Posted: 26/11/2023 08:34 Post subject: Aveva Plant SCADA 2020 (Citect) communicate with Omron CJ2M |
|
|
Hi All,
I aim to use Aveva Plant SCADA 2020 to read and write data from/to Omron CJ2M CPU35 PLC using OMFINS protocol. However I have Bad Data (Not #COM) in runtime.
The setting of SCADA and PLC shows below:
a. Omron CJ2M CPU35 built in Ethernet CJ2M-EIP21 - Unit 0, Node 10, Network :1, IP Address: 192.168.1.10, FINS/TCP Port: 9600.
Declared Symbol: A_Test_AI1, INT, D501, Publication
b. Aveva Plant SCADA 2020
Network Address: 192.168.1.1
{Boards} Server Name: IOServer1, Board Name: BOARD1, Board Type: TCP/IP, Address: 0
{Port} Server Name: IOServer1, Port Name: PORT1_BOARD1, Server Name: IOServer1, Port Number: 1, Particular Opt: -I192.168.1.10 -P9600 -T
{IODevice}: Server Name: IOServer1, Name: Omron_PLC, Number: 1, Address: 1/10/0/V, Protocol: OMFINS3, Port Name: PORT1_BOARD1, Automatic Refresh: TRUE
Declared Variable: A_TEST_AI1, Cluster1, Omron_PLC, INT, D501
{Citect.ini}: [OMFINS] Source: 1/1/0
I able to ping 192.168.1.10 (PLC IP address) from SCADA PC
From Kernel, I have error message below:
Error: Unit offline UINT 000c PORT1_BOARD1 Omron_PLC Error_in_CMD-3 16 Generic 000012 Driver 0000022 (0X00000016)
Appreciate that if anyone can give some hint to solve the problem
Thank you in advance |
|
| Back to top |
|
 |
Gennyttkyg Junior

Joined: 29 Dec 2023 Posts: 3
|
Posted: 25/04/2024 19:29 Post subject: Re: Aveva Plant SCADA 2020 (Citect) communicate with Omron C |
|
|
| xcyong89 wrote: | Hi All,
I aim to use Aveva Plant SCADA 2020 to read and write data from/to Omron CJ2M CPU35 PLC using OMFINS protocol. However I have Bad Data (Not #COM) in runtime.
The setting of SCADA and PLC shows below:
a. Omron CJ2M CPU35 built in Ethernet CJ2M-EIP21 - Unit 0, Node 10, Network :1, IP Address: 192.168.1.10, FINS/TCP Port: 9600.
Declared Symbol: A_Test_AI1, INT, D501, Publication
b. Aveva Plant SCADA 2020
Network Address: 192.168.1.1
{Boards} Server Name: IOServer1, Board Name: BOARD1, Board Type: TCP/IP, Address: 0
{Port} Server Name: IOServer1, Port Name: PORT1_BOARD1, Server Name: IOServer1, Port Number: 1, Special Opt: -I192.168.1.10 -P9600 -T
{IODevice}: Server Name: IOServer1, Name: Omron_PLC, Number: 1, Address: 1/10/0/V, Protocol: OMFINS3, Port Name: PORT1_BOARD1, Automatic Refresh: TRUE
Declared Variable: A_TEST_AI1, Cluster1, Omron_PLC, INT, D501
{Citect.ini}: [OMFINS] Source: 1/1/0
I able to ping 192.168.1.10 (PLC IP address) from SCADA PC
From Kernel, I have error message below:
Error: Unit offline UINT 000c PORT1_BOARD1 Omron_PLC Error_in_CMD-3 16 Generic 000012 Driver 0000022 (0X00000016)
Appreciate that if anyone can give some hint to solve the problem
Thank you in advance |
check
https://industrial-software.com/wp-content/uploads/Communication_Drivers/oi-communication-drivers-pack-2020-r2/Readme_OMRONFINS.html |
|
| Back to top |
|
 |
Yans Member junior

