PostPosted: 09/03/2018 17:48    Post subject: Configuration Netpro Reply with quote

I have questions about network architecture and configuration in Netpro.
I send you a picture of the entire configuratin of Netpro and pdf configuration plc's and Please you answer my questions.
1-Should be Terminal Bus configured in Net Pro?(Is it necessary to configure the TerminalBus separately in Net Pro?)
2-What is your opinion about configuration the network bus network in Netpro?Is there a redundancy?(Do two network PlantBus to be configured in Net Pro or not ?)
Installed on any server we have 1623 dual card
But along with each CPU, we have a 443-1 card. Is this correct?

link files of configuration: http://s000.tinyupload.com/download.php?file_id=09675733169634217861&t=0967573316963421786131794

http://s000.tinyupload.com/download.php?file_id=63473662163809046187&t=6347366216380904618789416
Back to top
View user's profile Send private message
ayurden
Junior
Junior


Joined: 05 Mar 2018
Posts: 3

PostPosted: 09/03/2018 19:46    Post subject: Reply with quote

It seems you have a PCS7 project.
Under these circumstances for taking advantage of Simatic Net communication you must define all stations and all terminal in the same project under the same Network.
Use NetPro for the entire project.
Back to top
View user's profile Send private message
rayen_6827
Member junior
Member junior


Joined: 21 Jun 2013
Posts: 67

PostPosted: 09/03/2018 20:00    Post subject: Reply with quote

Thanks
My question is
Is the configuration correct?
in the page61 and 63 manual https://cache.industry.siemens.com/dl/files/178/109476178/att_842975/v1/ps7red_b_en-US.pdf *SIMATIC
Process Control System PCS 7
Fault-tolerant Process Control
Systems
* of siemens there are 2 Solutions for the plant bus
The system is redundant, fault-tolerant plant bus or not?
Why in our system for each server, there are two 1623 cards installed, but next to each CPU is one card 443-1
Is this correct?
Back to top
View user's profile Send private message
ayurden
Junior
Junior


Joined: 05 Mar 2018
Posts: 3

PostPosted: 10/03/2018 12:06    Post subject: Reply with quote

As I see from this drawing ....yes you have a Plant Bus Redundancy with Fault Tolerant cell bus..

You have two Rings realised with FO OLM wired to 2 redundant Switches.read on the next drawings to see how OLMs are conected because the connections of OLMs lead to the ST Machine..
Configuration Netpro

Eventually make a hands drawing with the connections of the OLMs to see if the Ring is closed for every from the redundant channels for IM153.

Configuration Netpro

Configuration Netpro
Back to top
View user's profile Send private message
rayen_6827
Member junior
Member junior


Joined: 21 Jun 2013
Posts: 67

PostPosted: 10/03/2018 13:20    Post subject: Reply with quote

Yes thanks for your answer ichecked to st Machine.
but In your opinion do not need to have two 443-1 card for each cpu for redundat,fault-tolerant plant bus???
According to
Process Control System PCS 7 High Availability Process Control Systems (V9.0)
Function Manual page 54 and after that you can see there are two solutions for the Plant bus:
1-High availability plant bus
2-Redundant, high availability plant bus
I want my system redundant, high availability plantbus
Back to top
View user's profile Send private message
ayurden
Junior
Junior


Joined: 05 Mar 2018
Posts: 3

PostPosted: 12/03/2018 13:14    Post subject: Reply with quote

Configuration Netpro

this is what?

only check if the FO is in a ring.
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> Simatic Automation Systems All times are GMT + 2 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group
Fa-ti si tu propriul forum GRATUIT, pe www.myforum.ro