othmane_benz Junior

Joined: 10 Nov 2017 Posts: 14
|
Posted: 28/11/2017 20:14 Post subject: Communication Simatic between a CPU315 and ET200 |
|
|
Hello,
I have two hardware configuration and I would like if I'm in the right path,
1 #
* I have a CPU with ProfiBus / Dp
* I have a remote module ET200b - 32Di 131-0bl00-0xb0
does this configuration work without a coupler?
in this case I work with the blocks SFC14,15?
2 #
* I have a CPU with only MPI, and a CP Profibus Dp
* I have a remote module ET200b - 32Di 131-0bl00-0xb0
does this configuration work without a coupler?
in this case I work with FC1 and FC2 blocks?
Thanks for your help |
|
| Back to top |
|
 |
atto Junior 2

Joined: 01 Jul 2017 Posts: 22
|
Posted: 28/11/2017 20:51 Post subject: |
|
|
PROFIBUS GSD-Dateien : ET 200B
https://support.industry.siemens.com/cs/document/113304/
Stationstyp: ET 200B-32DI
Best.-Nr.: 6ES7 131-0BL00-0XB0
https://cache.industry.siemens.com/dl/files/304/113304/att_84580/s1/siem0004.gsd
Import GSD file in Device view (Menu Options -> Install G..S…D.. file) to get the ET200B shown in HW list under GSD.
Add the Device in Network view and connect with DP Port of S7 300.
Set addresses and download.
Then you can address the inputs and outputs.
Copy the data to DB via Load and transfer code and create HMI variables to access the data in DB.
Diagnostic package PNIODiag for diagnostic evaluation for PROFIBUS DP and PROFINET IO (STEP 7 V5.x)
https://support.industry.siemens.com/cs/document/98278878/
What CP do you want to use???
https://support.industry.siemens.com/cs/document/42413/rules-for-accessing-the-cpu-315-2-dp-on-distributed-i-o- (integrated-dp-interface-of-cpu-315-2-dp) |
|
| Back to top |
|
 |
othmane_benz Junior

Joined: 10 Nov 2017 Posts: 14
|
Posted: 03/12/2017 14:10 Post subject: |
|
|
| atto wrote: | PROFIBUS GSD-Dateien : ET 200B
https://support.industry.siemens.com/cs/document/113304/
Stationstyp: ET 200B-32DI
Best.-Nr.: 6ES7 131-0BL00-0XB0
https://cache.industry.siemens.com/dl/files/304/113304/att_84580/s1/siem0004.gsd
Import GSD file in Device view (Menu Options -> Install G..S…D.. file) to get the ET200B shown in HW list under GSD.
Add the Device in Network view and connect with DP Port of S7 300.
Set addresses and download.
Then you can address the inputs and outputs.
Copy the data to DB via Load and transfer code and create HMI variables to access the data in DB.
Diagnostic package PNIODiag for diagnostic evaluation for PROFIBUS DP and PROFINET IO (STEP 7 V5.x)
https://support.industry.siemens.com/cs/document/98278878/
What CP do you want to use???
https://support.industry.siemens.com/cs/document/42413/rules-for-accessing-the-cpu-315-2-dp-on-distributed-i-o- (integrated-dp-interface-of-cpu-315-2-dp) |
first of all thank you for your help,
your intervention she well detailed,
I installed the gsd file and compile without errors
but I could not have the data base.
how to import the data to the master for reading? |
|