SINAMICS G120 (CU2x0x-2): Activation of the know-how protection via the IOP.
The know-how protection (KHP) allows to completely hide all the modified converter parameters. The know-how protection can be activated via the STARTER resp. IOP
How can I activate the know-how protection via IOP?
Activation of the know-how protection via the IOP
The passwort is entered in the parameter p7767.
Each parameter index corresponds to a character in the ASCII format.
The password entry is completed by entering "0“ in the parameter index 29.
To confirm the passward, enter in the parameter p7768 the same password as in p7767.
The password entry is completed by entering "0“ in the parameter index 29.
Afterwards, the converter is know-how protected.
The passwort to cancel the know-how protection is entered via the parameter p7766
Manual
https://cache.industry.siemens.com/dl/files/450/101920450/att_81141/v1/IOP_BA15_0614_eng_en-US.pdf
When reading the parameter index, 42 ("*“) is always read out. |
|