PostPosted: 06/12/2016 16:03    Post subject: ACS 800 ABB (Cabinet Built) Reply with quote

Hi Everybody

I hope someone could clarify me on this issue.

We have an ACS 800 ABB Drive (cabinet built) for 400 kW motor. When it is powered only, there is a transformer Trafomic TNR 26492 that smells (like burning).

I would like to know for what purpose is this transformer.

If it operates for 10 mins, we get alarm ACS 800 temp i.e. IGBT overheat.

Can someone suggest what test and action may be required

Thanking you beforehand.
Back to top
View user's profile Send private message
lovato
Junior
Junior


Joined: 16 Oct 2016
Posts: 15

PostPosted: 06/12/2016 21:30    Post subject: Re: ACS 800 ABB (Cabinet Built) Reply with quote

a_rishi wrote:
Hi Everybody

I hope someone could clarify me on this issue.

We have an ACS 800 ABB Drive (cabinet built) for 400 kW motor. When it is powered only, there is a transformer Trafomic TNR 26492 that smells (like burning).

I would like to know for what purpose is this transformer.

If it operates for 10 mins, we get alarm ACS 800 temp i.e. IGBT overheat.

Can someone suggest what test and action may be required

Thanking you beforehand.


it's a 230VAC to 23V transformer?
ACS 800 ABB (Cabinet Built) Re: ACS 800 ABB (Cabinet Built)


Check ambient conditions.
Check air flow and fan operation.
Check heatsink fins for dust pick-up.
Check motor power against unit power.


Excessive IGBT junction to case temperature.
This can be caused by excessive load at low
frequencies (e.g. fast direction change with
excessive load and inertia).
remedy
R
Increase ramp time.
Reduce load.

Short circuit in brake chopper IGBT(s)
Replace brake chopper.
R
Ensure brake resistor is connected and not
damaged.

Excessive IGBT junction to case temperature.
This fault protects IGBT(s) and it can be
activated by short circuit at output of long
motor cables.
R
Check motor cables
Read
[URL=https://userscloud.com/zg6uf39ldp7d]ACS800_PCP_ESP_FW_B.pdf - 1.5 MB[/URL]
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    plc.myforum.ro Forum Index -> Drives & Inverters All times are GMT + 2 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum


Powered by phpBB © 2001, 2005 phpBB Group
Fa-ti si tu propriul forum GRATUIT, pe www.myforum.ro