PostPosted: 06/05/2018 21:01    Post subject: ACS1000i COMMISSIONING FAILURE Reply with quote

I need help with a acs1000 ABB DRIVE COMMISSIONING, the drive show a SM1Control FAULT in the operator panel, i have connected all the main breaker feedback signals from ABB Bypass with REM615 MODULE and i need some body help me with a cause and effect matrix about the control of main braker be cause i dont find an error in the conections.
_________________
ENG. RAFAEL AN
Back to top
View user's profile Send private message Send e-mail
deibal
Junior
Junior


Joined: 04 May 2018
Posts: 1

PostPosted: 07/05/2018 07:36    Post subject: Reply with quote

From Manual...

SM1Control Fault
Parameter: 9.08 Bit: B00

Meaning of message:
Synchronous bypass: motor circuit breaker 1 control fault (motor circuit breaker discrepancy between command and feedback).
Connections: DI13-IOEC5, terminals X110:1, X110:2.
The synchronous bypass functions are set in parameter group 65.
The fault will be activated if the motor circuit breaker did not follow the command from customer side.
Bypass circuit breaker is closed but should be opened due to the stop motor from line command.
This signal will continue for 60 seconds

Possible causes
Motor circuit breaker 1 feedback has not been received in time after a command

Hints for rectification

Check the motor circuit breaker control on customer side. Check the wiring of the feedback signal.
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> Drives & Inverters All times are GMT + 2 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group
Fa-ti si tu propriul forum GRATUIT, pe www.myforum.ro