Joined: 26 Jun 2023 Posts: 82
|
Posted: 11/05/2024 01:32 Post subject: Re: Aveva Plant SCADA 2020 (Citect) communicate with Omron C |
|
|
| Gennyttkyg wrote: | | xcyong89 wrote: | Hi All,
I aim to use Aveva Plant SCADA 2020 to read and write data from/to Omron CJ2M CPU35 PLC using OMFINS protocol. However I have Bad Data (Not #COM) in runtime.
The setting of SCADA and PLC shows below:
a. Omron CJ2M CPU35 built in Ethernet CJ2M-EIP21 - Unit 0, Node 10, Network :1, IP Address: 192.168.1.10, FINS/TCP Port: 9600.
Declared Symbol: A_Test_AI1, INT, D501, Publication
b. Aveva Plant SCADA 2020
Network Address: 192.168.1.1
{Boards} Server Name: IOServer1, Board Name: BOARD1, Board Type: TCP/IP, Address: 0
{Port} Server Name: IOServer1, Port Name: PORT1_BOARD1, Server Name: IOServer1, Port Number: 1, Singular Opt: -I192.168.1.10 -P9600 -T
{IODevice}: Server Name: IOServer1, Name: Omron_PLC, Number: 1, Address: 1/10/0/V, Protocol: OMFINS3, Port Name: PORT1_BOARD1, Automatic Refresh: TRUE
Declared Variable: A_TEST_AI1, Cluster1, Omron_PLC, INT, D501
{Citect.ini}: [OMFINS] Source: 1/1/0
I able to ping 192.168.1.10 (PLC IP address) from SCADA PC
From Kernel, I have error message below:
Error: Unit offline UINT 000c PORT1_BOARD1 Omron_PLC Error_in_CMD-3 16 Generic 000012 Driver 0000022 (0X00000016)
Appreciate that if anyone can give some hint to solve the problem
Thank you in advance |
check
https://industrial-software.com/wp-content/uploads/Communication_Drivers/oi-communication-drivers-pack-2020-r2/Readme_OMRONFINS.html |
Does anyone have AVEVA Plant SCADA 2023 R2? if anyone has it, please share the link with me |
|
| Back to top |
|
 |
absaud Member 2

Joined: 19 Apr 2014 Posts: 313
|
Posted: 11/05/2024 19:42 Post subject: Re: Aveva Plant SCADA 2020 (Citect) communicate with Omron C |
|
|
| Yans wrote: | | Gennyttkyg wrote: | | xcyong89 wrote: | Hi All,
I aim to use Aveva Plant SCADA 2020 to read and write data from/to Omron CJ2M CPU35 PLC using OMFINS protocol. However I have Bad Data (Not #COM) in runtime.
The setting of SCADA and PLC shows below:
a. Omron CJ2M CPU35 built in Ethernet CJ2M-EIP21 - Unit 0, Node 10, Network :1, IP Address: 192.168.1.10, FINS/TCP Port: 9600.
Declared Symbol: A_Test_AI1, INT, D501, Publication
b. Aveva Plant SCADA 2020
Network Address: 192.168.1.1
{Boards} Server Name: IOServer1, Board Name: BOARD1, Board Type: TCP/IP, Address: 0
{Port} Server Name: IOServer1, Port Name: PORT1_BOARD1, Server Name: IOServer1, Port Number: 1, Singular Opt: -I192.168.1.10 -P9600 -T
{IODevice}: Server Name: IOServer1, Name: Omron_PLC, Number: 1, Address: 1/10/0/V, Protocol: OMFINS3, Port Name: PORT1_BOARD1, Automatic Refresh: TRUE
Declared Variable: A_TEST_AI1, Cluster1, Omron_PLC, INT, D501
{Citect.ini}: [OMFINS] Source: 1/1/0
I able to ping 192.168.1.10 (PLC IP address) from SCADA PC
From Kernel, I have error message below:
Error: Unit offline UINT 000c PORT1_BOARD1 Omron_PLC Error_in_CMD-3 16 Generic 000012 Driver 0000022 (0X00000016)
Appreciate that if anyone can give some hint to solve the problem
Thank you in advance |
check
https://industrial-software.com/wp-content/uploads/Communication_Drivers/oi-communication-drivers-pack-2020-r2/Readme_OMRONFINS.html |
Does anyone have AVEVA Plant SCADA 2023 R2? if anyone has it, please share the link with me |
http://plc.myforum.ro/viewtopic.php?p=69018#69018 |
|
| Back to top |
|
 |
|
|
You cannot post new topics in this forum You cannot reply to topics in this forum You cannot edit your posts in this forum You cannot delete your posts in this forum You cannot vote in polls in this forum
|
Powered by phpBB © 2001, 2005 phpBB Group Fa-ti si tu propriul forum GRATUIT, pe www.myforum.ro
|