ControlNET problem

 
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> ALLEN-BRADLEY(Rockwell Automation) Reg. U
View previous topic :: View next topic  
Author Message
zer-gut
Junior
Junior


Joined: 24 Mar 2014
Posts: 5

PostPosted: 25/07/2015 14:49    Post subject: ControlNET problem Reply with quote

Hi. I have an issue with the Control Net module 1756-CN2R that keeps generating 'Duplicate Node Detected' (DND) in random ControNet nodes in the entire star redundant network which retains until the module is power recycled.The only way to get rid of the "DND" is to recycle power at the affected nodes. Please find the attached configuration for the source of duplicate node detected error. I have all fiber module 1786-RPFRXL v2.005 and RPA/B. There redundant system. Remote chassis connected by optics. Periodically there is a network failure, resulting in loss of the node (s) network. Maybe someone faced with a problem.

I tried to change the settings configuration RSNetwoRX media configuration - does not help.

0 - L74/B 19.53
1 - RM2/A 20.005
2 - CN2R/B 20.20
3 - CN2R/B 20.20
4 - EN2T/D - 10.7
5 - EN2T/ D - 10.7
6 - EN2T/D - 10.7



P.S.Enclosed structure of the network addresses[/img]
Back to top
View user's profile Send private message
Ryzhij
Junior 2
Junior 2


Joined: 26 Jun 2013
Posts: 22

PostPosted: 26/07/2015 17:00    Post subject: Reply with quote

Наш "пострел" везде поспел!
Припекло, видать...
На плцфорум.уз.уа ещё не написали? :-)
Там тоже толковые спецы обитают.
Back to top
View user's profile Send private message
zapata
Junior
Junior


Joined: 02 Jul 2015
Posts: 7

PostPosted: 26/07/2015 20:34    Post subject: Reply with quote

Ryzhij wrote:
Наш "пострел" везде поспел!
Припекло, видать...
На плцфорум.уз.уа ещё не написали? :-)
Там тоже толковые спецы обитают.


could you translate?
Back to top
View user's profile Send private message
gecko1
Member
Member
gecko1

Joined: 24 Nov 2013
Posts: 225

PostPosted: 26/07/2015 21:15    Post subject: Re: ControlNET problem Reply with quote

zer-gut wrote:
Hi. I have an issue with the Control Net module 1756-CN2R that keeps generating 'Duplicate Node Detected' (DND) in random ControNet nodes in the entire star redundant network which retains until the module is power recycled.The only way to get rid of the "DND" is to recycle power at the affected nodes. Please find the attached configuration for the source of duplicate node detected error. I have all fiber module 1786-RPFRXL v2.005 and RPA/B. There redundant system. Remote chassis connected by optics. Periodically there is a network failure, resulting in loss of the node (s) network. Maybe someone faced with a problem.

I tried to change the settings configuration RSNetwoRX media configuration - does not help.

0 - L74/B 19.53
1 - RM2/A 20.005
2 - CN2R/B 20.20
3 - CN2R/B 20.20
4 - EN2T/D - 10.7
5 - EN2T/ D - 10.7
6 - EN2T/D - 10.7



P.S.Enclosed structure of the network addresses[/img]

Check some hints on
http://www.plctalk.net/qanda/showthread.php?p=478175
Back to top
View user's profile Send private message
zer-gut
Junior
Junior


Joined: 24 Mar 2014
Posts: 5

PostPosted: 26/07/2015 22:23    Post subject: Reply with quote

Yes thank you. I found this topic. I pointed out to the media configuration RSNetWORX cable length and type cable, as well as converters and repeaters. It did not solve my problem (
Back to top
View user's profile Send private message
zer-gut
Junior
Junior


Joined: 24 Mar 2014
Posts: 5

PostPosted: 30/07/2015 18:28    Post subject: Reply with quote

Thank you for your help. The problem was solved, it was in the optical cable. More precisely in the connector. The attenuation in the natural range, but in microscopy - seen strong contamination. Well, that was found specialist equipment at the facility.

P.S.Topik can be closed.
Back to top
View user's profile Send private message
tanner
Member
Member


Joined: 07 Jun 2015
Posts: 134

PostPosted: 30/07/2015 20:55    Post subject: Reply with quote

zer-gut wrote:
Thank you for your help. The problem was solved, it was in the optical cable. More precisely in the connector. The attenuation in the natural range, but in microscopy - seen strong contamination. Well, that was found specialist equipment at the facility.

P.S.Topik can be closed.


Thanks zer-gut.
Other users only said..I solve the problem...but do not say a word how did do it.
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> ALLEN-BRADLEY(Rockwell Automation) Reg. U All times are GMT + 2 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group
Fa-ti si tu propriul forum GRATUIT, pe www.myforum.ro