a lower-case "i" in the toolbar.
DriveExecutive PowerFlex Drive Firmware Flashing Procedure DriveExecutive PowerFlex Drive Firmware Flashing Procedure
6. Select the "Component Details" tab in the PowerFlex 700 VC properties window.
DriveExecutive PowerFlex Drive Firmware Flashing Procedure DriveExecutive PowerFlex Drive Firmware Flashing Procedure
7. Under the Component Details tab, click on the "Flash Update" button.
DriveExecutive PowerFlex Drive Firmware Flashing Procedure DriveExecutive PowerFlex Drive Firmware Flashing Procedure
8. Select the PowerFlex 700 VC drive from the list. The firmware revision listed for your drive will most likely be different than the one listed in the example picture. After you select the PowerFlex 700 VC drive, click "Next".
DriveExecutive PowerFlex Drive Firmware Flashing Procedure DriveExecutive PowerFlex Drive Firmware Flashing Procedure
9. Select the firmware revision you wish to send to the drive. The available flash updates listed will depend on the amount of firmware files that you have downloaded in the past and installed on your computer. For flashing to firmware 4.005, select the file listed as 4.005.115 App, as indicated in the image below. Click "Next" to continue after clicking on the firmware.
DriveExecutive PowerFlex Drive Firmware Flashing Procedure DriveExecutive PowerFlex Drive Firmware Flashing Procedure
10. The "Confirm Flash Update" window will appear, and show you the current firmware revision, as well as the firmware revision that you are going to be flashing the device to. It is important to remove the HIM module before flashing the drive! If everything is as expected, then hit the "FLASH" button. It is imparitive that the flash process does NOT get interrupted.
DriveExecutive PowerFlex Drive Firmware Flashing Procedure DriveExecutive PowerFlex Drive Firmware Flashing Procedure
11. The flash process can take a few minutes. There is a status indicator that will count up as the process progresses.
DriveExecutive PowerFlex Drive Firmware Flashing Procedure DriveExecutive PowerFlex Drive Firmware Flashing Procedure
12. When finished, you will see a screen like the one below indicating the flash process has finished.
DriveExecutive PowerFlex Drive Firmware Flashing Procedure DriveExecutive PowerFlex Drive Firmware Flashing Procedure
13. You can now reinstall the HIM module onto the drive, and continue on to reprogramming the drive. There is a knowledgebase document that covers reprogramming the drive.
14. That document can be found here: G154752374 - Flash Upgrade Procedure for the PowerFlex 700VC Series B to Firmware 4.005
DriveExecutive PowerFlex Drive Firmware Flashing Procedure DriveExecutive PowerFlex Drive Firmware Flashing Procedure
http://www.ab.com/support/abdrives/webupdate/powerflex700.html#
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> ALLEN-BRADLEY(Rockwell Automation) All times are GMT + 2 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group
Fa-ti si tu propriul forum GRATUIT, pe www.myforum.ro