Do I need a 1756-ENET/B if I have a 1756-CNB/D

 
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> ALLEN-BRADLEY(Rockwell Automation) Reg. U
View previous topic :: View next topic  
Author Message
javihnrqz
Junior
Junior


Joined: 13 Dec 2018
Posts: 4

PostPosted: 14/02/2019 14:52    Post subject: Do I need a 1756-ENET/B if I have a 1756-CNB/D Reply with quote

Hi guys, I have a question regarding a ControlLogix PLC.
It happens that according to the drawings I might have two modules connected on the ControlLogix: a 1756-ENET/B and a 1756-CNB/D. What happens is that I only have one module that is the 1756-CNB/D that provides me ControlNet interface to the loop made by PowerFlex 70 drives. I see that the 1756-CNB/D has a Ethernet input, so my question is:

¿Do I need a 1756-ENET/B if I have the 1756-CNB/D?

Is it like built-in the Ethernet capability or how does it work?

Thanks in advance people.

Javier Henríquez.
Back to top
View user's profile Send private message Send e-mail
capo_di_tutti_capi
Junior
Junior


Joined: 17 Nov 2017
Posts: 10

PostPosted: 20/02/2019 19:58    Post subject: 1756-CNB Series B ControlNet Bridge Reply with quote

http://apps.watersurplus.com/techlib/Allen%20Bradley/AB_PowerFlexControlNetAdapter_20COMMC_user_D1101.pdf

PowerFlex 70/700: Typical PI Loop Configuration

Question
What is a typical PI loop configuration for PowerFlex 70/700 drives?

Environment
20A PowerFlex 70
20B PowerFlex 700
Answer
A typical PI loop configuration for PowerFlex 70/700 drives is described below:

Note: For PowerFlex 70 and 700 standard control drives only (not enhanced or vector control) set Parameter 80 [Speed Mode] to a value of 2 "Process PI".

Set Parameter 90 [Speed Ref A Sel] to a value of any true master speed reference such as an unused analog input or DPI port.

Set Parameter 124 [PI Configuration] bit 4 "Zero Clamp" = 1 . This will prevent the drive and motor from running in the reverse direction.

Set Parameter 124 [PI Configuration] bit 0 "Excl Mode" = 1. This exclusive mode forces the drive to receive its speed reference, acceleration, and deceleration rates from the PI loop.

Optional: Parameter 124 [PI Configuration] bit 1 "Invert Error" can be set to a value of 1 if the process requires it. For example, if the feedback is a temperature device that increases with temperature the fan will have to increase to decrease the temperature back to the setpoint. This type of inverse relationship requires this bit to be set or the PI output will increase when it should decrease and vice-versa.

Optional: To enable/disable the PI Loop:

Parameter 125 [PI Control] bit 0 "Enable PI" can be set to a value of 1 to enable or 0 to disable the PI Loop.

Set a digital input such as Parameter 364 [Digital In4 Sel] = 26 [PI Enable] to enable and disable the PI Loop through a digital input terminal. Note: In this case Parameter 125 [PI Control] bit 0 "Enable PI" must still be set to 1, and the digital input must have voltage applied in order to enable the PI loop.

Set Parameter 126 [PI Reference Sel] to a value of 0 "PI Setpoint" (default).

Set Parameter 127 [PI Setpoint] to a value of 50% (default).

Set Parameter 128 [PI Feedback Sel] to a value of 1 "Analog In 1" or 2 "Analog In 2".

Set Parameter 131 [PI Lower Limit] so that the value is equal to Parameter 55 [Maximum Frequency] for standard control PowerFlex 70/700 or a value of -100% for the PowerFlex 70/700 Enhanced/Vector Control.

Set Parameter 132 [PI Upper Limit] so that the value is equal to Parameter 55 [Maximum Frequency] for standard control PowerFlex 70/700 or otherwise a value of +100% for the PowerFlex 70/700 Enhanced/Vector Control.
Back to top
View user's profile Send private message
AIX
Junior
Junior


Joined: 06 Sep 2017
Posts: 9

PostPosted: 21/02/2019 06:15    Post subject: Reply with quote

RJ-45 on 1756-CNB isn't Ethernet, this is Network Access Port for connecting various clients, like PC, to ControlNet network with 1784-KTC, -KTCx,
or -PCC communication card and a 1786-CP cable.
If you want communicate with PLC from Ethernet network, you need 1756-ENxx module.
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> ALLEN-BRADLEY(Rockwell Automation) Reg. U All times are GMT + 2 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group
Fa-ti si tu propriul forum GRATUIT, pe www.myforum.ro