PostPosted: 22/11/2021 16:06    Post subject: Autostart WinCC Runtime Advanced (TIA Portal) Reply with quote

How is the Autostart in Windows configured and delayed for WinCC Runtime Advanced?
https://support.industry.siemens.com/cs/document/58565180/
The Autostart and the delay of the WinCC Runtime Advanced in Windows can be realized using the Windows Task Scheduler. This entry describes the procedure for PC stations and panels.
Depending on the configuration of your operator station, synchronization conflicts with other applications might arise with the Autostart of WinCC Runtime. You can avoid such conflicts by delaying the start of the Runtime by a specific time.

Section 1: PC station
1. Via "Start -> Windows -> Administrative Tools -> Task Scheduler"
you open the Task Scheduler.
Autostart  WinCC Runtime Advanced (TIA Portal) Autostart  WinCC Runtime Advanced (TIA Portal)
2. Create a new task in the Windows Task Scheduler by selecting "Create Task...".
Autostart  WinCC Runtime Advanced (TIA Portal) Autostart  WinCC Runtime Advanced (TIA Portal)
Fig. 02

3. Enter a program name and description.
Set the user and operating system. Then click "OK".
Autostart  WinCC Runtime Advanced (TIA Portal) Autostart  WinCC Runtime Advanced (TIA Portal)
Fig. 03

4. Switch to the "Trigger" tab and click "New...".
Autostart  WinCC Runtime Advanced (TIA Portal) Autostart  WinCC Runtime Advanced (TIA Portal)
Fig. 04

5. Apply the settings as shown in Fig. 05.
If necessary, change the delay time to suit your requirements.
Then click "OK".
Autostart  WinCC Runtime Advanced (TIA Portal) Autostart  WinCC Runtime Advanced (TIA Portal)
Fig. 05

6. Check the marked settings and click "OK".
Autostart  WinCC Runtime Advanced (TIA Portal) Autostart  WinCC Runtime Advanced (TIA Portal)
Fig. 06

7. Switch to the "Actions" tab and click "New...".
Autostart  WinCC Runtime Advanced (TIA Portal) Autostart  WinCC Runtime Advanced (TIA Portal)
Fig. 07

8. Select the action "Start a program" and search for the program/script to be started.
An example of a program path is shown in Fig. 09.
Autostart  WinCC Runtime Advanced (TIA Portal) Autostart  WinCC Runtime Advanced (TIA Portal)
Fig. 08
Autostart  WinCC Runtime Advanced (TIA Portal) Autostart  WinCC Runtime Advanced (TIA Portal)
Fig. 09

9. Switch to the "Conditions" tab and set the conditions as shown in Fig. 10.
Autostart  WinCC Runtime Advanced (TIA Portal) Autostart  WinCC Runtime Advanced (TIA Portal)
Fig. 10

10. Switch to the "Settings” tab and set them as shown in Fig. 11.
If necessary, change the settings to meet your requirements.
Then click "OK".
This completes the task scheduling.
Autostart  WinCC Runtime Advanced (TIA Portal) Autostart  WinCC Runtime Advanced (TIA Portal)
Fig. 11

11. Restart the PC station and test the Autostart.

Section 2: Panel
1. Call the Start Center via "Start -> Siemens Automation -> WinCC Runtime Loader".
Autostart  WinCC Runtime Advanced (TIA Portal) Autostart  WinCC Runtime Advanced (TIA Portal)
Fig. 12

2. Click "Settings".
Autostart  WinCC Runtime Advanced (TIA Portal) Autostart  WinCC Runtime Advanced (TIA Portal)
Fig. 13

3. If the WinCC project is already on the panel, set the parameters as follows:

Autostart  WinCC Runtime Advanced (TIA Portal) Autostart  WinCC Runtime Advanced (TIA Portal)
Fig. 14
Note: The executable project is located in the "Configuration path".

4. If the project still needs to be loaded, set the parameters as follows:

Autostart  WinCC Runtime Advanced (TIA Portal) Autostart  WinCC Runtime Advanced (TIA Portal)
Fig. 15

5. Click "Start" to start the Runtime.

Autostart  WinCC Runtime Advanced (TIA Portal) Autostart  WinCC Runtime Advanced (TIA Portal)
Fig. 16
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> SIEMENS SIMATIC HMI All times are GMT + 2 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group
Fa-ti si tu propriul forum GRATUIT, pe www.myforum.ro