longwangwl456 Member junior

Joined: 02 May 2018 Posts: 82
|
Posted: 14/11/2019 10:20 Post subject: bmep581020 02.70 in unity pro v12 |
|
|
a project saved as .zef file in unity pro v13.1
want to open in unity pro v12 on the other pc. but failed. get error message :
the configuration catalog is not compatible with current application.
some objects are missing or their version is incompatible.
the required cpu reference BMEP581020 02.70 is missing!
how to solve it?
thanks. |
|
| Back to top |
|
 |
mobu Junior

Joined: 21 Jul 2019 Posts: 3
|
Posted: 14/11/2019 12:42 Post subject: |
|
|
So you need first open file on newer v13 and on file open select v12 (or older v11.1) version for downgrade, then rebuild project and save to archive compus (*.sta).
You also maybe need select firmware version to lower on hardware config so that file open won't go to file converting error from sta-file that in case you have newer firmware selected on v13 version than v12 installation supports
Client needs then donwload v12 version to CPU, otherwise online connection isn't possible because project build version isn't the same on PC than on CPU.
Depending of project settings of old project all data is lost or maintained on CPU at download
Check Unity Pro Versions and PLC OS compatibility
This table gives the application version created with the different Unity Pro versions.
Application version corresponds to the processor OS version displayed in Unity Pro configuration screen.
The OS version corresponds to the minimum version required to execute an application functional level.
Higher OS versions ensure compatibility with a lower application version.
As example: an application version V2.00 generated by Unity Pro V3.0 can be executed by a PLC OS version V2.30.
https://www.se.com/ww/resources/sites/SCHNEIDER_ELECTRIC/content/live/FAQS/333000/FA333334/en_US/ReleaseNotes.html
After you use the manufacturer’s instructions to install a module or device DTM on your PC, update
the Unity Pro Hardware Catalog. The update makes the new Ethernet module or device available
to your Unity Pro application.
https://www.se.com/ww/resources/sites/SCHNEIDER_ELECTRIC/content/live/FAQS/330000/FA330869/en_US/M580UserGuide_UnityV8_EIO0000001578.00.pdf |
|
| Back to top |
|
 |
longwangwl456 Member junior

Joined: 02 May 2018 Posts: 82
|
Posted: 14/11/2019 16:16 Post subject: |
|
|
thanks.
currently i don't worry about link to the real plc. just want to check logic. |
|