Hi,
I'm trying to connect M340 with XBTGT2110 on usb cable with modbus, but i have issue linking the variable.
PLC(Unity pro xl) variable:
[url=http://www.99poze.ro/p/bf09c61a1f2685a4002eb9fce85bccbc.jpg] [/url]+
Trying to link the variable:
[url=http://www.99poze.ro/p/fce93eb84c74c86b30359a73a2b571e2.jpg] [/url]+
In Vijeo i've activate the data dictionary. |
|
| Back to top |
|
 |
atrack Junior

Joined: 01 Feb 2018 Posts: 2
|
Posted: 01/02/2018 20:03 Post subject: |
|
|
The Modbus port parameters are RS485, 19200 baud, 8 data bits, even parity, 1 stop bit. So you need a RS485 Modbus network (at 19200 baud) to connect to an M340 CPU with defaut parameters on Modbus port. Otherwise, you have to choose a different communication method (USB or Ethernet, for example) and configure the Modbus port parameters in the application.
you can use the M340 USB port to communicate to the Magelis but you need to select the Modbus/TCP driver and choose USB EQUIPMENT. |
|